DraftSight is a free AutoCAD clone (not just for Mac) that may be what
you're looking for.
On 2012/10/22 13:37, Jason Szumlanski wrote:
I don't know if you want a 3D modeling program, but Sketchup is free and
incredibly powerful. There is a Pro version also available with more
advanced tools. I
This is possible because they have cell-level MPPT. I'd guess that even
when the sun is perpendicular to the module you'd have a [tiny] bit of
extra current from diffuse light reflected onto the module, and you'd
see more substantial gains from reflection if the sun can "see" the
reflector and
Nick, what the AHJ is telling you may actually be in reference to
250.97; for most PV output circuits (yes these are necessarily dc) this
bonding requirement applies since array VOC > 250 VDC. As Kent just
pointed out, these dc conductors clearly don't meet the NEC definition
of a service.
"2
Rich,
We have been using SolaDeck PV roof mount enclosure. NEMA 3R with a flashed
penetration. Can use for combining, or simply as a pass through box.
Dave
David Palumbo
Independent Power LLC
462 Solar Way Drive
Hyde Park, VT 05655
www.independentpowerllc.com
NABCEP Certified PV Installer
Bill,
I think so. http://www.rstcenterprises.com/soladeck/
Dave
-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of William
Dorsett
Sent: Sunday, November 25, 2012 9:49 AM
To: 'RE-wrenches'
Subjec
Carl, you may also be interested in HOMER-- free 2-week trial available
of the latest version (after that, $99 per 6-month renewal, despite zero
updates since Nov 2010). There's also the free "legacy" version that's a
few years old.
http://homerenergy.com/
On 2012/11/26 22:40, Carl Adams wrot
oks example) that would have a much stronger
impact.
Dave
On 2012/11/27 15:14, penobscotso...@midmaine.com wrote:
Hi Holt,
We installed a commercial system a year ago for the National Park
Service that was designed by a competitor (?) and signed off on by an
engineer. It consisted of 13.2 k
string sizes and stay as
far as you can above the MPPT minimum voltage. These modules have a
power tolerance of +/-3%, which they accomplish with higher current
values that in some cases actually exceeded the 10% UL tolerance limit!
After 20 years, the VMP on these modules will be about 20
Hi all,
Just passing along a correction from Solectria on this issue. Since Dec
2010 these inverters have had a 205V+ window; apparently these units
just had an old label on them.
Dave
On 2012/11/29 9:39, Dave Click wrote:
Hi all,
I did an inspection recently that had 3 Solectria PVI13kW
Jason, for 9-11 year-olds this curriculum may be useful as a starting
point, and we've got some others for different age groups.
http://fsec.ucf.edu/en/education/k-12/curricula/sm2/index.htm
The "solar powered system" experiment is designed for a cell so we
suggested the load be a small propell
Well summarized. I think your mileage would vary based on the
anti-islanding algorithm used in the inverter and the generator's
ability to regulate frequency. So while it may "work" in that an
inverter syncs to a small generator's output, it's very unlikely that
reverse current backfed into the
;d guess you'd
have to pay for the extra mile of 3P distribution line.
Dave
On Fri, Dec 14, 2012 at 10:12 AM, wrote:
> Hello fellow wrenches,
>I am hoping someone here has come across this before and might have a
> suggestion or two for us. I have a client who has a large pi
that I see on
this unit complained of loud clunky noises).
Sun Frost units are too pricey for this application.
Any recommendations?
Thanks,
Dave
David Palumbo
Independent Power LLC
462 Solar Way Drive
Hyde Park, VT 05655
www.independentpowerllc.com
Vermont Solar Partne
as all the other
loads in the home.
Dave
-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Howie
Michaelson
Sent: Wednesday, January 09, 2013 3:01 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Fridge recom
Dan,
Good to know. I appreciate the comment on the relativity of the noise. I
will strongly consider going with the Frigidaire. I had heard the GE's were
noisy too.
Dave
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf O
This house has an OutBack FX 2012. I'm assuming that this will be a good
enough sine wave.
