Yes, you are 100% correct. 
However, if a General Information sign is required by NFPA 13, how would one comply with this requirement?

I think but I could be wrong, NFPA 13 and 25 need to be reviewed for conflicts on this issue. I’m open to thoughts.  

All - By the way, great discussion. This is how we improve our understanding of the standards or change the standards for the better. (In most cases 😜)

John

John August Denhardt, P.E.
Vice-President Engineering and Technical Services
American Fire Sprinkler Association 
301-343-1457

On May 11, 2023, at 12:55 PM, Anthony Carrizosa <[email protected]> wrote:



John

NFPA 25 -2020

13.2.3 MAIN DRAIN TEST. Shall be conducted annually for each water supply lead-in to a building.

13.2.3.1 Where the lead-in to a building supplies a header or manifold serving multiple systems, A single main drain test shall be permitted.

Of course as you state the AHJ must be consulted as they may require each system to be tested.

 

 

 

From: John Denhardt <[email protected]>
Sent: Thursday, May 11, 2023 10:41 AM
To: Discussion list on issues relating to automatic fire sprinklers <[email protected]>
Subject: [Sprinklerforum] Re: [EXTERNAL] Re: Fire Pump Drains

 

Craig - I see this when a main test is required by the AHJ on any system supplied by a fire pump system.   I also recommend testing all water flow devices with the fire pump system in its normal operating condition.

 

Each system is considered a separate system. Each system is supposed to have an annual main drain test. On acceptance test, the main drain is supposed to be recorded on the General Information sign for each system and the Aboveground Test Certificate. The original main drain test data is then to be used for comparison to annual NFPA 25 test data. I recommend main drain test are conducted with the fire pump in its normal operating condition. 

 

John

John August Denhardt, P.E.

Vice-President Engineering and Technical Services

American Fire Sprinkler Association 

301-343-1457

 

On May 11, 2023, at 12:31 PM, Prahl, Craig <[email protected]> wrote:



John,

 

I’m not sure of a situation or purpose where you’d have the pump running and be discharging flow through a 2” system drain. 

 

A drain on the fire pump discharge piping to be able to drain it before doing maintenance would be helpful. 

 

Craig Prahl | Jacobs | Group Lead/SME – Fire Protection | [email protected] | www.jacobs.com

1041 East Butler Road   Greenville, South Carolina  29606

CONTACT BY: Phone 1-864-676-5252, Email or MS TEAMS

 

 

From: John Denhardt <[email protected]>
Sent: Thursday, May 11, 2023 1:17 PM
To: Discussion list on issues relating to automatic fire sprinklers <[email protected]>
Subject: [EXTERNAL] [Sprinklerforum] Re: Fire Pump Drains

 

Craig - 100% agree. All systems need a main drain piped to an acceptable place of discharge that can handle full flow with the fire pump system (if provided) operating. 

 

There should also be a method to drain the fire pump system piping. 


John

John August Denhardt, P.E.

Vice-President Engineering and Technical Services

American Fire Sprinkler Association 

301-343-1457



On May 11, 2023, at 12:12 PM, Prahl, Craig <[email protected]> wrote:



I’m not sure I understand the correlation between system drains and the subject of this post?

 

There needs to be a drain from each sprinkler system valve, wet, dry, PA or Deluge, doesn’t matter.

 

There needs to be a drain in the fire pump room. 

 

Craig Prahl | Jacobs | Group Lead/SME – Fire Protection | [email protected] | www.jacobs.com

1041 East Butler Road   Greenville, South Carolina  29606

CONTACT BY: Phone 1-864-676-5252, Email or MS TEAMS

 

 

From: Brian Harris <[email protected]>
Sent: Thursday, May 11, 2023 11:23 AM
To: [email protected]
Subject: [EXTERNAL] [Sprinklerforum] Fire Pump Drains

 

Installing a Dry system fed from a pump and while running the 2” drain outside the building from the dry valve it dawned on me we never show a drain for the wet system. I’m assuming that’s taken care of from the casing drain on the pump?

 

Brian Harris, CET

BVS Systems Inc.

bvssystemsinc.com

Phone: 704.896.9989

Fax: 704.896.1935

 

 

 



NOTICE - This communication may contain confidential and privileged information that is for the sole use of the intended recipient. Any viewing, copying or distribution of, or reliance on this message by unintended recipients is strictly prohibited. If you have received this message in error, please notify us immediately by replying to the message and deleting it from your computer.

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

 



NOTICE - This communication may contain confidential and privileged information that is for the sole use of the intended recipient. Any viewing, copying or distribution of, or reliance on this message by unintended recipients is strictly prohibited. If you have received this message in error, please notify us immediately by replying to the message and deleting it from your computer.

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]


_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to