John
NFPA 25 -2020
13.2.3 MAIN DRAIN TEST. Shall be conducted annually for each water supply 
lead-in to a building.
13.2.3.1 Where the lead-in to a building supplies a header or manifold serving 
multiple systems, A single main drain test shall be permitted.
Of course as you state the AHJ must be consulted as they may require each 
system to be tested.



From: John Denhardt <[email protected]>
Sent: Thursday, May 11, 2023 10:41 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Re: [EXTERNAL] Re: Fire Pump Drains

Craig - I see this when a main test is required by the AHJ on any system 
supplied by a fire pump system.   I also recommend testing all water flow 
devices with the fire pump system in its normal operating condition.

Each system is considered a separate system. Each system is supposed to have an 
annual main drain test. On acceptance test, the main drain is supposed to be 
recorded on the General Information sign for each system and the Aboveground 
Test Certificate. The original main drain test data is then to be used for 
comparison to annual NFPA 25 test data. I recommend main drain test are 
conducted with the fire pump in its normal operating condition.

John
John August Denhardt, P.E.
Vice-President Engineering and Technical Services
American Fire Sprinkler Association
301-343-1457

On May 11, 2023, at 12:31 PM, Prahl, Craig 
<[email protected]<mailto:[email protected]>> wrote:

John,

I’m not sure of a situation or purpose where you’d have the pump running and be 
discharging flow through a 2” system drain.

A drain on the fire pump discharge piping to be able to drain it before doing 
maintenance would be helpful.

Craig Prahl | Jacobs | Group Lead/SME – Fire Protection | 
[email protected]<mailto:[email protected]> | 
www.jacobs.com<https://linkprotect.cudasvc.com/url?a=https%3a%2f%2fnam02.safelinks.protection.outlook.com%2f%3furl%3dhttps%253A%252F%252Furldefense.com%252Fv3%252F__http%253A%252Fwww.jacobs.com%252F__%253B%21%21KZTdOCjhgt4hgw%21-_khxU8gU0_6jc895I7kRbnU8JghRDsWgqOblZ4jr7Qp2IVbR30VYw_hWvNFtphnl0uWpB9KIvbYi1pvZz4%2524%26data%3d05%257C01%257Cjdenhardt%2540stricklandfire.com%257C3505a82b279142dcd6fd08db524564e2%257Cd658cbf30820420e8485ef2e373e8459%257C0%257C0%257C638194230232120314%257CUnknown%257CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%253D%257C3000%257C%257C%257C%26sdata%3ddBHPJuUVyx4PXT1uFe7wGjGyTHqKCJQWXfJ%252FsK2m3hk%253D%26reserved%3d0&c=E,1,yemVXhqjjK-8EqbQNunPIjbTxGLilt1HUSSVQMW1F43yrrkY8plQDGFi4l4f_1QhQkQ0WBaRxcbZRj_HXGJa57SNHegW8XDqL7sjWtiQ&typo=1>
1041 East Butler Road   Greenville, South Carolina  29606
CONTACT BY: Phone 1-864-676-5252, Email or MS TEAMS


From: John Denhardt 
<[email protected]<mailto:[email protected]>>
Sent: Thursday, May 11, 2023 1:17 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: [EXTERNAL] [Sprinklerforum] Re: Fire Pump Drains

Craig - 100% agree. All systems need a main drain piped to an acceptable place 
of discharge that can handle full flow with the fire pump system (if provided) 
operating.

There should also be a method to drain the fire pump system piping.

John
John August Denhardt, P.E.
Vice-President Engineering and Technical Services
American Fire Sprinkler Association
301-343-1457


On May 11, 2023, at 12:12 PM, Prahl, Craig 
<[email protected]<mailto:[email protected]>> wrote:

I’m not sure I understand the correlation between system drains and the subject 
of this post?

There needs to be a drain from each sprinkler system valve, wet, dry, PA or 
Deluge, doesn’t matter.

There needs to be a drain in the fire pump room.