Dave
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Dan Fink
Sent: Wednesday, January 09, 2013 3:24 PM
To: RE-wrenches
Subjec
Off grid.
And good suggestions from Rob and Todd on the cold location.
Best,
Dave
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of conrad
geyser
Sent: Wednesday, January 09, 2013 3:52 PM
To: 'RE-wrenches'
S
Michael,
This is the same list I referred to in my first post that has a bunch of
GE's listed for 311kWh. Un fortunately these units are no longer made.
Dave
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Michael
inter has averaged
less than 1 Sun Hour/Day. This ain't Cali!!
The PV array is already a C/10 ratio to the battery bank. And I am upping
that to a C/7.5 ratio in the spring, as much as I dare to go with Full River
AGM's.
Dave
-Original Message-
From: re-wrenches-boun...@lists.
I don't think these caps ever worked real well. And as batteries get older
they use more water, right?
Dave
-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of jay peltz
Sent: Wednesday, January 09, 2013
Solar Partner. In this way the state has some control over the
quality of net metered PV installations. Off grid systems receive no
incentives and are not being reviewed by any authorities.
Best,
Dave Palumbo
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun
Marco,
That's impressive!
Little ol' Vermont has done somewhat over 2,000 in the last 10 years with
2012 coming in at 500 systems installed (best yr to date).
Dave Palumbo
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org]
o
reroof beneath it, whereas PV would be easy but tedious. Clearly a
chiller should be elevated. I'd agree that PV should only be elevated if
they're requiring the same clearances under a lightning protection system.
Dave
On 2013/2/2 10:31, Jason Szumlanski wrote:
That is my usual "
d miles away. Puerto Rico has
similar requirements for the same reasons. I believe that next week the
IEEE 1547 committee will finalize what exactly these windows will be in
the new edition.
Dave
On 2013/2/4 18:44, Mark Frye wrote:
Folks,
I was told that because the HI grid has poor frequency
gion). If during
that time the utility again exceeds or falls short of acceptable limits, the
five-minute timer must restart and the microinverter may not begin producing
power for an additional short period following the last out-of-bounds
condition. >>
Best,
Dave
David Palumbo
I
Thanks Daryl. Does your system also sometimes stay off for longer periods
sometimes? My clients system can stay off for up to 64 minutes.
Dave
-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of
penobscotso
gy Renewable Systems, LLC
PO Box 58
Stoughton, WI 53589
PH: 608-712-7862
ryan.hark...@energycraft.com
www.energycraft.com
On Feb 5, 2013, at 11:10 AM, Dave Palumbo wrote:
Thanks Daryl. Does your system also sometimes stay off for longer
periods
sometimes? My clients system can stay off for up
.
To date I have measured (Kill A Watt meter) 741 WH/Day which projects out to
271kWh/Yr.
RF is located in an area that is 70 to 78 degrees in this small wood stove
heated home.
Best,
Dave
David Palumbo
Independent Power LLC
462 Solar Way Drive
Hyde Park, VT 05655
Al,
I believe that Eco Fasten Solar/ Alpine Snow Guards of Morrisville, Vermont
have been working on such a product.
www.ecofastensolar.com
1-877-859-3947
Best,
Dave
David Palumbo
Independent Power LLC
462 Solar Way Drive
Hyde Park, VT 05655
www.independentpowerllc.com
Kirk,
A few years ago Jeff Randal at DPW made us a nice cabinet for a single
Fronius inverter. It was not insulated. Maybe they could customize a unit to
your specs?
Dave
-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org
This could just be due to the better temperature coefficient, or maybe
they do slightly better than cSi at lower irradiance levels?
Solar Frontier CIS: -0.31%/degC
SolarWorld poly: -0.45%/degC
I don't know enough about CIS to comment on the light soaking.
On 2013/2/18 8:36, Marco Mangelsdorf w
e transformer (I'm just saying that it's an option)
or downsizing the main breaker, and at that point you're probably better
off just making it a load side connection. I'd go load side and argue
with the AHJ to use the 2011 update mentioned earlier.
