Re: [RE-wrenches] High Voltage MPPT units

2011-11-07 Thread Ray Walters
osses. Are there site specific conditions driving this that I'm not understanding? I've done quite a few GT systems w/ battery backup, so I'm always up for new ideas though. Ray On 11/7/2011 12:15 PM, Larry Crutcher, Starlight Solar Power Systems wrote: Hi Glen, That model is

Re: [RE-wrenches] Faulty PM-60 circuit board

2011-11-08 Thread Ray Walters
Rewiring the array for higher voltage gives the MPPT more range to play with, in addition to cutting the wire losses by half. Sometimes with older modules close to the battery voltage, the controller will operate the array below max power point, and not really see any boost. Ray On 11/7/2011

Re: [RE-wrenches] What inverter? (was Faulty PM-60 circuit board)

2011-11-09 Thread Ray Walters
He doesn't want battery backup? Ray On 11/9/2011 10:33 AM, Joel Davidson wrote: Wrenches, After telling my customer to upgrade to an MPPT charge controller (thanks Ray Walters and John Blittersdorf), he decided to really optimize his PV array and retire his Trace SW4048 inverter. He h

Re: [RE-wrenches] 90 degree wire bends

2011-11-16 Thread Ray Walters
;ve had to stop more than one journeyman from violating 300.34. I just tell them the bends should look like the long sweeps in conduit relative to the diameter of the wire: also purdy. Aloha, Ray On 11/16/2011 10:35 AM, Marco Mangelsdorf wrote: Some electricians have great fun in making 90

Re: [RE-wrenches] 3-phase wire run considerations

2011-11-17 Thread Ray Walters
wire will only encourage low voltage shut downs (<211 @ inverter). Ray Walters On 11/16/2011 10:49 PM, William Miller wrote: Luke: Maximum inverter output will occur rarely. Most of the time the inverter(s) will be running at lesser output amps. One approach is to size wiring for a cer

Re: [RE-wrenches] Convert Grid Tie SW4048 to Backup System; Add New Inverter, AC Coupled

2011-11-17 Thread Ray Walters
working for 30 years..." is great for the solar industry as a whole, but only if it makes sense. Ray On 11/17/2011 5:51 PM, jay peltz wrote: HI Richard, I'll chime in, although you won't like it. Dump the system and start over with a new battery less system and a genny as

Re: [RE-wrenches] 90 degree wire bends

2011-11-18 Thread Ray Walters
Was that on the hots or neutral? It's possible that might have been lightning too. I've heard of lightning using the pump wiring to get to the very well grounded well water. Ray On 11/18/2011 1:47 PM, Nik Ponzio wrote: I had an off-grid customer report that their huge well pump sur

Re: [RE-wrenches] Code reviewer issue with array disconnect location

2011-11-21 Thread Ray Walters
crawl around on the roof with a map trying to find every combiner. I think its the way we need to be moving for safety on all PV systems, it also would solve your current issue, without relocating all the combiner boxes. Ray On 11/21/2011 5:25 PM, Jeff Yago wrote: Thanks to all who replied with

Re: [RE-wrenches] Liability

2011-11-23 Thread Ray Walters
r, and spread by word of mouth, the good news to their off grid neighbors. This type of work is not for the squimish though, and I have had my share of 4 am worry sessions over some of this work. Also bill by Time and materials, you never know what you're going to run into, till you get everyth

Re: [RE-wrenches] Connectors and Crimpers

2011-11-28 Thread Ray Walters
a reliable long term connection. If you want to save money, just buy pre-made MC cables and cut them to length. You end up with some left over 10 ft peices of wire, but it's way cheaper than buying the tool. Ray On 11/28/2011 12:18 PM, Dave Bell wrote: Wondering if anyone has ever had any

Re: [RE-wrenches] calculating low string voltage

2011-11-29 Thread Ray Walters
ing is the actual Power coefficient, which shows the total power losses from higher temperatures, not just voltage. The calculation would be similar. Ray On 11/29/2011 2:07 PM, Darryl Thayer wrote: I am on road so I have no texts with me, but the same formula applies about 0.4% per degree (le

Re: [RE-wrenches] calculating low string voltage

2011-11-29 Thread Ray Walters
that really the best number for calculating this? Or is that too extreme a temperature, that wouldn't occur most of the time? Now I have to correct that coefficient for my next class..but that's why I asked for everybody to look it over. Thanks Everyone, Ray On 11/29/201

Re: [RE-wrenches] Recycling failed modules

2011-11-30 Thread Ray Walters
recycle electronics, I saw a drop off at Best Buy the other day. Ray On 11/30/2011 11:32 AM, Larry Crutcher, Starlight Solar Power Systems wrote: Take them to Quartzsite, AZ in January. You'll sell them in a day. Recycle that junk into cash! Seriously, we often get calls from desert

