I'll chime back in on a few points:

To MPPT or not: It all gets down to the budget: I find the tipping point to be around 250 to 400 watts. My small systems usually don't have MPPT, and as soon as I get into more than a pair of modules, I'm using the cheaper 60 cell modules with MPPT. I like Blue Sky's new PWM 30 amp controller that also includes a digital meter.

Temp compensation: it all depends on the temperature variation. If its warm year round, just program the charge settings lower, and as Dan said KISS.

Metering: Midnite's Battery Capacity Meter was specifically designed for the African market. Very simple LED "smiley face, frowny face" reading, It's cheap, and it actually does a decent job of tracking SOC. Its not a Trimetric, but its way better than a volt meter too.

R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760

On 12/31/2013 11:48 AM, Exeltech wrote:
Eric .. Allan .. and all ...

Allan wrote:
Re an MPPT controller: Nope, I wouldn't. First, this is equatorial west Africa.
It's a tropical climate with hot modules most of the year. MPPT offers the
greatest benefit when the voltage delta-T is greatest: cold modules and empty
batteries.
*** While Allan is correct about deriving maximum MPPT benefit when the PV are 
cold, at 75W per panel, and 120A-H battery, the PV are undersized for all but 
very light-duty system usage.  Obtaining the maximum possible charge current 
will help lengthen battery life.  If two 12V 40W PV in series could be 
economically utilized (vs. one 75W panel) .. it's worth considering.


Second, any controller with MPPT is more complex, and thus more expensive, than 
a simple PWM controller.
*** Hence my comment at the top of the suggestion list:  "...  if budget and circumstances 
permit...".  If not - go with a basic PWM unit and other cost-saving measures.  If they're 
going to hold your feet to the fire on the "seven year" battery performance requirement, 
you're going to have to limit the depth of discharge, and also institute other life-enhancing 
practices.



Re temperature compensation:....
*** Temperature compensation in this application may be a toss-up between fully 
recharging the battery and obtaining maximum battery life.  The choice here 
could go either way.  If it's always warm (or hot), compensation may not be 
needed.  In fact, it may be beneficial to help maximize the recharge if the 
controller thinks the battery is cooler than it really is, which in turn would 
push the charge voltage set-point up a bit.  Not knowing the environment where 
the systems will be installed makes this decision an unknown .  Also .. and 
keeping in mind that there are elevated equatorial areas where the weather can 
be cool .. compensation may or may not be a consideration.


To me the other features of the C12 - four adjustable settings, removable knobs 
and 15-minute reserve - were more important than MPPT.
*** There is much to be said for the KISS principle.


Re an LED SOC display: agreed just as Dan stated. Is there one that can be 
programmed to lie a little? (The best of these I ever knew was the Photron 
Batterylite, gone since around 1998. I wish someone would resurrect that tiny 
gem.)
*** With several hundred units in the mix, I'd think a small design house may 
be interested.  As long as you're at it, how about adding a low-voltage 
disconnect option into the monitor design .. and perhaps even an audible alarm 
(with user reset).  Each feature adds $ and complexity.  If the users will 
routinely look at such an LED monitor and use power accordingly, neither of 
these features would be needed.


Eric .. there's no singular (or simple) answer to your question.  If the 
project is going to be awarded on a strictly low-bid basis .. and they're 
adamant about seven year battery life .. you're going to have difficulty 
meeting their budget AND achieving their system goals.


Happy New Year to all....


Dan




--------------------------------------------
On Tue, 12/31/13, Allan Sindelar <al...@positiveenergysolar.com> wrote:

  Subject: Re: [RE-wrenches] Higher LVR to force full re-charge in small OGPV 
systems
  To: "Exeltech" <exelt...@yahoo.com>, e...@solarnexusinternational.com, 
"RE-wrenches" <re-wrenches@lists.re-wrenches.org>
  Date: Tuesday, December 31, 2013, 10:51 AM
Dan and Eric,

Now I'll respectfully argue with some of Dan's suggestions:

Re an MPPT controller: Nope, I wouldn't. First, this is equatorial west Africa. 
It's a tropical climate with hot modules most of the year. MPPT offers the 
greatest benefit when the voltage delta-T is greatest: cold modules and empty 
batteries. No chance for the former, and we're trying to get around the latter. 
If these systems were going to a cold climate I'd agree with you. Second, any 
controller with MPPT is more complex, and thus more expensive, than a simple 
PWM controller. Given the expressed competitive-bid budget limitations, MPPT is 
not a smart place to allocate costs. Dan is right about the weak C/rate. Spend 
the money (if you can) on a second or larger module.

Re cool batteries: agreed, although I don't know how to achieve this.

Re temperature compensation: as much as I push it strongly here, it may not 
matter in this case, and may be a hindrance. What's the annual ambient 
temperature swing? Again, if it's equatorial lowlands the temperature may stay 
around a constant 80ยบ all year. If so, TC is irrelevant. And they occasionally 
fail, which can cause settings to mess up. Once again, decide if the added cost 
is worth it in this application.

Re an LED SOC display: agreed just as Dan stated. Is there one that can be 
programmed to lie a little? (The best of these I ever knew was the Photron 
Batterylite, gone since around 1998. I wish someone would resurrect that tiny 
gem.)

To me the other features of the C12 - four adjustable settings, removable knobs 
and 15-minute reserve - were more important than MPPT.
Allan

Allan Sindelar
al...@positiveenergysolar.com
NABCEP Certified PV Installation Professional
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder, Positive Energy, Inc.