Dave
On 2013/2/28 9:55
isn't the right question to
ask. Try, "Do you, Mr./Mrs./Ms. Homeowner, want a PV system that
produces the best value for your investment?" Then show your super
impressive calculations, based on your years of experience, that your
recommended inverter is the best fit for them. All
http://www.smainverted.com/2013/02/21/groundbreaking-new-feature-on-sunny-boy-tl-us-emergency-power-when-the-grid-fails/
On 2013/3/25 11:56, Nik Ponzio wrote:
Forgive my senility. I recently read somewhere about development of
grid-tie inverters without batteries that offer emergency power via a
What problems is the system having?
Regarding your proposed 3P wiring solution, I don't know whether this
has been fixed recently, but Outbacks in 3P historically haven't
monitored the angle between phases. Under grid-connected operation it's
not a problem, but after they lose the grid connect
I don't believe this would work; official metal-clad cable would, but
not armored cable. Metal-clad only works under the 2011 NEC, and only
then when it meets 250.118(10).
On 2013/4/11 19:24, Hilton Dier III wrote:
I asked this one last year and got a few "That's interesting" responses,
but n
that appear
unrelated to utility pinging.
Thanks,
Dave
David Palumbo
Independent Power LLC
462 Solar Way Drive
Hyde Park, VT 05655
www.independentpowerllc.com
Vermont Solar Partner
25 Years Experience, (802) 888-7194
___
List sponsor
Jeremy,
<< What to look for? >>
Unfortunately, probably a different coffee maker.
I've gone through this with several different appliances over the years on
sine wave inverter output. Washing machines, refrigerators, dishwashers it
could be anything with electronics. Specific manufacturers typic
Wrenches will especially enjoy the IMP and ISC values, pictured in the
final image of the UL notice.
On 2013/4/16 13:29, Jason Szumlanski wrote:
Ray Johnson in Florida has done an excellent job documenting this
fiasco on his blow in the article below and several other articles.
http://www.re
efore they
know what's going on. Works very well as they are inactive until the sun
comes up. I still wear gloves, longsleeves, turtle neck shirt and a
bugnetting hat just to be careful. Then what to do with the bag of wasps?
Make sure it is double bagged and secured with duct tape etc.
Da
order for the
pump, from Germany! One month he says.
If anyone has any info on where these pumps might be available here in the
US I would appreciate it.
Thanks,
Dave
David Palumbo
Independent Power LLC
462 Solar Way Drive
Hyde Park, VT 05655
www.independentpowerllc.com
Vermont
Another option would be to compensate the customer for lost production
until you're out there to replace a second inverter. You can credit this
against Jason's diagnostic fee idea and/or the $150/unit reimbursement
from Enphase. Each unit down is about $30-60/year depending on location.
Could h
Here's the test report:
http://gosolarcalifornia.com/equipment/inverter_tests/summaries/Enphase%20M240_240V.pdf
As comparison, here's the SMA micro:
http://gosolarcalifornia.com/equipment/inverter_tests/summaries/SMA%20SB240-US-10.pdf
I don't understand why the test voltage ranges seem to be shr
erllc.com
Vermont Solar Partner
25 Years Experience, (802) 888-7194
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Carl Adams
Sent: Monday, May 13, 2013 3:17 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] SHW Sc
Jesse,
Check with manufacturer to be sure. I've had AGM's in 24v system's set at
29.2 Bulk/Absorb and other manufacturers (Full River for one) that say 29.6
is fine. So, with an FM80 I would recommend 4 strings of 2 modules to ensure
that you can always get that VMP up where it needs to be.
David
At SPI last year there was at least one company offering this, and
there's another company from Tallahassee also looking into it:
www.usa-eds.com
I'm not an expert by any means but I think that even 120F doesn't kill
legionella-- you need to get to 140F. And even if you do 140F, I imagine
you
t
can stay snow covered for weeks at a time. But I know that going in and I
take PV watts and de-rate the 5 months that we get significant snow here in
northern Vermont and no one is surprised and disappointed with the poor
winter production.