Re: [RE-wrenches] calculating low string voltage

2011-12-01 Thread Ray Walters
is obviously an important calculation. Should I suggest that my students just use the inverter manufacturers' online tools, and forget about trying to run this voltage calc themselves? Thanks, Ray On 12/1/2011 6:30 AM, Dave Click wrote: At an SMA training last year they recommended the fo

Re: [RE-wrenches] calculating low string voltage

2011-12-01 Thread Ray Walters
might need to be following this thread as well, and tweak their sizing tools appropriately. Ray On 12/1/2011 5:54 PM, Bill Brooks wrote: Ray, There is an explanation on the www.solarabcs.org/permitting <http://www.solarabcs.org/permitting> webpage for the interactive solar map. The 2%

Re: [RE-wrenches] old trace manual

2011-12-02 Thread Ray Walters
You can always add a boost transformer from Backwoods Solar, to boost the VAC slightly (10%) to increase charge amps. If you look at your peak voltage on that genny, its probably below 145 (should be 170 v peak for 120 v rms ) Ray On 12/2/2011 8:46 AM, jay peltz wrote: Hi Howie, They were

Re: [RE-wrenches] SMA combi switch in s.s.

2011-12-07 Thread Ray Walters
Midnite Solar has powder coated aluminum enclosures that also have the AFI option that can be added when available later. There also alot cheaper than some of the other solutions out there. Ray On 12/7/2011 6:57 PM, Dave Click wrote: Marco, the easiest solution may be to just replace it with

Re: [RE-wrenches] NEC 480 - battery enclosure question

2011-12-14 Thread Ray Walters
. 300.6 Has a lot of good info on corrosion that we in the solar biz should be all over, as well. So that's 3 pretty specific code references. Ray Walters On 12/13/2011 7:03 PM, b...@midnitesolar.com wrote: On 12/13/2011 5:47 PM, Dan Fink wrote: Esteemed Wrenches; An email question fr

Re: [RE-wrenches] Step-up/Step-down Transformer question

2018-09-19 Thread Sarah Ray
Fronius makes a single phase 1000vdc inverter. The Primo 11.4 now has an MPP voltage range of 240-800 V, and a maximum input voltage of 1,000V. You can download the datasheet at: http://www.fronius.com/en-us/usa/photovoltaics/products/all-products/inverters/fronius-primo/fronius-primo-11-4-1-208-2

[RE-wrenches] 225A Meter Main with Pass Through Lugs

2019-05-09 Thread Sarah Ray
eeder that is fed by the pass through lugs in the existing 200A meter main (which is located at another building.) The inverter output has a 60A OCPD, so the 200A meter main bus is not sufficient. Any suggestions you have would be greatly appreciated! Thank you, Sarah Ray OnSite Energy, Inc.

Re: [RE-wrenches] 225A Meter Main with Pass Through Lugs

2019-05-09 Thread Sarah Ray
t. >> That's another snag we run into. >> >> >> Jason Szumlanski >> Florida Solar Design Group >> >> >> >> >> On Thu, May 9, 2019 at 2:50 PM Sarah Ray wrote: >> >>> Hi Wrenches, >>> >>> Does

Re: [RE-wrenches] RE-wrenches Digest, Vol 6, Issue 276

2013-07-23 Thread Ray Walters
Some hardware stores carry a high strength double stick foam tape. I've used a permanent outdoor rated type (3M?) that won't come off. Just don't let the kids play with it. This looks like the stuff I used: http://www.uline.com/Product/Detail/S-10152/3M-VHB-Tapes/3M-5925-VHB-Double-Sided-Fo

Re: [RE-wrenches] Tri-Star MPPT

2013-07-23 Thread Ray Walters
Did you look for dead cells? I've seen many L 16 sets (including my own) only last 4-1/2 years, so that set was already almost done. If she started mixing new batteries in before, she knew she already had a problem. Did this system change from 12 v to 24 v? The rule of thumb for eons (or

Re: [RE-wrenches] Tri-Star MPPT

2013-07-23 Thread Ray Walters
The sulfated cell would show an artificially high SQ reading, if she tried to add acid to it: another bogus trick people try, when their batteries are going out. You might ask. Customers often have to try every other trick in the book before admitting they need to pay for new batteries. (a

Re: [RE-wrenches] Tax credit question.

2013-07-27 Thread Ray Walters
I use language like: "you may be eligible; it depends on interpretation; some people have taken the credit in this case; its not my business what you claim on your taxes," all followed by Allan's "check with your accountant, I'm not a licensed CPA" I feel that its fine to mention the

[RE-wrenches] Outback AC coupling Sunpower?

