I wrote the #20 committee years ago on pump rooms.  There should be a shotgun 
to hold the building during testing, especially transfer switches, and a main 
drain off that as the best way of conducting automatic starts of the fire and 
jockey pumps.  #13 covers us I believe in where we terminate drains, be they 
main drains, drain risers or reliefs; as the location must accommodate 
anticipated flow.

TD

From: John Denhardt <[email protected]> 
Sent: Thursday, May 11, 2023 1:17 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Re: Fire Pump Drains

 

Craig - 100% agree. All systems need a main drain piped to an acceptable place 
of discharge that can handle full flow with the fire pump system (if provided) 
operating. 

 

There should also be a method to drain the fire pump system piping. 


John

John August Denhardt, P.E.

Vice-President Engineering and Technical Services

American Fire Sprinkler Association 

301-343-1457





On May 11, 2023, at 12:12 PM, Prahl, Craig <[email protected] 
<mailto:[email protected]> > wrote:

 

I’m not sure I understand the correlation between system drains and the subject 
of this post?

 

There needs to be a drain from each sprinkler system valve, wet, dry, PA or 
Deluge, doesn’t matter.

 

There needs to be a drain in the fire pump room.  

 

Craig Prahl | Jacobs | Group Lead/SME – Fire Protection |  
<mailto:[email protected]> [email protected] | www.jacobs.com

1041 East Butler Road   Greenville, South Carolina  29606 

CONTACT BY: Phone 1-864-676-5252, Email or MS TEAMS

 

 

From: Brian Harris <[email protected] 
<mailto:[email protected]> > 
Sent: Thursday, May 11, 2023 11:23 AM
To: [email protected] 
<mailto:[email protected]> 
Subject: [EXTERNAL] [Sprinklerforum] Fire Pump Drains

 

Installing a Dry system fed from a pump and while running the 2” drain outside 
the building from the dry valve it dawned on me we never show a drain for the 
wet system. I’m assuming that’s taken care of from the casing drain on the pump?

 

Brian Harris, CET

BVS Systems Inc.

bvssystemsinc.com

Phone: 704.896.9989

Fax: 704.896.1935

 

 

 

  _____  


NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected] 
<mailto:[email protected]> 

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to