I am wondering if anyone has had a NABCEP stamp made to stamp plans. I have a
city agency who is comfortable with the NABCEP certification as a
qualification, but would like to see a stamp. Has anyone out there done this?
Troy
___
List sponsored by H
> I think that Bill has summed it up very well. Stamps on plans generally imply
> the review of a duly recognized engineer. NABCEP Certification is not an
> equivalency to being a PE.
Confusion with an engineer is my main concern (although I'm a EE, like most not
a PE).
However there are a lot
Either way both are just tests, and both are just there solely for the
formality of AHJ.
I've done enough hiring of engineers to be thoroughly unconvinced any testing,
certification, GPA, degree level makes any indication of level of ability. I
remember a time a few years back when i hired a 2n
That's exactly the process. Not surprising since they are a german
company. Anybody have the Schuco install reference materials?
Troy Harvey
-
Heliocentric
801-453-9434
tahar...@heliocentric.org
On Apr 23, 2009, at 1:53 PM, Tump wrote:
Review Schuco panels they
6000 Watt inverter at any given time. So would like to have
the system intelligently remove less important breakers until the
system is below the inverter operation wattage.
Anyone know of a inverter system that is smart like that?
Troy Harvey
-
Heliocentric
801-453-
really had the
feature either).
Troy Harvey
-
Heliocentric
801-453-9434
tahar...@heliocentric.org
On Jun 23, 2009, at 9:31 PM, David Palumbo wrote:
esigned and installed grid connected net metered PV systems with
battery back up for grid outages using OutBack, Xantrex and
ch more than 50 AMPs for the whole house at any one time.
How do you select what is important? Either the inverter is
complicated or the electricians wiring is complicated.
Troy Harvey
-
Heliocentric
801-453-9434
tahar...@heliocentric.org
On Jun 23, 2009, at 10:01 PM,
I am being told we need rooftop DC disconnects for a 6 string
commercial solar install, instead of DC disconnects in the mech room.
I don't see anything about this in the NEC. Any truth to this?
thanks
Troy Harvey
-
Heliocentric
801-453-9434
tahar...@heliocentri
causing flicker.
Has anyone dealt with this issue successfully (other than switching to
incandescent lights)? Would a static capacitor bank at the house do the trick,
or do we need some type of active PFC? And if static did you have any issues
with constant power draw from the capacitors?
ith the LED dimmer circuits which are already doing a bit of magic to
turn TRIAC waveforms into a DC constant current.
thanks,
Troy Harvey
-
Principal Engineer
Heliocentric
801-453-9434
tahar...@heliocentric.org
On Feb 3, 2014, at 8:33 AM, Richard L Ratico
wrote:
&
Thanks for your suggestions. I wanted to get ideas before heading out the site
since it is 4 hours away and in the middle of nowhere with no local resources!
I'll followup once I go visit.
thanks,
Troy Harvey
-
Principal Engineer
Heliocentric
801-453-9434
own good?
Also would you say that the 120% is based on the inverter max output or
backfeed breaker size?
thanks,
Troy Harvey
-
Principal Engineer
Heliocentric
801-453-9434
tahar...@heliocentric.org
___
List sponsored by Home
d be that associated with 300
> amps, not the
> 200 amps the panel was designed and listed for. Panel manufacturers have
> stated that
> these panels cannot pass UL listing tests with those excessive thermal loads.
>
> On 2014/3/27, 14:34, Troy Harvey wrote:
>> I am won
work on these days is over 120%.
So how is everyone else dealing with this?
thanks,
Troy Harvey
On Mar 28, 2014, at 8:38 PM, Bill Brooks wrote:
> Dave and Troy,
>
> I don’t think JW had his facts correct on this. The standard test for a
> busbar is to place the highest allowa
but I personally don't see the
proven value, other than the "appearance" of code defensibility. Anybody have
proof?
thanks,
Troy Harvey
-
Principal Engineer
Heliocentric
801-453-9434
tahar...@heliocentric.org
___
Li
Glenn, I understand where you are coming from, However
My concern is that flashings could be worse. Unless the flashing design
supports sealant + flashing, it will most likely be worse. I've never seen a
L-foot leak, but I've seem many flashings that rely on gravity leak. An L-foot
sealed w
s are thousands of times more durable than the
inverters.
What is your experience?
thanks,
Troy Harvey
-
Principal Engineer
Heliocentric
801-453-9434
tahar...@heliocentric.org
___
List sponsored by Home Power magazine
List Addres
Your experience?
thanks,
Troy Harvey
-
Principal Engineer
Heliocentric
801-453-9434
tahar...@heliocentric.org
___
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Options & settings:
http:/
Ray, we engineer every system using the ASCE structural load manual. Roof snow
load has to be below 113 SQFT (for high snow load modules) after taking the
ASCE slippery surface reductions based on slope.
thanks,
Troy Harvey
-
Principal Engineer
Heliocentric
801-453-9434
that some shingles
out there are just not that good. When facing 100 feet in a residential
install, the chances of ripping shingles in my mind needs to be balanced with
the benefits... I am not all that certain of which is really higher risk.
thanks,
Troy Harvey
-
Principal
always goes downhill, right? Well not always, in ice dams, water often goes
uphill. There is a real question as to whether a modern sealant system is
better or worse than a flashing. I'd like to see data.
thanks,
Troy Harvey
-
Principal Engineer
Heliocentric
801-453-9434
come across?
thanks,
Troy Harvey
-
Principal Engineer
Heliocentric
801-453-9434
tahar...@heliocentric.org
___
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Change email address & setti
The zilla flashing looks perfect. Thanks!
thanks,
Troy Harvey
-
Principal Engineer
Heliocentric
801-453-9434
tahar...@heliocentric.org
On Mar 25, 2013, at 1:37 PM, Aaron Mandelkorn wrote:
> I believe that Zilla and Quick Mount makes flashed options for conduit en
, the wire will be under-protected for its ampacity rating. Any
thoughts on the catch-22?
thanks,
Troy Harvey
-
Principal Engineer
Heliocentric
801-453-9434
tahar...@heliocentric.org
___
List sponsored by Home Power magazine
Li
Allan,
that is a good graph. Thanks. The time vs current is way different than whst
I've seen from fuse charts in the past.