2013-07-30 Thread Ray Walters
Hi All; I know AC coupled systems have been covered before, but I have a new issue: positive grounding. A customer with an existing 8kw Sunpower system wants to add backup. He was put off by the high cost the Sunny Island, so I was steering him towards a single Outback VFX coupled to just

Re: [RE-wrenches] Outback AC coupling Sunpower?

2013-07-30 Thread Ray Walters
trician Solar Design Engineer 303 505-8760 On 7/30/2013 2:59 PM, Ray Walters wrote: Hi All; I know AC coupled systems have been covered before, but I have a new issue: positive grounding. A customer with an existing 8kw Sunpower system wants to add backup. He was put off by the high cost the Su

Re: [RE-wrenches] Outback AC coupling Sunpower?

2013-07-30 Thread Ray Walters
505-8760 On 7/30/2013 5:29 PM, Jay Peltz wrote: Hi ray Magnum does have a way to do it Theirs is a bit different, but all the data is on their web site Jay Peltz power Sent from my iPhone On Jul 30, 2013, at 4:23 PM, Ray Walters wrote: The Outback rep got me some good info, and I'm likin

Re: [RE-wrenches] Outback AC coupling Sunpower?

2013-07-31 Thread Ray Walters
taller, Licensed Master Electrician Solar Design Engineer 303 505-8760 On 7/30/2013 11:37 PM, Kelly Keilwitz, Whidbey Sun & Wind wrote: Ray, The battery-based inverter in an AC-coupled system should not be grid-interactive. The grid passes through the BB inverter to the grid-direct inverter(s).

Re: [RE-wrenches] Outback AC coupling Sunpower?

2013-07-31 Thread Ray Walters
Corey; Would you mind sharing what relay didn't work, and which ones did, along with inverter output current? Since the relays will be running for hours at inverter rated output, my thinking would be to oversize the relay by at least a factor of three. I might try Outback's relay/ breaker

Re: [RE-wrenches] Unknown rail.

2013-07-31 Thread Ray Walters
Looks like SnapNRack. Get some new bolt and clamp sets before you start loosening anything. The SS bolts can spall, and the last one we worked on, we had to replace 1/3 of the hardware. We used anti-seize thread lubricant and a torque wrench on reinstallation. SnapN Rack seems pretty decent

Re: [RE-wrenches] (no subject)

2013-08-03 Thread Ray Walters
Mac; Is this off grid? The Intimidator is not a high cycle life battery. I've had trouble finding exact ratings, but its probably in the 250 to 300 cycles at 80% DOD. I'd expect 3 years max in an off grid application. Also the Intimidators I've seen are actually AGM, not Gel, but I don'

Re: [RE-wrenches] (no subject)

2013-08-03 Thread Ray Walters
Ray Walters CTO, Solarray, Inc Nabcep Certified PV Installer, Licensed Master Electrician Solar Design Engineer 303 505-8760 On 8/3/2013 7:46 PM, Mac Lewis wrote: Ray, Yes, this is an off-grid applications. I think you are right, the battery guy sold him what he had. Pretty pricey battery lesson t

Re: [RE-wrenches] Battery backup under attack in CA

2013-08-08 Thread Ray Walters
Just to add to the discussion: Maui Electric (MECO) has had the same policy of denying all battery based systems. My understanding is they won't even allow simple battery backup systems (no grid tie, so sell back). PNM (in Alan's backyard) used to require a very expensive and unnecessary load

Re: [RE-wrenches] 2500 W inverter for $300

2013-08-09 Thread Ray Walters
These cheapo inverters are nothing new; we've had to sell against them for over a decade. Its all about longevity, and how bad life might be with a several week outage. Weight is a great, simple place to start. The quality inverters are transformer based, and weigh much more. Which one is goin

Re: [RE-wrenches] Hawker versusu MK

2013-08-13 Thread Ray Walters
We use a high lift jack to lift the case up onto a carrier we've made. Roll them right into the room. We then use the high lift to push them exactly into place, with a wood brace against the wall. I'm still a HUP fan fro the cycle life (2100 cycle to 80% DOD) but if the 1500 cycle batteries are

Re: [RE-wrenches] PV Assist

2013-08-16 Thread Ray Walters
Hi William; One thing to consider is that you want to cycle the batteries at least 20% DOD. If you look at the cycle charts for regular Lead acid batteries, the total KWH you can get from a battery for its lifetime is fairly equal from around 20% DOD to 80% DOD. (basically you can get twice