A Certified B CorporationTM
3209 Richards Lane
Santa Fe , New Mexico 87507
505 424-1112 office 780-2738 cell
www.positiveenergysolar.com

On 12/30/2013 7:32 PM, Exeltech wrote:
Eric,

Allan's recommendations on both points are excellent, and spot-on.


I would add the following suggestions for your controller and system if budget 
and circumstances permit:

1) Use a MPPT model controller to enhance the recharge rate under 
less-than-ideal conditions.  The PV is already undersized for the battery you 
indicated (below).

2) If you get the job .. install the batteries in a location that will keep 
them as cool as possible.  Heat is just as detrimental to battery life as is 
failure to fully charge.

3) Temperature-compensated charging will enhance battery life.  However, the 
75W PV vs. 120 A-H battery allows for only a C/20 recharge rate at best.  This 
is not conducive to full recharge on a regular basis unless the loads are very 
small and are lightly used.  If the budget allows for opportunity to double the 
PV wattage .. it would be wise to do so.

4) A simple "stop-light" style LED voltage display won't consume much power, 
but can go a long way toward providing a visual indicator for state-of-charge, especially 
if it's adjustable, and can be be biased toward a higher SOC (in essence, make it fib a 
little, and indicate a low SOC sooner than than is actually the case).  Worth considering 
as an option .. but easily omitted to reduce cost and/or simplify the system.

I wish you success on winning the project.


Regards,


Dan

--------------------------------------------
On Mon, 12/30/13, Allan Sindelar <al...@positiveenergysolar.com> wrote:

  Subject: Re: [RE-wrenches] Higher LVR to force full re-charge in small OGPV 
systems
  To: e...@solarnexusinternational.com, "RE-wrenches" 
<re-wrenches@lists.re-wrenches.org>
  Date: Monday, December 30, 2013, 6:48 PM
Eric,
Yes, one of the classic problems with small systems and less educated users. 
Just a small contribution: it would seem to me that in this case the LVD 
setting is as key as the LVR. What if the LVD was set as high as possible - 
say, 12.0 V with sealed batteries, along with a 13.8 - 14.0 V LVR. The system 
would still be run until it shuts off, but the battery remains at a relatively 
high SOC. The next day the system will return to operation, but with a much 
higher range of SOC. The users will still experience shutdown, and will over 
time become familiar with when to expect it and how to live within its 
capacity, but the battery life will be protected.

This approach seems counter-intuitive, but the more I think about it the more 
sense it makes. The system would also return to operation sooner following 
cloudy weather - in fact, it would provide a minimal amount during each of the 
cloudy evenings.

Is the C12 still made? It would still seem ideal if so: bulk, float, LVD and 
LVR, all adjustable, with removable knobs and a 15-minute reserve button after 
initial LVD shutdown. Rock-solid reliable, too, in my experience.

I'd be interested in what approach you select. This intrigues me.
Allan

Allan Sindelar
al...@positiveenergysolar.com
NABCEP Certified PV Installation Professional
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder, Positive Energy, Inc.

A Certified B CorporationTM
3209 Richards Lane
Santa Fe , New Mexico 87507
505 424-1112 office 780-2738 cell
www.positiveenergysolar.com

On 12/30/2013 5:00 PM, Eric Youngren wrote:
Hi Wrenches,

We are bidding on a project to provide several hundred small (75Wpv, 120AH 
battery) 12V DC off-grid solar home systems for rural villages in West Africa.  
The project planners have requested that the systems be designed and built to 
provide 7 years of battery life.  That seems crazy optimistic to me but I'm 
trying to design the systems that will give the batteries a fighting chance of 
lasting that long.

In my experience with these types of installations, the system users have 
little or no understanding of how to properly manage their batteries and 
usually no metering or SOC indication to help them even if they knew what to 
look for.  So, the default control strategy becomes:  run the loads until the 
Low Voltage Disconnect (LVD) turns them off, then wait until the Sun returns 
and the voltage rises to the Low Voltage Reconnect (LVR) setpoint (around 12.5V 
is a common default) , upon which point the cycle repeats, with the result that 
the battery bounces between LVD and LVR, almost never reaches a full SOC, and 
the batteries are lucky to survive for maybe two years.  After that the system 
will provide a little power during the day while the Sun is shining but the 
batteries will quickly crash below the LVD after the sun goes down.

So, we want to offer a controller with a high LVR setting that will ensure the 
batteries reach a full recharge after each and every LVD incident.    I know the 
C-12 has an adjustable LVR setpoint and I see one Chinese brand (Manson) that can 
do it.   Does anyone have any other suggestions of small (<20A) PWM controllers 
that can be adjusted to not reconnect until 14V or so?     Price is going to be a 
factor in this project so they need to be low cost.

Any other suggestions?  What would you use for the optimal LVD and LVR in this 
situation?     These are rural household, DC only systems with primarily 
lighting and small device charging loads.   I know that this strategy will mean 
that they might not have any access to battery power for up to a few days if 
they hit the LVD during the rainy season and there is not enough sunshine to 
get the battery charged in a single day.  My thinking is that experience will 
provide good feedback that will encourage them to conserve and manage their 
batteries to avoid the LVD situation as much as possible.     That's the idea, 
anyway.  I'd appreciate any advice from you all.  Thanks!

Wishing you all a happy and productive 2014!

Best energy,
Eric

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to