Re: [RE-wrenches] Power Crimper and Stripper Recommendations and Questions

2024-10-22 Thread Tyrone Houck via RE-wrenches
Here's a link to the dies(U style copper) https://www.platt.com/p/0010680/milwaukee/8-600-mcm-copper-u-style-die-kit/045242339372/mil4916kitc And the tool.. https://www.platt.com/p/0010677/milwaukee/600-350-mcm-crimping-tool/045242339488/mil267922 They have a larger one for up to 750mcm and a m

Re: [RE-wrenches] OB Charging/Comms Issues

2024-11-08 Thread Tyrone Houck via RE-wrenches
Out of curiosity, what mode are you in and what are the respective set points for absorb, float, rebulk, etc. For PV vs inverter? Tyrone Houck Oregon Solarworks LLC LRT #076 541-787-1366 tyr...@oregonsolarworks.com On Fri, Nov 8, 2024, 1:28 PM Chris Sparadeo via RE-wrenches < re-wrenches@lists

Re: [RE-wrenches] Midnite Powerflo16 with Radian

2024-11-09 Thread Tyrone Houck via RE-wrenches
Maybe a silly question but have you tried shutting off all load breakers(ac output) and charge controller breakers before powering up? I've noticed radians have a hard time powering up on homegrids if they have a load. If I have to do a hard reset on a radian I also shutdown the charge controllers

Re: [RE-wrenches] More Issues with Parallel Sol-Ark 15K System

2024-11-09 Thread Tyrone Houck via RE-wrenches
We've noticed a compatability issue with the limitless 15k units and the newest incarnation of the same(limitless 15k) inverter(additional circuitry in the wiring compartment associated with the pv inputs is the one way I'm aware of to tell the difference)..the older units and the newer units don't

Re: [RE-wrenches] Alternate LVD shutdown

2025-01-02 Thread Tyrone Houck via RE-wrenches
> > On Jan 2, 2025, at 10:04 AM, Tyrone Houck via RE-wrenches < > re-wrenches@lists.re-wrenches.org> wrote: > >  > Forgive my ignorance but why won't the vfx lbco work for lithium? > > > > > On Thu, Jan 2, 2025, 8:19 AM Bill Battagin via RE-wrenches < &g

Re: [RE-wrenches] No more Mate3-SL upgrades

2025-02-03 Thread Tyrone Houck via RE-wrenches
Can the mate3SL not use the mate3S firmware? Is there a reason to need a version other than 001.004.007? Or am I misunderstanding your post? Tyrone Houck Oregon Solarworks LLC CCB #204937 LRT #076 541-787-1366 tyr...@oregonsolarworks.com On Mon, Feb 3, 2025, 12:50 PM Nick Lucchese via RE-wrenche

Re: [RE-wrenches] Midnite Powerflo16 to old OB inverters

2025-02-02 Thread Tyrone Houck via RE-wrenches
I think the answer is using a flexnet DC's aux relay terminal to control the on/off switch terminals of the FX inverter. You'll need a mate3S/SL but that should do it without having to change the inverter... On Sun, Feb 2, 2025, 8:52 PM Bill Battagin via RE-wrenches < re-wrenches@lists.re-wrenc

Re: [RE-wrenches] No more Mate3-SL upgrades

2025-02-04 Thread Tyrone Houck via RE-wrenches
less for supporting a client effectively > especially for most off grid sites that tend to be off the beaten path. > > Nick > > On Mon, Feb 3, 2025 at 5:52 PM Tyrone Houck via RE-wrenches < > re-wrenches@lists.re-wrenches.org> wrote: > >> Can the mate3SL not use the mate3

[RE-wrenches] Winco pss12h 12v start to dry contact start

2025-02-10 Thread Tyrone Houck via RE-wrenches
Greetings wrenches, We recently replaced an Outback Fx system with a MN15-12K-AIO and are trying to figure out how to convert the exiting winco genetic from a relay driven 12v auto start to a 2 wire dry contact start. Their tech support is a pain to get ahold of and I figured there are probably fol