Craig Prahl | Jacobs | Group Lead/SME – Fire Protection | 
[email protected]<mailto:[email protected]> | 
www.jacobs.com<https://linkprotect.cudasvc.com/url?a=https%3a%2f%2fnam02.safelinks.protection.outlook.com%2f%3furl%3dhttps%253A%252F%252Furldefense.com%252Fv3%252F__https%253A%252Fnam02.safelinks.protection.outlook.com%252F%253Furl%253Dhttps%2a3A%2a2F%2a2Furldefense.com%2a2Fv3%2a2F__http%2a3A%2a2Fwww.jacobs.com%2a2F__%2a3B%21%21KZTdOCjhgt4hgw%21-_khxU8gU0_6jc895I7kRbnU8JghRDsWgqOblZ4jr7Qp2IVbR30VYw_hWvNFtphnl0uWpB9KIvbYi1pvZz4%2a24%2526data%253D05%2a7C01%2a7Cjdenhardt%2a40stricklandfire.com%2a7C2129380d08804f1fd3e008db5242e1ae%2a7Cd658cbf30820420e8485ef2e373e8459%2a7C0%2a7C0%2a7C638194219452249732%2a7CUnknown%2a7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%2a3D%2a7C3000%2a7C%2a7C%2a7C%2526sdata%253DeXdq3TZwd5ABk9RVJ3GeROxeZtLDhqKF1K%2a2Fqh8I32Uw%2a3D%2526reserved%253D0__%253BJSUlJSUlJSUlJSUlJSUlJSUlJSUlJSUlJSUl%21%21B5cixuoO7ltTeg%21HiCuRAlm_f8hPDx_4h0wfAR2fNG3K8-6p5IX2VwYH7JupHpvt4E65t88GlZK7TRiJGojm3tX5QoabwjBUmK4OevjLQ%2524%26data%3d05%257C01%257Cjdenhardt%2540stricklandfire.com%257C3505a82b279142dcd6fd08db524564e2%257Cd658cbf30820420e8485ef2e373e8459%257C0%257C0%257C638194230232120314%257CUnknown%257CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%253D%257C3000%257C%257C%257C%26sdata%3dr0uz99GBAZa9pqcEQ5LHPnD3rWzzWWzwC1mX%252BZ7hMq4%253D%26reserved%3d0&c=E,1,Ji7RoSka2w_Wnb8s2w6mGAXVQwQ_BKagTtUZZl4FDG3jsb6vIQlgOjTvrbLj7n3J0FhMzVpuvudapQZkT1p3LtKsbaMT3BCzBclxE0AE-MQY_Ex3dDbTPDQ,&typo=1>
1041 East Butler Road   Greenville, South Carolina  29606
CONTACT BY: Phone 1-864-676-5252, Email or MS TEAMS


From: Brian Harris <[email protected]<mailto:[email protected]>>
Sent: Thursday, May 11, 2023 11:23 AM
To: 
[email protected]<mailto:[email protected]>
Subject: [EXTERNAL] [Sprinklerforum] Fire Pump Drains

Installing a Dry system fed from a pump and while running the 2” drain outside 
the building from the dry valve it dawned on me we never show a drain for the 
wet system. I’m assuming that’s taken care of from the casing drain on the pump?

