[RE-wrenches] NABCEP Stamp

2011-03-30 Thread Troy Harvey
I am wondering if anyone has had a NABCEP stamp made to stamp plans. I have a city agency who is comfortable with the NABCEP certification as a qualification, but would like to see a stamp. Has anyone out there done this? Troy ___ List sponsored by H

Re: [RE-wrenches] Forward re: NABCEP Stamp

2011-03-31 Thread Troy Harvey
> I think that Bill has summed it up very well. Stamps on plans generally imply > the review of a duly recognized engineer. NABCEP Certification is not an > equivalency to being a PE. Confusion with an engineer is my main concern (although I'm a EE, like most not a PE). However there are a lot

Re: [RE-wrenches] Nabcep Stamp

2011-03-31 Thread Troy Harvey
Either way both are just tests, and both are just there solely for the formality of AHJ. I've done enough hiring of engineers to be thoroughly unconvinced any testing, certification, GPA, degree level makes any indication of level of ability. I remember a time a few years back when i hired a 2n

Re: [RE-wrenches] Solar Combi-systems: Heat dump or Stagnate?

2009-04-23 Thread Troy Harvey
That's exactly the process. Not surprising since they are a german company. Anybody have the Schuco install reference materials? Troy Harvey - Heliocentric 801-453-9434 tahar...@heliocentric.org On Apr 23, 2009, at 1:53 PM, Tump wrote: Review Schuco panels they

[RE-wrenches] Grid-Connect Inverter with battery, AND auto backoff?

2009-06-23 Thread Troy Harvey
6000 Watt inverter at any given time. So would like to have the system intelligently remove less important breakers until the system is below the inverter operation wattage. Anyone know of a inverter system that is smart like that? Troy Harvey - Heliocentric 801-453-

Re: [RE-wrenches] Grid-Connect Inverter with battery, AND auto backoff?

2009-06-23 Thread Troy Harvey
really had the feature either). Troy Harvey - Heliocentric 801-453-9434 tahar...@heliocentric.org On Jun 23, 2009, at 9:31 PM, David Palumbo wrote: esigned and installed grid connected net metered PV systems with battery back up for grid outages using OutBack, Xantrex and

Re: [RE-wrenches] Grid-Connect Inverter with battery, AND auto backoff?

2009-06-23 Thread Troy Harvey
ch more than 50 AMPs for the whole house at any one time. How do you select what is important? Either the inverter is complicated or the electricians wiring is complicated. Troy Harvey - Heliocentric 801-453-9434 tahar...@heliocentric.org On Jun 23, 2009, at 10:01 PM,

[RE-wrenches] Rooftop DC disconnects

2009-09-22 Thread Troy Harvey
I am being told we need rooftop DC disconnects for a 6 string commercial solar install, instead of DC disconnects in the mech room. I don't see anything about this in the NEC. Any truth to this? thanks Troy Harvey - Heliocentric 801-453-9434 tahar...@heliocentri

[RE-wrenches] Long transmission line inductance and LED light flicker

2014-02-02 Thread Troy Harvey
causing flicker. Has anyone dealt with this issue successfully (other than switching to incandescent lights)? Would a static capacitor bank at the house do the trick, or do we need some type of active PFC? And if static did you have any issues with constant power draw from the capacitors?

Re: [RE-wrenches] Long transmission line inductance and LED light flicker

2014-02-11 Thread Troy Harvey
ith the LED dimmer circuits which are already doing a bit of magic to turn TRIAC waveforms into a DC constant current. thanks, Troy Harvey - Principal Engineer Heliocentric 801-453-9434 tahar...@heliocentric.org On Feb 3, 2014, at 8:33 AM, Richard L Ratico wrote: &

Re: [RE-wrenches] Long transmission line inductance and LED light flicker

2014-02-12 Thread Troy Harvey
Thanks for your suggestions. I wanted to get ideas before heading out the site since it is 4 hours away and in the middle of nowhere with no local resources! I'll followup once I go visit. thanks, Troy Harvey - Principal Engineer Heliocentric 801-453-9434

[RE-wrenches] Busbar 120% rule

2014-03-27 Thread Troy Harvey
own good? Also would you say that the 120% is based on the inverter max output or backfeed breaker size? thanks, Troy Harvey - Principal Engineer Heliocentric 801-453-9434 tahar...@heliocentric.org ___ List sponsored by Home

Re: [RE-wrenches] Busbar 120% rule

2014-03-28 Thread Troy Harvey
d be that associated with 300 > amps, not the > 200 amps the panel was designed and listed for. Panel manufacturers have > stated that > these panels cannot pass UL listing tests with those excessive thermal loads. > > On 2014/3/27, 14:34, Troy Harvey wrote: >> I am won

Re: [RE-wrenches] Busbar 120% rule

2014-04-02 Thread Troy Harvey
work on these days is over 120%. So how is everyone else dealing with this? thanks, Troy Harvey On Mar 28, 2014, at 8:38 PM, Bill Brooks wrote: > Dave and Troy, > > I don’t think JW had his facts correct on this. The standard test for a > busbar is to place the highest allowa

[RE-wrenches] Flashing vs Sealant... again (is sealant code defensible?)