I'd rather use DC-breakers, but I'm having trouble finding 350AMP DC breakers
for 350MCM cable. Any resources?
thanks,
Troy Harvey
Ray,
One thing I didn't understand is how you can pair a 400 amp class-T fuse with a
4/0 cable. The 400 fuse curve looks like the continuous rating is 350A in the
graph supplied by Allan. Which is well above the 4/0 ampacity of 250A (copper).
Anyone want to explain?
thanks,
Troy H
look like it is
still around.
thanks,
Troy Harvey
-
Principal Engineer
Heliocentric
801-453-9434
tahar...@heliocentric.org
___
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Change email add
en have big consumption. And really if they are going near
net-zero, we should only commend them.
thanks,
Troy Harvey
-
Principal Engineer
Heliocentric
801-453-9434
tahar...@heliocentric.org___
List sponsored by Home Power magazine
L
a module that has a 5 or 6-sigma reliability,
with an inverter that has a 1 or 2-sigma reliability.
thanks,
Troy Harvey
-
Principal Engineer
Heliocentric
801-453-9434
tahar...@heliocentric.org
___
List sponsored by Home Power ma
rray just to
get at the micro inverter. Then I have to put the array back together. Its an
all day activity for two people for 1 inverter. And then I have to do it on the
same array the next year again. With a string inverter the swap is simple.
thanks,
Troy Harvey
-
P
a
micro to have a higher MTBF is believable. But first they need better design,
more market experience, and will never reach 25 year lifespan like they say
until they take electrolytic caps out of their designs.
thanks,
Troy Harvey
-
Principal Engineer
Helioc
> Why would you "rip apart an array?" We only remove one module in almost every
> case, replace the WEEBs, replace the inverter, and we're done. If there are
> more than two rows of modules, you might need to remove an additional module
> or two, but that takes almost no time. Our steepest roof
All of my enphase failure are in the desert (Utah)
We have had Power-one units in the field for 5 or 6 years.
- Troy Harvey
On May 9, 2013, at 10:28 AM, August Goers wrote:
> This is fascinating - the majority of the Enphase failures reported on this
> list seem to be near coastal
urvey of failure rates by manufacturer,
like these for canadian solar and Yingli:
http://www.warrantyweek.com/archive/ww20111208.html
(notice they do creep up a bit around 2009, Yingli doesn't look as good as CSI)
Troy Harvey
-
Principal Engineer
Heliocentric
801-453-
Any thoughts on how to flash a copper pipe roof penetration on a metal
roof. The brazed copper flashing we typically use would cause
corrosion with the steel roof I'm afraid. WHat have others used in
this situation?
Troy Harvey
-
Heliocentric
801-453-9434
[
e tax credits? Any other creative finance mechanisms through a
solar investment bank that can take the credits?
Troy Harvey
-
Heliocentric
801-453-9434
tahar...@heliocentric.org
___
List sponsored by Home Power magazine
List Addres
seal to the metal roof.
Troy Harvey
-
Heliocentric
801-453-9434
tahar...@heliocentric.org
On Feb 5, 2009, at 10:14 PM, Greg Egan wrote:
Jeff, Joel, William and all,
Thanks for all the input. I think the general consensus is that
giving out wholesale price information is
could cause buckling at the seams, and thus leak?
Troy Harvey
-
Heliocentric
801-453-9434
tahar...@heliocentric.org
On Feb 6, 2009, at 11:22 AM, Matt Tritt wrote:
It is my current understanding that some manufacturers of metal
roofing will not warranty their produc
at we did was mount the
inverter on two inverted L-feet. Worked really nicely, no tolerance
problems.
Troy Harvey
-
Heliocentric
801-453-9434
tahar...@heliocentric.org
___
List sponsored by Home Power magazine
List Addres
roblems with thermal expansion and mounting feet
lagged through the roofing pan?
Troy Harvey
-
Heliocentric
801-453-9434
tahar...@heliocentric.org
___
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-w
of by the force of the screws.
But, yes it makes me nervous to cut a roof
Troy Harvey
-
Heliocentric
801-453-9434
tahar...@heliocentric.org
On Feb 7, 2009, at 3:09 PM, William Miller wrote:
Troy:
How are you planning on attaching the rubber boot to the roof
sheeting?
to a heat dump. Does anyone have experience with
this?
Troy Harvey
-
Heliocentric
801-453-9434
tahar...@heliocentric.org
___
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Options &
d drainback" in over heating conditions.
Here is a couple of links:
http://www.aee-intec.at/0uploads/dateien48.pdf
http://www.suterconsulting.com/CISBAT.pdf
I'm hoping to find someone with experience with this kind of system to
overcome my fears
Troy Harvey
-