Dave Palumbo
-Original Message-
From: re-wrenches
Actually, one is the manufacturer closest to you, Paul- the Solectria
SGI 225-500kW class does a 600VAC output.
On 2013/5/15 14:03, Paul Lyons wrote:
Stump the RE-Wrenches:
You know the NPR radio show, Car Talk, when they play "Stump the
Chumps"? I visited a manufacturing plant last week th
What about AUO/BenQ Solar AC Unison modules. We installed 3 systems in late
2011 and they used SolarBridge inverters then. Results have been OK so far.
The data logger was clunky then. We are getting an upgraded version now.
David Palumbo
Independent Power LLC
462 Solar Way Drive
Hyde Park,
Jeff,
This has been sent out on the list a few times but I don't remember
anyone sharing their personal experiences with it:
http://solarprofessional.com/articles/products-equipment/product-launches/milbank-offers-load-tap-connector
200+ 60 for a meter main is trickier. The $1100 (list) Schne
As a quick clarification- SolarEdge requires PV WIRE per 690.35. Regular
USE-2 doesn't work for these systems.
On 2013/6/15 7:25, SwingJunkie wrote:
Marco,
We installed our first Enphase system in December 2009, and our last
in December 2011, when their high failure rate became a problem.
(Cu
Unfortunately, the benefits are somewhat limited since you still have to
size the neutral at the same size as your EGC, and you have to upsize
your EGC thanks to your voltage drop. So now instead of a #6 neutral,
you're running them as 8s? Hey, every bit helps...
On 2013/6/20 16:18, Drake wr
690.35(D) does *not* require PV WIRE be used for the whole dc circuit.
You can use either: (quoting directly from 2008)
1) Nonmetallic jacketed multiconductor cables
2) Conductors installed in raceways, or
3) Conductors listed and identified as PV WIRE installed as exposed,
single conductors
S
that the intent is to permit the ground to be
carried with the current carrying conductors, not require."
Am I missing something?
Thanks,
Dave
___
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Change ema
All these manufacturers making cable clips are going to be so upset when
they learn that we know about this quick, cost-effective wire management
method!
You could start with 110.3(B) where the module installation manual may
prohibit anything adhered to the back of the module.
Or 338.10(B)(4
Belated thanks for the replies on this, Jason et al. Sorry for my lack
of a clear explanation- Jason interpreted me correctly. Apparently this
Lennox unit was installed without a neutral- I'm awaiting more info from
the PE.
On 2013/7/5 19:25, Jason Szumlanski wrote:
I think what Da
I think that the 230s required positive grounding, so you can't swap out
the inverter for a TL unit. These two circuits in parallel will be fine
for your MPPT, you'll have essentially the same voltages but slightly
higher current in your new second string.
DKC
On 2013/7/12 19:27, August Goers
William,
Though I wouldn't call it foolproof, and I'm not sure how accurate it
would be for your application, Google Earth has topographic data in it--
just hover your mouse over a point to get its elevation. Not exactly a
substitute for a laser level, but it may be helpf
http://www.nfpa.org/freecodes/free_access_agreement.asp?id=7008SB
It's not the fastest thing, but it's free! It's in Java, and you need to
be online to view it. You do need to create an NFPA account first (which
is also free).
Original Message
Subject: [RE-wrenches] online N
According to REA, yes that cap (and a few others) has been lifted:
http://www.renewableenergyworld.com/rea/news/article/2009/02/update-house-passes-final-version-of-stimulus-package
"Caps on the tax credits for residential solar hot water, geothermal
heat and small wind systems will be removed un
(just to add another Dave to the thread)
Original Message
Subject: Re: [RE-wrenches] Long MC Cable Mid String
From: Drake Chamberlin
To: dk...@aeesolar.com, RE-wrenches
Date: 2009/04/22 10:15
I have scratched my head on this one before, because it seems that two
terminals
x27;t used this
specific one before, but I did order one today :)
Cheers,
Dave
*Dave Tedeyan, PE*
Senior Engineer | Taitem Engineering, PC
110 South Albany Street | Ithaca, NY 14850
o. *607.277.1118 x121* f. 607.277.2119
www.taitem.com
Solar • Sustainability • Energy • Design
Certified B-Corpor
ooler than if
the micro was not working.