Brian Harris, CET
BVS Systems Inc.
bvssystemsinc.com<https://linkprotect.cudasvc.com/url?a=https%3a%2f%2fnam02.safelinks.protection.outlook.com%2f%3furl%3dhttps%253A%252F%252Furldefense.com%252Fv3%252F__https%253A%252Fnam02.safelinks.protection.outlook.com%252F%253Furl%253Dhttps%2a3A%2a2F%2a2Furldefense.com%2a2Fv3%2a2F__http%2a3A%2a2Fbvssystemsinc.com%2a2F__%2a3B%21%21B5cixuoO7ltTeg%21F2vnBf8jFbCIMGxunXjCuULCm5nmOipnJACm9JB3vRtzJ4CbQc5V2JF3OH7Vgp20nZOrM9KYKj4EZ8vSoLLbgehD%2a24%2526data%253D05%2a7C01%2a7Cjdenhardt%2a40stricklandfire.com%2a7C2129380d08804f1fd3e008db5242e1ae%2a7Cd658cbf30820420e8485ef2e373e8459%2a7C0%2a7C0%2a7C638194219452249732%2a7CUnknown%2a7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%2a3D%2a7C3000%2a7C%2a7C%2a7C%2526sdata%253DJkw7%2a2Fv0iHOD%2a2BxwAuYmSD7YMiAAGm8bDelOw1BUuMbnI%2a3D%2526reserved%253D0__%253BJSUlJSUlJSUlJSUlJSUlJSUlJSUlJSUlJSUlJQ%21%21B5cixuoO7ltTeg%21HiCuRAlm_f8hPDx_4h0wfAR2fNG3K8-6p5IX2VwYH7JupHpvt4E65t88GlZK7TRiJGojm3tX5QoabwjBUmIp1jUNXw%2524%26data%3d05%257C01%257Cjdenhardt%2540stricklandfire.com%257C3505a82b279142dcd6fd08db524564e2%257Cd658cbf30820420e8485ef2e373e8459%257C0%257C0%257C638194230232120314%257CUnknown%257CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%253D%257C3000%257C%257C%257C%26sdata%3dZq4Nr4Q4BIQ57jxd35JhqnZKSZHqr7NvjuElOPGle74%253D%26reserved%3d0&c=E,1,5AInHSLbQlT7n4sDjJl94Gils-2DygszP_MuYoVwxSy-5LkduI9HBVDgXKkW3bBxPz25o9IidEuq1USjhyGtU0ntaKh_6N0eKfSh9KVXwv-u0Q,,&typo=1>
Phone: 704.896.9989
Fax: 704.896.1935



________________________________

NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org<https://linkprotect.cudasvc.com/url?a=https%3a%2f%2fnam02.safelinks.protection.outlook.com%2f%3furl%3dhttps%253A%252F%252Furldefense.com%252Fv3%252F__https%253A%252Flists.firesprinkler.org%252Flist%252Fsprinklerforum.lists.firesprinkler.org__%253B%21%21B5cixuoO7ltTeg%21HiCuRAlm_f8hPDx_4h0wfAR2fNG3K8-6p5IX2VwYH7JupHpvt4E65t88GlZK7TRiJGojm3tX5QoabwjBUmJ-7uXNLQ%2524%26data%3d05%257C01%257Cjdenhardt%2540stricklandfire.com%257C3505a82b279142dcd6fd08db524564e2%257Cd658cbf30820420e8485ef2e373e8459%257C0%257C0%257C638194230232120314%257CUnknown%257CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%253D%257C3000%257C%257C%257C%26sdata%3depUNOENnteqZMZWrw8yO9tDZsjTui3jSjz89JJ%252BdTUw%253D%26reserved%3d0&c=E,1,-HJlEjyLAP7aXyaWiUw9Zm50_k_0Tjpge5aPJDRvTnrbumcaVGija52QE3u2cj3Nsc01f-PiYZ7QYnOsCNePU7rNBZTxN9oZmlVhYSZ1rSOqy73__w7ODnxbuQ,,&typo=1>
To unsubscribe send an email to 
[email protected]<mailto:[email protected]>

________________________________

NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org<https://linkprotect.cudasvc.com/url?a=https%3a%2f%2flists.firesprinkler.org%2flist%2fsprinklerforum.lists.firesprinkler.org&c=E,1,W0-7pBb-_l9rWLgnzRGjoFmlzD09fIpqO9a_LIwi2iDS-ZcOZj0n-TzqWLJIJ-Y9XBdjzunUv8ZCo0h-1Qban2MbsLE41tp-WEUB-RQLM8EzitqWL56GrgtSuZYC&typo=1&ancr_add=1>
To unsubscribe send an email to 
[email protected]<mailto:[email protected]>
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to