Re: [RE-wrenches] PV Assist

2013-08-16 Thread Ray Walters
I find its also about the money. If they're expecting a $20k system to perform like a $100k one, then yes, move on. I agree with Daryl that you keep a good record by picking your clients. On the other hand, I have some fairly wealthy customers that don't want to reduce their loads, and are wil

Re: [RE-wrenches] PV Assist

2013-08-16 Thread Ray Walters
Hi Kevin; Which watering system did you find that worked? We've been through a bunch that were worse than no watering system at all. R.Ray Walters CTO, Solarray, Inc Nabcep Certified PV Installer, Licensed Master Electrician Solar Design Engineer 303 505-8760 On 8/16/2013 5:38 PM, Kevin Pegg

Re: [RE-wrenches] PV Assist

2013-08-16 Thread Ray Walters
st members, this was supposed to be off list. todd On Friday, August 16, 2013 8:51pm, toddc...@finestplanet.com said: "If the customer wants a mega system and is willing to pay for it, why is it our business to judge them?" hi ray, is it judging them? or simply saying: "i do this

Re: [RE-wrenches] Reading material for Off Grid client

2013-08-18 Thread Ray Walters
My all time favorite is "the Solar Electric Independent Home Book" by New England Solar. Its dated at this point, but does the best job I've seen of conveying the overall design philosophy and life style. Very simple easy read. R.Ray Walters CTO, Solarray, Inc Nabcep Certified PV Installer,

[RE-wrenches] Outback efficiency?

2013-08-18 Thread Ray Walters
I have a couple of Outback questions. On my load analysis sheet, I include 20 w x 24hr/ day for the inverter's no load draw. In the past I had very poor luck with the search mode on most inverters, and found that when I adjusted it so that it came on with efficient lighting, that the no load dr

Re: [RE-wrenches] Hawker versusu MK

2013-08-29 Thread Ray Walters
Full River has better cycle life specs for a sealed battery. We've gotten good feed back from the field so far. B&B is another that I've abused and had good luck with. Their cycle life is lower, but comparable to the Hawker or MK. R.Ray Walters CTO, Solarray, Inc Nabcep Certified PV Installer

Re: [RE-wrenches] Minimum Lux needed

2013-09-05 Thread Ray Walters
On module IV curves, 100 w/m2 is the lowest insolation level usually listed. It would also depend on the charge controller or inverter being used. I've seen arrays make power at below 100 w/ m2 if there is enough array to overcome the operating losses of the electronics. R.Ray Walters CTO,

Re: [RE-wrenches] Off Grid LP Gen advice

2013-09-15 Thread Ray Walters
What supplier are folks using for the Ecogen? R.Ray Walters CTO, Solarray, Inc Nabcep Certified PV Installer, Licensed Master Electrician Solar Design Engineer 303 505-8760 On 9/15/2013 9:19 AM, Dave Palumbo wrote: Ecogen it is. Thanks everybody. Dave Plaumbo *From:*re-wrenches-boun...@lists

Re: [RE-wrenches] Li-I question

2013-09-19 Thread Ray Walters
Looks interesting, I've been waiting for Li+ to start making sense on larger scales. The cycle life does not appear to be better than a HUP lead acid battery, despite the claims of "10 times the cycle life of an AGM battery" I'm confused because in their white paper they also claim: 200 cycle

Re: [RE-wrenches] Battery Warranty Question (was Li-I question)

2013-09-20 Thread Ray Walters
AM, Howie Michaelson wrote: Hi Ray, I have never received compensation for installation time on warranty replacements. Is this something you commonly get? From whom? Thanks, Howie ___ List sponsored by Home Power magazine List Address: RE-wrenche

[RE-wrenches] Wet Romex?

2013-09-22 Thread Ray Walters
Hi Wrenches; This might be slightly off topic for a solar list, but I'm doing some flood damage work for my sister in Boulder, who's basement was completely filled with water last week. We stripped all the sheet rock and carpets, etc. out, and then had a company come in to dry out the lumbe

Re: [RE-wrenches] Li-I question

2013-09-23 Thread Ray Walters
m:* re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org]*On Behalf Of *Ray Walters *Sent:* September 19, 2013 9:51 PM *To:* RE-wrenches *Subject:* Re: [RE-wrenches] Li-I question Looks interesting, I've been waiting for Li+ to

Re: [RE-wrenches] transformerless inverters and conductor colors

2013-09-23 Thread Ray Walters
Hi Marco; Article 200.7 specifically prohibits using white wire for anything but grounded conductors. This came up last year on a large project with an ungrounded array, that also had white incorrectly specified in the plans. The appropriate colors would be red for positive, and black for n

