Here's a link to the dies(U style copper)
https://www.platt.com/p/0010680/milwaukee/8-600-mcm-copper-u-style-die-kit/045242339372/mil4916kitc
And the tool..
https://www.platt.com/p/0010677/milwaukee/600-350-mcm-crimping-tool/045242339488/mil267922
They have a larger one for up to 750mcm and a m
Out of curiosity, what mode are you in and what are the respective set
points for absorb, float, rebulk, etc. For PV vs inverter?
Tyrone Houck
Oregon Solarworks LLC
LRT #076
541-787-1366
tyr...@oregonsolarworks.com
On Fri, Nov 8, 2024, 1:28 PM Chris Sparadeo via RE-wrenches <
re-wrenches@lists
Maybe a silly question but have you tried shutting off all load breakers(ac
output) and charge controller breakers before powering up? I've noticed
radians have a hard time powering up on homegrids if they have a load. If I
have to do a hard reset on a radian I also shutdown the charge controllers
We've noticed a compatability issue with the limitless 15k units and the
newest incarnation of the same(limitless 15k) inverter(additional circuitry
in the wiring compartment associated with the pv inputs is the one way I'm
aware of to tell the difference)..the older units and the newer units don't
>
> On Jan 2, 2025, at 10:04 AM, Tyrone Houck via RE-wrenches <
> re-wrenches@lists.re-wrenches.org> wrote:
>
>
> Forgive my ignorance but why won't the vfx lbco work for lithium?
>
>
>
>
> On Thu, Jan 2, 2025, 8:19 AM Bill Battagin via RE-wrenches <
&g
Can the mate3SL not use the mate3S firmware? Is there a reason to need a
version other than 001.004.007? Or am I misunderstanding your post?
Tyrone Houck
Oregon Solarworks LLC
CCB #204937 LRT #076
541-787-1366
tyr...@oregonsolarworks.com
On Mon, Feb 3, 2025, 12:50 PM Nick Lucchese via RE-wrenche
I think the answer is using a flexnet DC's aux relay terminal to control
the on/off switch terminals of the FX inverter. You'll need a mate3S/SL but
that should do it without having to change the inverter...
On Sun, Feb 2, 2025, 8:52 PM Bill Battagin via RE-wrenches <
re-wrenches@lists.re-wrenc
less for supporting a client effectively
> especially for most off grid sites that tend to be off the beaten path.
>
> Nick
>
> On Mon, Feb 3, 2025 at 5:52 PM Tyrone Houck via RE-wrenches <
> re-wrenches@lists.re-wrenches.org> wrote:
>
>> Can the mate3SL not use the mate3
Greetings wrenches,
We recently replaced an Outback Fx system with a MN15-12K-AIO and are
trying to figure out how to convert the exiting winco genetic from a relay
driven 12v auto start to a 2 wire dry contact start. Their tech support is
a pain to get ahold of and I figured there are probably fol
Any further investigation into the hardware differences between the newer
15k and the original 15k I mentioned before? That was the only thing that
fixed the issue for us. We had to insist they replaced it with a newer
matching inverter. I should have made note of the serial numbers to try to
narro
Around that time there were some issues with solaredge
equipment..specifically bad optimizers the SE tech support affectionately
dubbed "sleepy optimizers". We had one job from that production run that we
replaced several of the optimizers on.. in general though we've had great
luck with solaredge
She wants ZERO risk of
> fire? She needs to live in a concrete bunker with no electricity at all.
> Every electrical connection, every outlet, every appliance has a risk of
> fire. Period.
>
> Ray Walters
> Remote Solar
> On 1/12/2025 9:39 AM, Tyrone Houck via RE-wrenches wrote:
I hate to be the one to say it but LFP has arguably less fire risk than
agm. A short circuit in an agm could be disastrous and AGM is not
necessarily any safer or less prone to thermal runaway events than modern
LFP. I'd recommend a cobalt free LFP like homegrid, simpliphi, or midnite
if it were me
;
> I know there will be million reasons to not do this...
>
>
> --
> *From:* RE-wrenches on behalf
> of Tyrone Houck via RE-wrenches
> *Sent:* Friday, January 17, 2025 9:01 AM
> *To:* RE-wrenches
> *Cc:* Tyrone Houck
> *Subject:* [RE-wr
Thinking of ordering one from the UK. Curious if anyone has used one and
what the limitations are regarding which optimizers it will work on.
Appreciate any insights!
Sunny Regards,
Tyrone Houck
Oregon Solarworks LLC
LRT 76, CCB 204937
tyroneho...@gmail.com
541-787-1366
___
Forgive my ignorance but why won't the vfx lbco work for lithium?
On Thu, Jan 2, 2025, 8:19 AM Bill Battagin via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> I am trying to use the "low battery disconnect" in aux mode in a newly
> installed OB FM80 CC for Li battery low voltage pr
So funny you say that...I've had several problems with those SMA RSD boxes.
Commonly, relays sticking open and requiring replacement.. also few with
faults internal to the circuit board. Relatively easy to troubleshoot but
still a pain.
Anybody had any issues with APSmart? I've been using those la
Yep. And the 10 year warranty is only good if connected to the internet.
Firmware update of every module is crucial or else there will likely be
imbalances. You may be able to address it as 1 and shut of the others and
charge it through the bus but if it's cell voltage is too low it may be an
rma s
In light of the recent conversations about tigo mlpe's I'm curious what
experiences others have had with APSmart. We have a lot of them out there
and never had any issues with them that we are aware of though I've often
thought how difficult it may be to troubleshoot if there ever were issues.
We h
That is odd. In my experience that's a very common condition as space in
equipment rooms is often in high demand. As long as it's not within the
working clearance it should be a non issue.
