Of note: NFPA 25 -2020 A13.2.3 states that if on a fire pump which is tested 
annually it not required to perform a main drain test since the water supply is 
tested through the fire pump. So tis main drain would just be used to drain the 
wet system for any repairs needed.

From: John Denhardt <[email protected]>
Sent: Thursday, May 11, 2023 10:17 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Re: Fire Pump Drains

Craig - 100% agree. All systems need a main drain piped to an acceptable place 
of discharge that can handle full flow with the fire pump system (if provided) 
operating.

There should also be a method to drain the fire pump system piping.

John
John August Denhardt, P.E.
Vice-President Engineering and Technical Services
American Fire Sprinkler Association
301-343-1457


On May 11, 2023, at 12:12 PM, Prahl, Craig 
<[email protected]<mailto:[email protected]>> wrote:

I’m not sure I understand the correlation between system drains and the subject 
of this post?

There needs to be a drain from each sprinkler system valve, wet, dry, PA or 
Deluge, doesn’t matter.

There needs to be a drain in the fire pump room.

Craig Prahl | Jacobs | Group Lead/SME – Fire Protection | 
[email protected]<mailto:[email protected]> | 
www.jacobs.com<https://linkprotect.cudasvc.com/url?a=https%3a%2f%2fnam02.safelinks.protection.outlook.com%2f%3furl%3dhttps%253A%252F%252Furldefense.com%252Fv3%252F__http%253A%252Fwww.jacobs.com%252F__%253B%21%21KZTdOCjhgt4hgw%21-_khxU8gU0_6jc895I7kRbnU8JghRDsWgqOblZ4jr7Qp2IVbR30VYw_hWvNFtphnl0uWpB9KIvbYi1pvZz4%2524%26data%3d05%257C01%257Cjdenhardt%2540stricklandfire.com%257C2129380d08804f1fd3e008db5242e1ae%257Cd658cbf30820420e8485ef2e373e8459%257C0%257C0%257C638194219452249732%257CUnknown%257CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%253D%257C3000%257C%257C%257C%26sdata%3deXdq3TZwd5ABk9RVJ3GeROxeZtLDhqKF1K%252Fqh8I32Uw%253D%26reserved%3d0&c=E,1,UO125Bj7VAQzqTXqPcNJd4DjRz5nnEtX9QCkagquLyG5_bZxVhSBZZHYFYVTF7DO2eM96rEzJg8Tmfwqd5c8oYDXtfwASnOVfD4lYBsf&typo=1>
1041 East Butler Road   Greenville, South Carolina  29606
CONTACT BY: Phone 1-864-676-5252, Email or MS TEAMS


From: Brian Harris <[email protected]<mailto:[email protected]>>
Sent: Thursday, May 11, 2023 11:23 AM
To: 
[email protected]<mailto:[email protected]>
Subject: [EXTERNAL] [Sprinklerforum] Fire Pump Drains

Installing a Dry system fed from a pump and while running the 2” drain outside 
the building from the dry valve it dawned on me we never show a drain for the 
wet system. I’m assuming that’s taken care of from the casing drain on the pump?

Brian Harris, CET
BVS Systems Inc.
bvssystemsinc.com<https://linkprotect.cudasvc.com/url?a=https%3a%2f%2fnam02.safelinks.protection.outlook.com%2f%3furl%3dhttps%253A%252F%252Furldefense.com%252Fv3%252F__http%253A%252Fbvssystemsinc.com%252F__%253B%21%21B5cixuoO7ltTeg%21F2vnBf8jFbCIMGxunXjCuULCm5nmOipnJACm9JB3vRtzJ4CbQc5V2JF3OH7Vgp20nZOrM9KYKj4EZ8vSoLLbgehD%2524%26data%3d05%257C01%257Cjdenhardt%2540stricklandfire.com%257C2129380d08804f1fd3e008db5242e1ae%257Cd658cbf30820420e8485ef2e373e8459%257C0%257C0%257C638194219452249732%257CUnknown%257CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%253D%257C3000%257C%257C%257C%26sdata%3dJkw7%252Fv0iHOD%252BxwAuYmSD7YMiAAGm8bDelOw1BUuMbnI%253D%26reserved%3d0&c=E,1,ptVk5zAUtktx4e753ksBmZb4nkmcdgQsP-8ixU7IVwrH_iEOkIc_wq6dQUxrG5BvqSLpWgLK8iiR5uebIYQPWxkiskuc_XUoRJhD2aC-CoMS7ievzYahaikNZ8g,&typo=1>
Phone: 704.896.9989
Fax: 704.896.1935



________________________________

NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org<https://linkprotect.cudasvc.com/url?a=https%3a%2f%2flists.firesprinkler.org%2flist%2fsprinklerforum.lists.firesprinkler.org&c=E,1,tcl1ZTuy67ZvTtCnVzxRiVyGnmgUJlKR5FvPBdqEFMyp6AjlNPHW4E4yyOSjcm16fevTHnMibdfb0nPR1avK_s9WWbGelhgicnSQTDyFxMHv&typo=1&ancr_add=1>
To unsubscribe send an email to 
[email protected]<mailto:[email protected]>
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to