Re: [RE-wrenches] transformerless inverters and conductor colors

2013-09-23 Thread Ray Walters
All Cable and probably other companies can add striping and marking to any wire you need. R.Ray Walters CTO, Solarray, Inc Nabcep Certified PV Installer, Licensed Master Electrician Solar Design Engineer 303 505-8760 On 9/23/2013 10:57 PM, d...@energysolarnow.com wrote: Marco- You should not tr

Re: [RE-wrenches] transformerless inverters and conductor colors

2013-09-24 Thread Ray Walters
ng the conductor polarity with tape, wouldn't that fall foul of the NEC rule that only allows wire colouring on conductors larger than #6? On Tue, Sep 24, 2013 at 2:17 AM, Ray Walters <mailto:r...@solarray.com>> wrote: All Cable and probably other companies can add striping

Re: [RE-wrenches] Breaker Space Knockouts

2013-09-25 Thread Ray Walters
I just did one with 32 tooth/ in. jig saw, then filed it to clean the edges. Came out decent, but took about 20 minutes. I would tape over as well to avoid scratches. I know they make punches, but they're stupid expensive, and easy to break the corners off. R.Ray Walters CTO, Solarray, Inc Na

Re: [RE-wrenches] Energy usage for an electric car

2013-09-27 Thread Ray Walters
We did a charging station for a Chevy Volt earlier this year. We actually ran the charger for about a week to come up with the design, based on their mileage ,etc. This also accounted for battery and inverter losses. We added about a 3400 w array (off grid) and they drove about 40 miles round

Re: [RE-wrenches] Off Grid LP Gen advice

2013-09-27 Thread Ray Walters
On Sep 15, 2013, at 8:56 PM, Ray Walters <mailto:r...@solarray.com>> wrote: What supplier are folks using for the Ecogen? R.Ray Walters CTO, Solarray, Inc Nabcep Certified PV Installer, Licensed Master Electrician Solar Design Engineer 303 505-8760

Re: [RE-wrenches] Energy usage for an electric car

2013-09-27 Thread Ray Walters
:05pm, "Ray Walters" said: We did a charging station for a Chevy Volt earlier this year. We actually ran the charger for about a week to come up with the design, based on their mileage ,etc. This also accounted for battery and inverter losses. We added about a 3400 w array (off

Re: [RE-wrenches] On demand WH

2013-09-29 Thread Ray Walters
If its a Rinai, I measured one once that was 30 watts AC standby, and jumped a bit higher when firing. It also needed pure sine. The customer swapped it for a regular hot water tank. Some Bosches and old Palomas, etc. had either a piezo ignition or pilot, but took no power. I'm working on a sy

Re: [RE-wrenches] Generator automatic disconnect

2013-09-30 Thread Ray Walters
3rd option would be to have a separate charger (IOTA) that just runs from the generator. No pass through loads to the generator. 4th option would be to use a larger Kohler for backup. My experience is that even if they don't think they'll need it, they eventually will actually use it. Large

Re: [RE-wrenches] Generator automatic disconnect

2013-10-01 Thread Ray Walters
11 AM, Larry Crutcher, Starlight Solar Power Systems wrote: William, Chris, Ray, Allan, et al. Gen support would be ideal but this inverter setup will be a quad pack of Magnum 4024PAE (120/240 split; 16kW). Their New MSH inverter is single phase only and can not be stacked. While disabling l

Re: [RE-wrenches] Generator automatic disconnect

2013-10-01 Thread Ray Walters
4-1112 office 780-2738 cell* _www.positiveenergysolar.com_ <http://www.positiveenergysolar.com/> On 10/1/2013 9:16 AM, Ray Walters wrote: Sounds like they need a 20 Kw Kohler. Hot Tub in the future? They'll love their Kohler. The Generac is just way too small to even consider IMHO. R.Ray Walters CTO, Solar

Re: [RE-wrenches] Kohler 20kW (Generator automatic disconnect)

2013-10-02 Thread Ray Walters
alters CTO, Solarray, Inc Nabcep Certified PV Installer, Licensed Master Electrician Solar Design Engineer 303 505-8760 On 10/2/2013 9:48 AM, Larry Crutcher, Starlight Solar Power Systems wrote: Ray, I heard back from Kohler and they told me that the 20kW has no warranty if used off grid. They have 3

Re: [RE-wrenches] question about pole mount interconnection

2013-10-07 Thread Ray Walters
That's too many separate poles, they get to be a real hassle at more than two (and costly too). I'd go to a multipole mount arrangement, (here's one:http://www.dpwsolar.com/index.php/applications/commercial/9-commercial/17-multi-pole-mounts-g2-mpm-g2 and then all your cabling won't have to jum

