Yes, good point about the 120% rule - thanks Jason. Unfortunately the
existing meter main isn't one where we can downgrade the main breaker. I
did find this lug kit that we can add to a 225A Eaton meter main which
might do the trick.

https://www.platt.com/platt-electric-supply/Load-Center-Accessories-Sub-Feed-Lug-Blocks/Eaton/BRS225/product.aspx?zpid=270025


Sarah

On Thu, May 9, 2019 at 1:20 PM Jason Szumlanski <
ja...@floridasolardesigngroup.com> wrote:

> I should note that if you are on NEC 2014 the 60 OCPD is not the correct
> figure to use in the 120% rule. It would be 125% of the Inverter Output
> Circuit rated current.
>
> It's probably a moot point in this case, but it is an important
> distinction.
>
>
>
> On Thu, May 9, 2019 at 3:06 PM Jason Szumlanski <
> ja...@floridasolardesigngroup.com> wrote:
>
>> Calc loads and see if you can replace the main with a 175A breaker if it
>> exists, or even 150A. This main breaker downsizing has been a go-to
>> exercise for us for existing meter-mains. It's frustrating being limited to
>> 40A on the load side. That doesn't even get to 10kWdc with Enphase IQ7+,
>> which is becoming a pretty small system these days around here. I tell
>> every home builder I see to avoid meter-main combos but they keep putting
>> them in.
>>
>> Sadly our utility accepts NONE of the "solar ready" panels on the market.
>> That's another snag we run into.
>>
>>
>> Jason Szumlanski
>> Florida Solar Design Group
>>
>>
>>
>>
>> On Thu, May 9, 2019 at 2:50 PM Sarah Ray <sarahm...@gmail.com> wrote:
>>
>>> Hi Wrenches,
>>>
>>> Does anyone have a recommendation for a meter main with a 225A bus and
>>> pass through lugs? Eaton and SquareD make meter mains with a 225A bus, but
>>> no pass-through lugs, so they don't work well for most retrofit
>>> applications.
>>>
>>> We would like to connect our inverter output to a feeder that is fed by
>>> the pass through lugs in the existing 200A meter main (which is located at
>>> another building.) The inverter output has a 60A OCPD, so the 200A meter
>>> main bus is not sufficient.
>>>
>>> Any suggestions you have would be greatly appreciated!
>>>
>>> Thank you,
>>>
>>> Sarah Ray
>>>
>>> OnSite Energy, Inc.
>>> 619 N Church Ave, Suite 4
>>> Bozeman, MT 59715
>>> Cell: (406) 579-6512
>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> List Address: RE-wrenches@lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>> <https://mailtrack.io/trace/link/d413296e828a0e208b2d0ff5432ecc5b908495fe?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=64bdd88fc0bbb783>
>>>
>>> List-Archive:
>>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>> <https://mailtrack.io/trace/link/45219de793b9098a8d5ffcc67ca9f44b071c0d48?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=6149e0d8a0774b09>
>>>
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>> <https://mailtrack.io/trace/link/8be75159e5a0c4a3889df5150d9b70bf4ea0d604?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=54b4c005f0a209b3>
>>>
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org
>>> <https://mailtrack.io/trace/link/cd63071172203220e2b175dbbda003eef34fdc00?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=48d52634fc25b5da>
>>>
>>> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to