You would need to look at the FM listing of the head.  All heads should be 
listed as storage or non and quick or standard response in the FM approval 
guide, which is available online.  If the head isn’t FM listed and you’re going 
to use it anyway typically anything with an RTI <50 (ESFR, listed quick 
response, residential) would be accepted as QR to FM.

Mike Morey
CFPS 3229 • NICET S.E.T. 123677
Project Manager • Fire Protection Group
Shambaugh & Son, LP an EMCOR Company
7614 Opportunity Drive • Fort Wayne, IN • 46825
direct 260.487.7824 /  cell 260.417.0625 /  fax 260.487.7991
email [email protected]
[cid:[email protected]]

From: Gregg Fontes <[email protected]>
Sent: Friday, May 12, 2023 10:25 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] FM Data Sheets & ESFR (Storage) Sprinklers

When applying FM Data tables that call for quick response fire sprinklers, is a 
ESFR fire sprinkler considered quick response or as the cut sheet states fast 
response? Or is quick response and fast response considered the same? Thanks, 
Gregg
ZjQcmQRYFpfptBannerStart
This Message Is From an External Sender
This message originated outside your organization.
ZjQcmQRYFpfptBannerEnd
When applying FM Data tables that call for quick response fire sprinklers, is a 
ESFR fire sprinkler considered quick response or as the cut sheet states fast 
response?  Or is quick response and fast response considered the same?

Thanks,
Gregg Fontes
Lead Estimator
O: 209-334-9119
[email protected]<mailto:[email protected]>

[image001.jpg]

This and any attached documents are for the use of the intended recipient(s) 
only and may contain information that is privileged, confidential, or work 
product that may be exempt from disclosure under applicable law. If you are not 
the intended recipient, any use, dissemination, distribution, or copying of 
this communication and any attachments is strictly prohibited, and you are 
hereby requested to delete this message and any attached documents, to destroy 
any printed copies, and to telephone or otherwise contact the sender 
immediately about the error



This message is for the named person's use only.  It may contain confidential, 
proprietary or legally privileged information. No confidentiality or privilege 
is waived or lost by any mistransmission.  If you receive this message in 
error, please  immediately delete it and all copies of it from your system, 
destroy any hard copies of it and notify the sender.  You must not, directly or 
indirectly, use, disclose, distribute, print, or copy any part of this message 
if you are not the intended recipient.
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to