2014-04-11 Thread Troy Harvey
but I personally don't see the proven value, other than the "appearance" of code defensibility. Anybody have proof? thanks, Troy Harvey - Principal Engineer Heliocentric 801-453-9434 tahar...@heliocentric.org ___ Li

Re: [RE-wrenches] Flashing vs Sealant... again (is sealant code defensible?)

2014-04-14 Thread Troy Harvey
Glenn, I understand where you are coming from, However My concern is that flashings could be worse. Unless the flashing design supports sealant + flashing, it will most likely be worse. I've never seen a L-foot leak, but I've seem many flashings that rely on gravity leak. An L-foot sealed w

[RE-wrenches] Enphase failures

2012-07-05 Thread Troy Harvey
s are thousands of times more durable than the inverters. What is your experience? thanks, Troy Harvey - Principal Engineer Heliocentric 801-453-9434 tahar...@heliocentric.org ___ List sponsored by Home Power magazine List Addres

[RE-wrenches] Roof flashings on L-feet in high snow load conditions

2012-11-13 Thread Troy Harvey
Your experience? thanks, Troy Harvey - Principal Engineer Heliocentric 801-453-9434 tahar...@heliocentric.org ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options & settings: http:/

Re: [RE-wrenches] Roof flashings on L-feet in high snow load conditions

2012-11-14 Thread Troy Harvey
Ray, we engineer every system using the ASCE structural load manual. Roof snow load has to be below 113 SQFT (for high snow load modules) after taking the ASCE slippery surface reductions based on slope. thanks, Troy Harvey - Principal Engineer Heliocentric 801-453-9434

Re: [RE-wrenches] Roof flashings on L-feet in high snow load conditions

2012-11-14 Thread Troy Harvey
that some shingles out there are just not that good. When facing 100 feet in a residential install, the chances of ripping shingles in my mind needs to be balanced with the benefits... I am not all that certain of which is really higher risk. thanks, Troy Harvey - Principal

Re: [RE-wrenches] Roof flashings on L-feet in high snow load conditions

2012-11-14 Thread Troy Harvey
always goes downhill, right? Well not always, in ice dams, water often goes uphill. There is a real question as to whether a modern sealant system is better or worse than a flashing. I'd like to see data. thanks, Troy Harvey - Principal Engineer Heliocentric 801-453-9434

[RE-wrenches] Soladeck Alternatives

2013-03-25 Thread Troy Harvey
come across? thanks, Troy Harvey - Principal Engineer Heliocentric 801-453-9434 tahar...@heliocentric.org ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Change email address & setti

Re: [RE-wrenches] Soladeck Alternatives

2013-03-25 Thread Troy Harvey
The zilla flashing looks perfect. Thanks! thanks, Troy Harvey - Principal Engineer Heliocentric 801-453-9434 tahar...@heliocentric.org On Mar 25, 2013, at 1:37 PM, Aaron Mandelkorn wrote: > I believe that Zilla and Quick Mount makes flashed options for conduit en

[RE-wrenches] Fuse sizing in battery circuits

2013-04-05 Thread Troy Harvey
, the wire will be under-protected for its ampacity rating. Any thoughts on the catch-22? thanks, Troy Harvey - Principal Engineer Heliocentric 801-453-9434 tahar...@heliocentric.org ___ List sponsored by Home Power magazine Li

Re: [RE-wrenches] Fuse sizing in battery circuits

2013-04-07 Thread Troy Harvey
Allan, that is a good graph. Thanks. The time vs current is way different than whst I've seen from fuse charts in the past. I'd rather use DC-breakers, but I'm having trouble finding 350AMP DC breakers for 350MCM cable. Any resources? thanks, Troy Harvey

Re: [RE-wrenches] Fuse sizing in battery circuits

2013-04-22 Thread Troy Harvey
Ray, One thing I didn't understand is how you can pair a 400 amp class-T fuse with a 4/0 cable. The 400 fuse curve looks like the continuous rating is 350A in the graph supplied by Allan. Which is well above the 4/0 ampacity of 250A (copper). Anyone want to explain? thanks, Troy H

[RE-wrenches] Dual Channel Inverters

2013-05-07 Thread Troy Harvey
look like it is still around. thanks, Troy Harvey - Principal Engineer Heliocentric 801-453-9434 tahar...@heliocentric.org ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Change email add

Re: [RE-wrenches] Dual Channel Inverters

2013-05-07 Thread Troy Harvey
en have big consumption. And really if they are going near net-zero, we should only commend them. thanks, Troy Harvey - Principal Engineer Heliocentric 801-453-9434 tahar...@heliocentric.org___ List sponsored by Home Power magazine L

Re: [RE-wrenches] Dual Channel Inverters

2013-05-07 Thread Troy Harvey
a module that has a 5 or 6-sigma reliability, with an inverter that has a 1 or 2-sigma reliability. thanks, Troy Harvey - Principal Engineer Heliocentric 801-453-9434 tahar...@heliocentric.org ___ List sponsored by Home Power ma