Cheers,
Dave
On Fri, Jul 31, 2020, 7:13 AM Al Frishman wrote:
> Hey Dave,
> I am curious. You note that the non working module will be warmer than
> the rest. I would think that if a micro is not working then that module
> will be coo
rvice point even though it
comes first? Or is this not something that is allowed? We are on NEC 2017
here in NY..
.
Thanks!
-Dave
*Dave Tedeyan, PE*
Senior Engineer | Taitem Engineering, PC
110 South Albany Street | Ithaca, NY 14850
o. *607.277.1118 x121* f. 607.277.2119
www.taitem.com
ot; is the first
point of overcurrent protection for the service. What I am thinking of is
similar to the disconnect allowed on the line side of the meter (230.82
(3)), although this one is on the load side of the meter.
Cheers,
Dave
*Dave Tedeyan, PE*
Senior Engineer | Taitem Engineering, PC
110 So
oring site, but that one seems to be
almost as slow, and give only basic system information.
I am curious if others are having success monitoring their Sunpower
systems, or if people are having similar issues.
Cheers,
Dave
*Dave Tedeyan, PE*
Senior Engineer | Taitem Engineering, PC
110 South A
Jason,
Bright sunny days, disconnect on the west side of house, maybe in the sun?
43.56A * 1.25 for continuous duty = 54.45A. If these disconnects are also
baking in the sun, maybe the extra ambient heat is enough to push it over
the edge? Just a thought.
Cheers,
Dave
*Dave Tedeyan, PE*
Senior
generator from Harbor Freight.
I have not laid my own eyes on it yet, but will be there in the next day or
two. Just wondering if anyone has experienced these symptoms and have a
good idea of what to look for first.
Thanks!
-Dave
*Dave Tedeyan, PE*
Senior Engineer | Taitem Engineering, PC
110
>From what I understand, they have had the system for a little over a year,
and have not done any maintenance on the generator.
I was also more suspicious of the generator, and was going to try turning
down the charging amps to see if the generator will work better not being
so loaded.
Dave,
around 52Hz, when loaded. After, we got it to stay around 56Hz.
Fortunately, the homeowner is open to getting a better generator.
Thanks for the tips!
*Dave Tedeyan, PE*
Senior Engineer | Taitem Engineering, PC
110 South Albany Street | Ithaca, NY 14850
o. *607.277.1118 x121* f. 607.277.2119
It's big and expensive, but you can do a SQD DTU361. At least that part
number should get you on the right track. You are looking for a double pole
double throw switch, correct?
Cheers,
Dave
On Mon, Feb 22, 2021, 4:59 PM Dave Angelini Offgrid Solar <
offgridso...@sti.net> wrote:
>
Dave,
That is actually exactly how I used this one. It is only rated for 30A.
Some sites will only list it for 600V AC, but it is also 600VDC rated as
well.
Cheers,
Dave
On Mon, Feb 22, 2021, 7:10 PM Dave Angelini Offgrid Solar <
offgridso...@sti.net> wrote:
> I will search SQD and see
There is also a menu (I don't have the code handy now, but Fronius tech
support should be able to tell you) where you can specifically adjust the
individual operating windows - voltage and frequency trips and trip times.
Cheers,
Dave
*Dave Tedeyan, PE*
Senior Engineer | Taitem Engineerin
put
the ENH202 in the middle of someone's house and generally aim it in the
right direction and there would be great signal 500' away even through some
trees. The TP link one needs a much better line of sight.