Re: [RE-wrenches] Teck 90

2013-10-09 Thread Ray Walters
How is TEK 90 referenced in the NEC? Does it meet the qualifications to be used inside an attic for instance? Finally the onestopbuy link was very light on info; are the cables inside stranded or solid? Thanks, R.Ray Walters CTO, Solarray, Inc Nabcep Certified PV Installer, Licensed Master El

Re: [RE-wrenches] Point of connection question

2013-10-09 Thread Ray Walters
HI William; I think you might have a problem. Looking at Enphase's ratings, the M190 has an output rating of 800mA, while the M250 has an output rating of 1.0 A. 10 M250s = 10 amps, 9 M190s = 7.2 amps 17.2 amps exceeds 80% of your 20 amp breaker. I know this won't actually happen, but my und

Re: [RE-wrenches] Oddball wire request

2013-10-10 Thread Ray Walters
I just ran into this on a new Dasol 12 v module. I ended up wiring with USE but couldn't do the series connections. I had to bring each module wire into a J Box. I'm now using Kyocera, as that was a PITA. Since your project is low amperage, have you considered smaller USE like 12 or 14 GA?

Re: [RE-wrenches] GTBB resistance

2013-10-10 Thread Ray Walters
Just to add to Phil's comments: I've been calculating total life cost of battery storage (KWH x cycle life x %DOD) and the costs are 15 to 35 cents/ KWH to cycle a battery. Its even higher for sealed batteries and Li+. It would have to be an amazing cost difference in the TOU rates to beat

Re: [RE-wrenches] SWWP Whisper 200 - Looking for a Short to Ground

2013-10-15 Thread Ray Walters
Not familiar with a Whisper, but here's troubleshooting guide for Bergey with a short. Does it have a rectifier? That could be burned out. R.Ray Walters CTO, Solarray, Inc Nabcep Certified PV Installer, Licensed Master Electrician Solar Design Engineer 303 505-8760 On 10/14/2013 8:55 PM, All

Re: [RE-wrenches] Trace 2548 intermittent power problem

2013-10-17 Thread Ray Walters
While the problems seem related, I'm guessing the gen set issue is a low coolant or low oil condition. The generator has sensors that shut it down if they don't see fluid (coolant, or oil) after a few seconds. The symptoms fit that. For the inverter, it is either fried or has some programming

Re: [RE-wrenches] MC Cable for DC runs

2013-10-21 Thread Ray Walters
/I issue this pre disclaimer, as I don't have references to back all my following statements up. Bill B. is very right about references./ My "Understanding" is that if a UL listed wire, cable, or device has a voltage rating and that volt rating just says 600 V, then it applies to both AC and D

[RE-wrenches] Midnite Breaker Boxes (was: Adding Controllers)

2013-10-24 Thread Ray Walters
Hi Jesse; Midnite's breaker boxes would solve your disconnect issue, but I wouldn't use the baby box or Quad box, they're small and tight. I'd actually consider their 6 position combiner box, even though its outdoor rated. Another option would be the Mini DC box. Here's my quick, real man's

Re: [RE-wrenches] Controller Adjustment?

2013-10-28 Thread Ray Walters
Larry's advise is good for us pros, but I find many customers get mixed up and have a harder time properly programming today's MPPT controllers. If the programming gets messed up, much worse things can happen, and its hard to troubleshoot over the phone. I just advise they turn some of the sub

Re: [RE-wrenches] 12V battery charger

2013-10-30 Thread Ray Walters
I just looked into it. Yes there are other options, but none are even close to the price point of the Iota. They are also super simple to setup, get the new IQ4 option. The only downside to the Iota, is they aren't that conducive to a NEC install; you got to live with some exposed cabling, un

Re: [RE-wrenches] Engineered rafters

2013-11-06 Thread Ray Walters
We just did one, and I used some fairly short Timberlok type lags (thinner and stronger)  I wasn't super excited about only having an inch of wood to grab, but the edge wood is stronger and denser than regular 2x material it seemed.  I predrilled the holes, and g

Re: [RE-wrenches] Square D Disconnects mounted on the slope of the roof.

2013-11-09 Thread Ray Walters
We've made up mounting brackets with unistrut for this purpose as well.  We just bend their regular 45 deg angle brackets to match the roof tilt.  It's a bit of work though, so we are going to other solutions like the Soladek, or just putting the combiner box in a

Re: [RE-wrenches] House fire news

2013-11-11 Thread Ray Walters
I've always found much of BIPV using amorphous technology to be somewhat less safe.  Ever see the Unisolar BIPV setup, with all the parallel connections made loose in the attic?  Yuk. R.Ray Walters CTO, Solarray, Inc Nabcep Certified PV Installer, Licensed Master