Tyrone Houck
Oregon Solarworks LLC
CCB #204937 LRT #076
541-787-1366
tyr...@oregonsolarworks.com
On Thu, M
ll available
> to do remotely. Is that not the case? I assume it requires a Windows laptop
> like EG4, HomeGrid, etc. That's something else I don't want to carry in my
> truck. I'm a Mac user.
>
> Jason Szumlanski
> Principal Solar Designer | Florida Solar Design Gro
I don't have another recommendation for a 600v charge controller but I can
tell you Midnite does make a standard, single space panelmount 125a
breaker. Also keep in mind the PV input breaker would have to be 600v
rated, also readily available from Midnite..
Tyrone Houck
Oregon Solarworks LLC
CCB #
Maybe it was timing and I was ahead of the integration curve but Midnite
tech support sent my installer account login via email. I agree it seems an
odd prospect to get technical support or monitoring access from a sales
rep, though I have yet to use eg4 or any other equipment that channels it's
te
Not sure how shipping would work but may make sense to replace the hydro
with a new 12v nominal DC hydro and dumpload combo or a rectifier circuit
of some kind..Jerry at www.APMhydro.com(based in southern Oregon) is an
excellent resource and may have a solution for you. Best of luck!
Tyrone Houck
We use the milwaukee cordless 6t k/o tool. It seems to work with most
fittings including the MN snap in bushings when knockouts are lined up
well. Definitely a tight fit though with bushings and BAs in general. Works
great though!
On Tue, Apr 29, 2025, 7:03 PM Lou Russo via RE-wrenches <
re-wren
Greetings wrenches,
In Pacific Power territory we are coming up against roadblocks with regards
to whole house battery backup systems with inverter ratings higher than
25kw. Even when the generation capacity is below the 25kw residential
limit, net metering applications are being rejected based on
Florida Certified Electrical Contractor EC13013208
>
> On Mon, Feb 17, 2025 at 12:58 PM Dave Angelini Offgrid Solar via
> RE-wrenches wrote:
>
> Why is there a need for more than 25KW for residential please? Just
> curious. In Nevada, 25KW is way into commercial.
>
>
>
>
My understanding of code is that all circuits need to be protected from
physical damage. It's the same with AC circuits in an unfinished
garage..can't have exposed romex under 8' in that scenario either.
On Tue, Feb 18, 2025, 8:34 AM Christopher Warfel via RE-wrenches <
re-wrenches@lists.re-wren
As far as ground mounted arrays are concerned there is one clear protection
mandated by the NEC-the requirement for protection from physical damage for
all conductors under 8'.. although this isn't as specific or redundant as
rapid shutdown requirements, it typically means conduit or at least some
<https://offgridsolar1.com/> <http://members.sti.net/offgridsolar/>
> e-mail offgridso...@sti.net
> text 209 813 0060*
>
>
> On 2025-02-17 9:43 am, Tyrone Houck via RE-wrenches wrote:
>
> Greetings wrenches,
> In Pacific Power territory we are coming up against ro
Screw down metal roofs are notorious for expansion/contraction
issues...especially over long horizontal spans. It's possible that the
array is actually fixing that section in place better than the rest of the
roof(while simultaneously keeping that part of the roof cooler) . I would
investigate the
Probably goes without saying but definitely worth setting the optics reboot
interval short..might help if it's something that hasn't been done
On Sat, Feb 22, 2025, 9:17 AM Nick Lucchese via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> About a dozen of my sites are using Starlink t
A couple more things that may help are using a higher quality cable than
the supplied Outback cables and putting the electrostatic goop on the
ends. Again, maybe these are obvious suggestions but they have certainly
made a difference in the many Outback systems we have in the field. Over
the years
Anybody got any recommendations for grid tied inverters especially ones
that work with APSmart? I'm seeing a serious need for alternatives and not
sure if I'm ready to go all in with enphase yet as I still have customers
out there who got burnt from their early years and lack of compatability
and s
In my experience the communication between battery/inverter has been
seamless, the internet connectivity has also been very reliable. You can
program settings and monitor remotely. No email notifications. I have only
installed the AIO and haven't used the Rosie, Hawkes Bay, or Barcelona..my
favorit
Curious what options are available and what people are using for a digital
display that shows BMS info via CANbus/rj45. Something that would work with
a PYLONtech type battery like the MNPowerflo5 and/or other server rack type
LFP battery. I am aware of the solar assistant and it's benefits but
loo
That's interesting that you say Sol-Ark has been fast and competent in
comparison to solaredge... that hasn't been my experience at all. In my
dealings Sol-Ark has been responsive only when pressured repeatedly and
confidently, required a large deposit for RMAs, reluctant to provide return
labels,
That's my understanding as well. Sure would be cool if there was an
automatic reconnect mode that could be set.
On Tue, Jul 15, 2025, 7:56 AM Jason Szumlanski via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> With this new breed of AIO inverters, when the battery reaches low voltag
The lynx is awesome too especially with 3 or more batteries or of you need
fusingneeds a big enclosure though... I fit one in a 10x10 gutter once
but I probably won't do that again as it was pretty tight.
On Wed, Jul 16, 2025, 5:19 PM Jason Szumlanski via RE-wrenches <
re-wrenches@lists.re-w
I agree. With one inverter and two batteries just face the lugs toward each
other and land on the inverter battery terminals. Nice long posts
accommodate that method nicely!
On Wed, Jul 16, 2025, 12:52 PM Jason Szumlanski via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> What is th
At my house(before I got hip to using bigger gutters) I furred out the wall
with 2x4s and 1/2" plywood and used a 6" for my AIO...worked nicely.
On Fri, Jul 25, 2025, 3:43 PM Zeke Yewdall via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> I noticed this on a SolArk job -- I think I