Taylor-I believe Tyco offers one; it might be a bit hard to locate on their site though.
Cary Webber CFPS Director, Technical Services Reliable Automatic Sprinkler Co., Inc. 1470 Smith Grove Road, Liberty, SC 29657 Tel: 864-843-5161 [https://www.reliablesprinkler.com/sites/default/files/image001.png]<http://www.reliablesprinkler.com/> From: Taylor Schumacher <[email protected]> Sent: Tuesday, May 23, 2023 2:05 PM To: '[email protected]' <[email protected]> Subject: [Sprinklerforum] Sidewalls for 18 Inches Down CAUTION: This email originated from outside of the organization. Do not click links or open attachments unless you can confirm the sender and know the content is safe. Does anyone know of a sprinkler that meets the allowance for up 18 inches below a ceiling? I have an architect that's quoting that section, but I've never seen that unicorn... 8.7.4.1.1.2 Horizontal sidewall sprinklers shall be permitted to be located in a zone 6 in. to 12 in. (150 mm to 300 mm) or 12 in. to 18 in. (300 mm to 450 mm) below noncombustible and limited-combustible ceilings where listed for such use. Taylor Schumacher Security Fire Sprinkler<http://www.j-berd.com/> 1 Industrial Blvd | Sauk Rapids, MN 56379 Office: 320.656.0847 | Direct: 320.640.7050