Re: [RE-wrenches] Dual Channel Inverters; Hosed By Fronius

2013-05-09 Thread Troy Harvey
rray just to get at the micro inverter. Then I have to put the array back together. Its an all day activity for two people for 1 inverter. And then I have to do it on the same array the next year again. With a string inverter the swap is simple. thanks, Troy Harvey - P

Re: [RE-wrenches] Enphase / Inverter failures

2013-05-09 Thread Troy Harvey
a micro to have a higher MTBF is believable. But first they need better design, more market experience, and will never reach 25 year lifespan like they say until they take electrolytic caps out of their designs. thanks, Troy Harvey - Principal Engineer Helioc

Re: [RE-wrenches] Dual Channel Inverters; Hosed By Fronius

2013-05-09 Thread Troy Harvey
> Why would you "rip apart an array?" We only remove one module in almost every > case, replace the WEEBs, replace the inverter, and we're done. If there are > more than two rows of modules, you might need to remove an additional module > or two, but that takes almost no time. Our steepest roof

Re: [RE-wrenches] Enphase / Inverter failures

2013-05-09 Thread Troy Harvey
All of my enphase failure are in the desert (Utah) We have had Power-one units in the field for 5 or 6 years. - Troy Harvey On May 9, 2013, at 10:28 AM, August Goers wrote: > This is fascinating - the majority of the Enphase failures reported on this > list seem to be near coastal

Re: [RE-wrenches] Defective modules-Chinese crap?

2013-05-30 Thread Troy Harvey
urvey of failure rates by manufacturer, like these for canadian solar and Yingli: http://www.warrantyweek.com/archive/ww20111208.html (notice they do creep up a bit around 2009, Yingli doesn't look as good as CSI) Troy Harvey - Principal Engineer Heliocentric 801-453-

[RE-wrenches] solar hot water penetration flashing

2008-12-10 Thread troy Harvey
Any thoughts on how to flash a copper pipe roof penetration on a metal roof. The brazed copper flashing we typically use would cause corrosion with the steel roof I'm afraid. WHat have others used in this situation? Troy Harvey - Heliocentric 801-453-9434 [

[RE-wrenches] Trading federal tax credits?

2009-01-23 Thread troy Harvey
e tax credits? Any other creative finance mechanisms through a solar investment bank that can take the credits? Troy Harvey - Heliocentric 801-453-9434 tahar...@heliocentric.org ___ List sponsored by Home Power magazine List Addres

[RE-wrenches] Mounting to metal roofs and thermal expansion

2009-02-05 Thread Troy Harvey
seal to the metal roof. Troy Harvey - Heliocentric 801-453-9434 tahar...@heliocentric.org On Feb 5, 2009, at 10:14 PM, Greg Egan wrote: Jeff, Joel, William and all, Thanks for all the input. I think the general consensus is that giving out wholesale price information is

Re: [RE-wrenches] Mounting to metal roofs and thermal expansion

2009-02-06 Thread Troy Harvey
could cause buckling at the seams, and thus leak? Troy Harvey - Heliocentric 801-453-9434 tahar...@heliocentric.org On Feb 6, 2009, at 11:22 AM, Matt Tritt wrote: It is my current understanding that some manufacturers of metal roofing will not warranty their produc

Re: [RE-wrenches] Enphase Micro Inverter Energy System

2009-02-06 Thread Troy Harvey
at we did was mount the inverter on two inverted L-feet. Worked really nicely, no tolerance problems. Troy Harvey - Heliocentric 801-453-9434 tahar...@heliocentric.org ___ List sponsored by Home Power magazine List Addres

Re: [RE-wrenches] Mounting to metal roofs and thermal expansion

2009-02-07 Thread Troy Harvey
roblems with thermal expansion and mounting feet lagged through the roofing pan? Troy Harvey - Heliocentric 801-453-9434 tahar...@heliocentric.org ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-w

Re: [RE-wrenches] Mounting to metal roofs and thermal expansion

2009-02-07 Thread Troy Harvey
of by the force of the screws. But, yes it makes me nervous to cut a roof Troy Harvey - Heliocentric 801-453-9434 tahar...@heliocentric.org On Feb 7, 2009, at 3:09 PM, William Miller wrote: Troy: How are you planning on attaching the rubber boot to the roof sheeting?

[RE-wrenches] Solar Combi-systems: Heat dump or Stagnate?

2009-04-23 Thread Troy Harvey
to a heat dump. Does anyone have experience with this? Troy Harvey - Heliocentric 801-453-9434 tahar...@heliocentric.org ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options &

Re: [RE-wrenches] Heat dump or Stagnate?

2009-04-23 Thread Troy Harvey
d drainback" in over heating conditions. Here is a couple of links: http://www.aee-intec.at/0uploads/dateien48.pdf http://www.suterconsulting.com/CISBAT.pdf I'm hoping to find someone with experience with this kind of system to overcome my fears Troy Harvey -