Cheers,
Dave
*Dave Tedeyan, PE*
Senior Engineer | Taitem Engineering, PC
110 So
, and also if there is a battery failure at some point they can still
run as a grid tied system.
Cheers,
Dave
*Dave Tedeyan, PE*
Senior Engineer | Taitem Engineering, PC
110 South Albany Street | Ithaca, NY 14850
o. *607.277.1118 x121* f. 607.277.2119
www.taitem.com
Solar • Sustainability • Energy
u actually
lose about 2% at 0.5 and about 8% production at a ratio of 2.
So I can only conclude that either PVWatts does not have a great
calculation, or the efficiency loss due to not running the inverter at
rated power is worse than I assumed.
Cheers,
Dave
On Wed, Mar 3, 2021, 6:14 PM Jason Szuml
Then just as a follow up, I looked at the SMA-41 datasheet. This shows that
it runs at it's highest efficiency when the output power / rated power is
about 0.4 to 0.6, and the only real loss in efficiency comes when you are
running at about 0.1 and below.
On Wed, Mar 3, 2021, 8:35 PM
Hi Don,
The Sunny Boy US models are able to be configured for positive ground. I
have found some of them here before for replacements:
https://you-love-solar.myshopify.com/search?type=product&q=love+solar
Looks like they even have an old Sunpower one on their front page.
Cheers,
Dave
On Fri,
allow all the solar to independently charge each battery? Is
there another product out there that people would recommend for this?
Thanks for the help!
Cheers,
Dave
--
*Dave Tedeyan, PE*
[image: Sungineer Solar]
1653 Slaterville Road, Ithaca, NY 14850
Cell: 607-288-2898
www.sungineersolar.com
Hi Chris,
Another company that may be worth looking at is ELM.
http://www.elmmicrogrid.com/
It looks like they have some 480V commercial packages.
Cheers
Dave
On Wed, Apr 21, 2021 at 3:48 PM Chris Schaefer
wrote:
> All good ideas, but what I'm trying to avoid is putting 3 inverters
&g
William, Jeremy,
I have been using Quickmount QMSE-Lag flashings for years. They have the
raised seal that does not rely on an EPDM bushing. It's more expensive than
most other flashings, but I figure this small added cost is definitely
worth the peace of mind.
Cheers,
Dave
On Fri, Apr 23,
will need something rated for just over 30A. This
seems like a better way to allow the generator to run at any time it is
needed, especially if it is a gloomy, snowy, winter day.
Cheers,
Dave
--
*Dave Tedeyan, PE*
[image: Sungineer Solar]
1653 Slaterville Road, Ithaca, NY 14850
Cell: 60
maybe A would be more of a concern. But for grid tied, I would
think option B would be worse.
Does anyone have a fail safe method of doing this?
Cheers,
Dave
On Tue, May 4, 2021, 4:41 PM Chris Schaefer
wrote:
> Jason,
>
> A valid concern which is why I always wire them as powered o
I would certainly agree with you all that AC coupled for off-grid is not
the best design choice. But just for clarification, this is a grid-tied
system where there is already an Enphase M215 system and a whole house
generator set up.
Cheers,
Dave
On Fri, May 7, 2021 at 11:10 AM Jerry Shafer
Hi Dave,
You did get the Square D part right. See the Schneider website, which shows
that it is 600V DC and does have an off in the middle.
https://www.se.com/us/en/product/DTU361/safety-switch%2C-double-throw%2C-non-fusible%2C-30a%2C-600-vac-vdc%2C-3-poles%2C-30-hp%2C-nema-1/
Cheers,
Dave
On
Kirk,
Could there be a loose wire connection to the breaker? That could cause it
to heat up an trip sooner than it otherwise would.
Cheers,
Dave
On Sat, May 8, 2021, 2:13 PM Kirk Herander, VSE wrote:
> I have a system where the SE1 inverter fried internally. The 60A AC
> output b
generator is on.