Re: [RE-wrenches] PV Wiring methods

2013-11-14 Thread Ray Walters
Where are you buying them from? I am so ready to move away from plastic zip ties. 59 cents is quite a bit, but that's actually doable. Last time I looked at SS ties, they were a couple bucks each. Thanks, R.Ray Walters CTO, Solarray, Inc Nabcep Certified PV Installer, Licensed Master Electr

Re: [RE-wrenches] PV Wiring methods

2013-11-14 Thread Ray Walters
of strong opinion, and we are far from standardization and an accepted set of best practices. Jason Szumlanski Fafco Solar On Thu, Nov 14, 2013 at 1:03 PM, Kirpal Khalsa wrote: Augustthank youyou are right they are actually a Heyco productmy bad!!! Ray, we recently g

Re: [RE-wrenches] PV Wiring methods

2013-11-14 Thread Ray Walters
I definitely think cable tray is a good compromise between conduit and loose zip tie wiring; I primarily question rodent protection. Even cable trays can go horribly wrong: I've seen them not supported properly and bend or even fall over spilling cables onto the roof or ground. R.Ray Walters C

Re: [RE-wrenches] SW4024 relay spark issue

2013-11-18 Thread Ray Walters
I thought the relays on the SWs were sealed, so visible arcing sounds bad. Are you sure its not a loose connection? Also on the batteries, anytime I've ever seen someone replace just a couple of cells in a bank that old, it never ended well. It was like that gopher stomping game, and you hit o

Re: [RE-wrenches] SW4024 relay spark issue

2013-11-18 Thread Ray Walters
o perform well under load testing, totally crash, less than 6 months later. R.Ray Walters CTO, Solarray, Inc Nabcep Certified PV Installer, Licensed Master Electrician Solar Design Engineer 303 505-8760 On 11/18/2013 6:31 PM, Allan Sindelar wrote: Ray, Yes, I know... Doesn't ten yea

Re: [RE-wrenches] A related question - Individual AC conductors through separate conduits

2013-11-20 Thread Ray Walters
My take on 250.110, is that you could run separate EGCs from either end to bond the metal J boxes, and not have the EGC run the entire length through the PVC. Option 2: attach a Bobcat to one end of the PVC and rip it out of the ground, then use the freshly made trench to reinstall what the in

Re: [RE-wrenches] NEC E-Book Access

2013-11-22 Thread Ray Walters
PDF was pretty decent for searching and copying quotes. Never tried the E book. My electrical supply house had a great deal on the book before with a free download of the PDF version. I'm about to ging hunting up the best deal on the 2014 Handbook. Any leads? R.Ray Walters CTO, Solarray, In

Re: [RE-wrenches] Fwd: Re: DC arc welder?

2013-11-23 Thread Ray Walters
Leave it to Windy to be about a generation ahead of the rest of us on all things RE once again. Cheers to Windy:-) I still own a Battery Weld 2000 from the 90s, which is a MIG machine that runs on 24 v dc. The limit is the battery. It can blast at over 200 amps, if you have enough battery t

Re: [RE-wrenches] Remote monitoring for off-grid system

2013-12-05 Thread Ray Walters
First, Outback does have a solution: the Flexnet and Mate 3 stuff; Outback's stuff is pricey though. They're also a mess to wire IMHO. Here's 2 others to consider: Pentametric from Bogart Engineering, and Midnite Solar. Midnite Solar's monitoring is free when you buy their controllers. They al

Re: [RE-wrenches] Remote monitoring for off-grid system

2013-12-05 Thread Ray Walters
rends (battery voltage, SOC, battery currents etc) over time? I like to show people that they are using more power than they think. Thanks On Thu, Dec 5, 2013 at 6:30 PM, Ray Walters <mailto:r...@solarray.com>> wrote: First, Outback does have a solution: the Flexnet and Mate 3 stuff;

[RE-wrenches] Fwd: Re: Remote monitoring for off-grid system

2013-12-06 Thread Ray Walters
e Sky Controllers, to more accurately reach full state of charge. R.Ray Walters CTO, Solarray, Inc Nabcep Certified PV Installer, Licensed Master Electrician Solar Design Engineer 303 505-8760 Hi Ray ! The Whizbang Junior works for ending amps, too, on the Classic controller. Just for folks

Re: [RE-wrenches] Chloride batteries

2013-12-11 Thread Ray Walters
Hi William; My now apparently orphaned copy of Maui Solar Software has Pacific Chloride Brand batteries listed in its data base that are industrial flooded lead acid batteries. They have very similar performance parameters as other fork lift batteries like the HUP. I don't have cycle life i

Re: [RE-wrenches] Entertainment: A contrarian approach to off grid PV

2013-12-16 Thread Ray Walters
I've found that instead of insulting them, I just let them talk about it for a while. Then usually they mention what a pain it is, and how unreliable, and then I gently point to the various potential fire hazards, and that even though 12 vdc can't electrocute you, it sure can start fires I