Re: [RE-wrenches] More Issues with Parallel Sol-Ark 15K System

2024-12-13 Thread Tyrone Houck via RE-wrenches
Any further investigation into the hardware differences between the newer 15k and the original 15k I mentioned before? That was the only thing that fixed the issue for us. We had to insist they replaced it with a newer matching inverter. I should have made note of the serial numbers to try to narro

Re: [RE-wrenches] SolarEdge

2024-12-13 Thread Tyrone Houck via RE-wrenches
Around that time there were some issues with solaredge equipment..specifically bad optimizers the SE tech support affectionately dubbed "sleepy optimizers". We had one job from that production run that we replaced several of the optimizers on.. in general though we've had great luck with solaredge

Re: [RE-wrenches] AGM battery recommendations

2025-01-12 Thread Tyrone Houck via RE-wrenches
She wants ZERO risk of > fire? She needs to live in a concrete bunker with no electricity at all. > Every electrical connection, every outlet, every appliance has a risk of > fire. Period. > > Ray Walters > Remote Solar > On 1/12/2025 9:39 AM, Tyrone Houck via RE-wrenches wrote:

Re: [RE-wrenches] AGM battery recommendations

2025-01-12 Thread Tyrone Houck via RE-wrenches
I hate to be the one to say it but LFP has arguably less fire risk than agm. A short circuit in an agm could be disastrous and AGM is not necessarily any safer or less prone to thermal runaway events than modern LFP. I'd recommend a cobalt free LFP like homegrid, simpliphi, or midnite if it were me

Re: [RE-wrenches] Anybody play around with a Solaredge S1000 Key?

2025-01-17 Thread Tyrone Houck via RE-wrenches
; > I know there will be million reasons to not do this... > > > -- > *From:* RE-wrenches on behalf > of Tyrone Houck via RE-wrenches > *Sent:* Friday, January 17, 2025 9:01 AM > *To:* RE-wrenches > *Cc:* Tyrone Houck > *Subject:* [RE-wr

[RE-wrenches] Anybody play around with a Solaredge S1000 Key?

2025-01-17 Thread Tyrone Houck via RE-wrenches
Thinking of ordering one from the UK. Curious if anyone has used one and what the limitations are regarding which optimizers it will work on. Appreciate any insights! Sunny Regards, Tyrone Houck Oregon Solarworks LLC LRT 76, CCB 204937 tyroneho...@gmail.com 541-787-1366 ___

Re: [RE-wrenches] Alternate LVD shutdown

2025-01-02 Thread Tyrone Houck via RE-wrenches
Forgive my ignorance but why won't the vfx lbco work for lithium? On Thu, Jan 2, 2025, 8:19 AM Bill Battagin via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > I am trying to use the "low battery disconnect" in aux mode in a newly > installed OB FM80 CC for Li battery low voltage pr

Re: [RE-wrenches] Tigo inverter experience

2025-02-15 Thread Tyrone Houck via RE-wrenches
So funny you say that...I've had several problems with those SMA RSD boxes. Commonly, relays sticking open and requiring replacement.. also few with faults internal to the circuit board. Relatively easy to troubleshoot but still a pain. Anybody had any issues with APSmart? I've been using those la

Re: [RE-wrenches] Issues with HomeGrid

2025-02-11 Thread Tyrone Houck via RE-wrenches
Yep. And the 10 year warranty is only good if connected to the internet. Firmware update of every module is crucial or else there will likely be imbalances. You may be able to address it as 1 and shut of the others and charge it through the bus but if it's cell voltage is too low it may be an rma s

[RE-wrenches] APSmart MLPE

2025-02-14 Thread Tyrone Houck via RE-wrenches
In light of the recent conversations about tigo mlpe's I'm curious what experiences others have had with APSmart. We have a lot of them out there and never had any issues with them that we are aware of though I've often thought how difficult it may be to troubleshoot if there ever were issues. We h

Re: [RE-wrenches] 210.8

2025-03-20 Thread Tyrone Houck via RE-wrenches
That is odd. In my experience that's a very common condition as space in equipment rooms is often in high demand. As long as it's not within the working clearance it should be a non issue. Tyrone Houck Oregon Solarworks LLC CCB #204937 LRT #076 541-787-1366 tyr...@oregonsolarworks.com On Thu, M