Cheers,
Dave
On Fri, May 7, 2021 at 9:06 PM Dave Angelini Offgrid Solar <
offgridso...@sti.net> wrote:
> Thanks! I thought this was for Offgrid and that was my mistake.
>
> Will it run a 15A table saw without losing power, or was that just too
> much expertise? I
the
inverter when the transfer switch loses the 240V signal. My plan was to
rewire that start signal to the Sol-Ark inverter, but keep the transfer
switch as the main service point to prevent any kind of backfeeding to the
grid.
Cheers,
Dave
On Thu, Jun 17, 2021 at 9:41 AM r...@solshineenergy.com
boat, so I'll stick to marine inverters for this one.
Cheers,
Dave
On Wed, Jun 30, 2021 at 5:30 PM b...@midnitesolar.com
wrote:
>
> If you can't find a single compatible charger, what also works it to use 2
> (two) separate
>
> MPPT charge controllers each with a separa
Dave,
This is for a boat that will stay mostly on the finger lakes and in the
Erie Canal system in upstate NY. Definitely not an ocean boat. But the plan
is to convert it to a full time residence, potentially in the winter as
well.
Cheers,
Dave
On Thu, Jul 1, 2021 at 11:52 AM Dave Angelini
Hi Chris,
I also am curious of others experiences. I've got one system with SMA and
the TS4-R-F. No problems, but it's only 6 months old. I hear that SMA now
recommends the ones made by JMS, but it looks like essentially the same
thing.
Cheers,
Dave
On Tue, Aug 24, 2021, 11:22 AM C
Hi All,
I am looking for recommendations for a solar racking system that can be put
on a flat commercial roof where the point loads can span 12-13" east/west.
I am imagining a system built up almost like a ground mount. Does anyone
have manufacturer suggestions?
Thanks!
some kind of fault in the inverter itself
that
occasionally induces extra current? Is there any way to tweak the settings
so that it
actually produces a bit more than 11.4kw? I appreciate your thoughts.
Cheers,
Dave
--
[image: Logo] <https://www.sungineersolar.com/>
Dave Tedeyan, P.E.
ystem at the same site, so the original
installers' wire pulling technique is certainly suspect.
Cheers,
Dave
On Mon, Nov 1, 2021, 6:05 PM Jerry Shafer wrote:
> Does this system have monitoring, what time of day is this happening, the
> monitoring site should show output at time of failure
stem turned
off.
Not being my original install, I am not sure if this was an issue before. I
wonder if somehow the IQ series could be more sensitive to overvoltage? But
anyway, try checking voltage...
Cheers,
Dave
On Mon, Nov 1, 2021, 6:31 PM Jason Szumlanski <
ja...@floridasolardesigngroup.com&
It is always the left fuse! Thanks all for the pointers. I'll double check
the monitoring, but am thinking that I will be replacing the switch with a
SQD, and replacing the taps and AC wires as well while I'm at it.
Cheers,
Dave
On Mon, Nov 1, 2021, 9:13 PM Jerry Shafer wrote:
&g
, but
supposedly they were not selling very many of those.
Cheers,
Dave
On Mon, Dec 6, 2021 at 11:42 PM frenergy wrote:
> Wrenches,
>
> Not sure if AC panels are being installed yet, am I living
> under a rock? We've been really happy with LG NeON 370 watt panels and
380w ones from your first link. My supplier should be getting
the 380's by around the new year, as they just switched over from the
375's. Then there are also 370w ones with the black backsheet. (
https://www.lg.com/us/business/neon-2/lg-lg370m1k-a6).
Cheers,
Dave
On Wed, Dec 8, 2021 a
whole controller.
Thanks!
-Dave
--
[image: Logo] <https://www.sungineersolar.com/>
Dave Tedeyan, P.E.
Owner | Sungineer Solar
p: he | him | his
a: 1653 Slaterville Rd. | Ithaca, NY 14850
w: www.sungineersolar.com <http://www.sungineersolar.com/>
401 - 500 of 1277 matches
Mail list logo