[RE-wrenches] Cycle Life

2013-12-18 Thread Ray Walters
Hi; I was just doing some cost comparisons of different batteries for a customer. I found that on Rolls website, they've apparently upgrade their cycle life of the S5000 series to 2100 cycles (or more) at 80% DOD. It has been 1500 cycles at 80% DOD for quite a while, so: Question 1, what new

Re: [RE-wrenches] Cycle Life

2013-12-18 Thread Ray Walters
rtified PV Installer, Licensed Master Electrician Solar Design Engineer 303 505-8760 On 12/18/2013 3:37 PM, Larry Crutcher, Starlight Solar Power Systems wrote: Ray, To question 2: I find Rolls batteries to be outstanding. Our oldest banks are over ten years now and trouble free. I can say the

Re: [RE-wrenches] Sick pack

2013-12-19 Thread Ray Walters
You can waste lots of time trying to save an already dieing set of batteries, or just cut to the chase and install a new set. L16s are not a long life battery. While some folks can baby them and get 10 years, I've seen failures at less than 5 years. Compare cycle life; most L16s are only 600

Re: [RE-wrenches] Higher LVR to force full re-charge in small OGPV systems

2013-12-30 Thread Ray Walters
I agree with Allan and Dan, and would also add that modeling the performance in some type of software would also be important. Both PV Design Pro (now apparently obsolete) and HOMER allow you to set on and off set points based on SOC. You can literally see how the battery is cycled to predict i

Re: [RE-wrenches] Higher LVR to force full re-charge in small OGPV systems

2013-12-31 Thread Ray Walters
I'll chime back in on a few points: To MPPT or not: It all gets down to the budget: I find the tipping point to be around 250 to 400 watts. My small systems usually don't have MPPT, and as soon as I get into more than a pair of modules, I'm using the cheaper 60 cell modules with MPPT. I like

Re: [RE-wrenches] OFF-LINE: Re: Higher LVR to force full re-charge in small OGPV systems

2013-12-31 Thread Ray Walters
ep Certified PV Installer, Licensed Master Electrician Solar Design Engineer 303 505-8760 On 12/31/2013 1:43 PM, Exeltech wrote: Hey Mr. Ray ... Aren't you just a gluttony of good info! You're darned handy to have around. I wasn't aware of the Midnite unit. I'll have to scope

Re: [RE-wrenches] Deka AGMs

2014-01-06 Thread Ray Walters
I finally found a cycle life chart on these: they're rated at 1200 cycles to 80% DOD, and about 2000 cycles @40% DOD. In an "average" off grid system at 12 years old, I'd say they're near the end of their life. In a back up setup, who knows. I've tested systems like this before, I basically turn

Re: [RE-wrenches] IBE Battery Flags

2014-01-06 Thread Ray Walters
Hi William; I haven't seen any standard really.  I noticed that HUPs switched from 5/16" hardware to 1/4".  I'm old school like you, and prefer 5/16" hardware, however I think if you look at the lbs of compression that the 1/4" bolt can provide, it's still

Re: [RE-wrenches] Replacement for Whisper 500

2014-01-17 Thread Ray Walters
Bergey is the only reliable choice I'm aware of right now.  They have the XL.1  1000 watt, and I believe it jumps to the 10 kw unit. The 1 Kw units are now using Midnite Controllers, which is definitely an improvement. I can't advise on adapting to the tower

Re: [RE-wrenches] Outback 200 RE

2014-01-18 Thread Ray Walters
Also consider the large industrial batteries such as the Trojan Industrial 2 v models, HUPs, IBE, etc. They have longer cycle life, and therefore are a better deal in the long run. Batteries are the weak link in off grid systems, so you want to really make sure you're getting the right battery,

Re: [RE-wrenches] Very small PV systems for surveillance or other "micro" loads

2014-01-21 Thread Ray Walters
On these small projects, its very important to nail down the exact load, to keep the pricing sane. I list on the estimate what the system is designed to do; for instance 18 w load 24 hrs/ day. Then if something goes wrong and they are running more than they should you just gently point out tha

Re: [RE-wrenches] Very small PV systems for surveillance or other "micro" loads

2014-01-21 Thread Ray Walters
ore in 5 years. R.Ray Walters CTO, Solarray, Inc Nabcep Certified PV Installer, Licensed Master Electrician Solar Design Engineer 303 505-8760 On 1/21/2014 10:26 AM, Dan Fink wrote: I also see lots of "load creep" Ray"oh, forgot to tell youwe need to add some all-night LED a