Re: [RE-wrenches] Midnite Inverter products, monitoring

2025-03-27 Thread Tyrone Houck via RE-wrenches
ll available > to do remotely. Is that not the case? I assume it requires a Windows laptop > like EG4, HomeGrid, etc. That's something else I don't want to carry in my > truck. I'm a Mac user. > > Jason Szumlanski > Principal Solar Designer | Florida Solar Design Gro

Re: [RE-wrenches] Outback MX60 Replacement

2025-04-18 Thread Tyrone Houck via RE-wrenches
I don't have another recommendation for a 600v charge controller but I can tell you Midnite does make a standard, single space panelmount 125a breaker. Also keep in mind the PV input breaker would have to be 600v rated, also readily available from Midnite.. Tyrone Houck Oregon Solarworks LLC CCB #

Re: [RE-wrenches] Distributors versus manufacturers providing support

2025-04-22 Thread Tyrone Houck via RE-wrenches
Maybe it was timing and I was ahead of the integration curve but Midnite tech support sent my installer account login via email. I agree it seems an odd prospect to get technical support or monitoring access from a sales rep, though I have yet to use eg4 or any other equipment that channels it's te

Re: [RE-wrenches] Converter from 230VAC to 12VDC

2025-04-23 Thread Tyrone Houck via RE-wrenches
Not sure how shipping would work but may make sense to replace the hydro with a new 12v nominal DC hydro and dumpload combo or a rectifier circuit of some kind..Jerry at www.APMhydro.com(based in southern Oregon) is an excellent resource and may have a solution for you. Best of luck! Tyrone Houck

Re: [RE-wrenches] iTools Gear Punch and Midnite AIO

2025-04-29 Thread Tyrone Houck via RE-wrenches
We use the milwaukee cordless 6t k/o tool. It seems to work with most fittings including the MN snap in bushings when knockouts are lined up well. Definitely a tight fit though with bushings and BAs in general. Works great though! On Tue, Apr 29, 2025, 7:03 PM Lou Russo via RE-wrenches < re-wren

[RE-wrenches] Inverter ratings exceeding 25kw fir battery backup

2025-02-17 Thread Tyrone Houck via RE-wrenches
Greetings wrenches, In Pacific Power territory we are coming up against roadblocks with regards to whole house battery backup systems with inverter ratings higher than 25kw. Even when the generation capacity is below the 25kw residential limit, net metering applications are being rejected based on

Re: [RE-wrenches] Inverter ratings exceeding 25kw fir battery backup

2025-02-18 Thread Tyrone Houck via RE-wrenches
Florida Certified Electrical Contractor EC13013208 > > On Mon, Feb 17, 2025 at 12:58 PM Dave Angelini Offgrid Solar via > RE-wrenches wrote: > > Why is there a need for more than 25KW for residential please? Just > curious. In Nevada, 25KW is way into commercial. > > > >

Re: [RE-wrenches] RSS: Is it necessary?

2025-02-18 Thread Tyrone Houck via RE-wrenches
My understanding of code is that all circuits need to be protected from physical damage. It's the same with AC circuits in an unfinished garage..can't have exposed romex under 8' in that scenario either. On Tue, Feb 18, 2025, 8:34 AM Christopher Warfel via RE-wrenches < re-wrenches@lists.re-wren

Re: [RE-wrenches] RSS: Is it necessary?

2025-02-17 Thread Tyrone Houck via RE-wrenches
As far as ground mounted arrays are concerned there is one clear protection mandated by the NEC-the requirement for protection from physical damage for all conductors under 8'.. although this isn't as specific or redundant as rapid shutdown requirements, it typically means conduit or at least some

Re: [RE-wrenches] Inverter ratings exceeding 25kw fir battery backup

2025-02-17 Thread Tyrone Houck via RE-wrenches
<https://offgridsolar1.com/> <http://members.sti.net/offgridsolar/> > e-mail offgridso...@sti.net > text 209 813 0060* > > > On 2025-02-17 9:43 am, Tyrone Houck via RE-wrenches wrote: > > Greetings wrenches, > In Pacific Power territory we are coming up against ro

Re: [RE-wrenches] Popping Sounds From Roof

2025-03-05 Thread Tyrone Houck via RE-wrenches
Screw down metal roofs are notorious for expansion/contraction issues...especially over long horizontal spans. It's possible that the array is actually fixing that section in place better than the rest of the roof(while simultaneously keeping that part of the roof cooler) . I would investigate the

Re: [RE-wrenches] Outback OpticsRE+Starlink redux

2025-02-22 Thread Tyrone Houck via RE-wrenches
Probably goes without saying but definitely worth setting the optics reboot interval short..might help if it's something that hasn't been done On Sat, Feb 22, 2025, 9:17 AM Nick Lucchese via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > About a dozen of my sites are using Starlink t

Re: [RE-wrenches] Outback OpticsRE+Starlink redux

2025-02-23 Thread Tyrone Houck via RE-wrenches
A couple more things that may help are using a higher quality cable than the supplied Outback cables and putting the electrostatic goop on the ends. Again, maybe these are obvious suggestions but they have certainly made a difference in the many Outback systems we have in the field. Over the years

Re: [RE-wrenches] SolarEdge Has Gone Too Far

2025-02-19 Thread Tyrone Houck via RE-wrenches
Anybody got any recommendations for grid tied inverters especially ones that work with APSmart? I'm seeing a serious need for alternatives and not sure if I'm ready to go all in with enphase yet as I still have customers out there who got burnt from their early years and lack of compatability and s

Re: [RE-wrenches] Midnite Inverter products, monitoring

2025-03-27 Thread Tyrone Houck via RE-wrenches
In my experience the communication between battery/inverter has been seamless, the internet connectivity has also been very reliable. You can program settings and monitor remotely. No email notifications. I have only installed the AIO and haven't used the Rosie, Hawkes Bay, or Barcelona..my favorit

[RE-wrenches] Battery monitor for Lifepo4 batteries

2025-06-16 Thread Tyrone Houck via RE-wrenches
Curious what options are available and what people are using for a digital display that shows BMS info via CANbus/rj45. Something that would work with a PYLONtech type battery like the MNPowerflo5 and/or other server rack type LFP battery. I am aware of the solar assistant and it's benefits but loo

Re: [RE-wrenches] Sol-Ark Warranty Support

2025-06-04 Thread Tyrone Houck via RE-wrenches
That's interesting that you say Sol-Ark has been fast and competent in comparison to solaredge... that hasn't been my experience at all. In my dealings Sol-Ark has been responsive only when pressured repeatedly and confidently, required a large deposit for RMAs, reluctant to provide return labels,

Re: [RE-wrenches] Midnite AIO Battery Low/Lost Behavior

2025-07-15 Thread Tyrone Houck via RE-wrenches
That's my understanding as well. Sure would be cool if there was an automatic reconnect mode that could be set. On Tue, Jul 15, 2025, 7:56 AM Jason Szumlanski via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > With this new breed of AIO inverters, when the battery reaches low voltag

Re: [RE-wrenches] Combining two PowerFlo16 to single Midnite AIO

2025-07-16 Thread Tyrone Houck via RE-wrenches
The lynx is awesome too especially with 3 or more batteries or of you need fusingneeds a big enclosure though... I fit one in a 10x10 gutter once but I probably won't do that again as it was pretty tight. On Wed, Jul 16, 2025, 5:19 PM Jason Szumlanski via RE-wrenches < re-wrenches@lists.re-w

Re: [RE-wrenches] Combining two PowerFlo16 to single Midnite AIO

2025-07-16 Thread Tyrone Houck via RE-wrenches
I agree. With one inverter and two batteries just face the lugs toward each other and land on the inverter battery terminals. Nice long posts accommodate that method nicely! On Wed, Jul 16, 2025, 12:52 PM Jason Szumlanski via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > What is th

Re: [RE-wrenches] Knockouts far from the backplane.

2025-07-25 Thread Tyrone Houck via RE-wrenches
At my house(before I got hip to using bigger gutters) I furred out the wall with 2x4s and 1/2" plywood and used a 6" for my AIO...worked nicely. On Fri, Jul 25, 2025, 3:43 PM Zeke Yewdall via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > I noticed this on a SolArk job -- I think I