As I remember the FXR inverters will rarely connect to any generators
beside very well controlled or inverter type generators. I agree that I
don't think there is any automatic transfer from grid tie to generator
input.
Brad Bassett
On Thu, Oct 24, 2024 at 3:42 PM Wayne Irwin via RE-wrenches <
re
Jeremy:
Question: Did you install the ATS as a work-around to the problem
described?
William Miller
Miller Solar
17395 Oak Road, Atascadero, CA 93422
805-438-5600
www.millersolar.com
CA Lic. 773985
*From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
Behalf
Generac Eco Gen
Jeremy Rodriguez
Solar Installation / Design
All Solar, Inc.
1453 M St.
Penrose Colorado 81240
Sent by Jeremy's iPhone. Sorry for typos and shorthand.
On Oct 23, 2024, at 9:06 PM, Jerry Shafer via RE-wrenches
wrote:
What gen set are you using
Fun times
On Wed, Oct 23, 2024
We Installed the automatic transfer switch so the inverter AC input could be
either grid or generator.
Jeremy Rodriguez
Solar Installation / Design
All Solar, Inc.
1453 M St.
Penrose Colorado 81240
Sent by Jeremy's iPhone. Sorry for typos and shorthand.
On Oct 24, 2024, at 10:41 AM, William Mil
Hi Jeremy,
We have a client with 4 of the VFXR3648's in the same situation, GTBB and
you've described our solution perfectly although we installed a manual transfer
switch instead of the ATS, so if someone has figured out a better solution we'd
like to know what it is, thanks.
Chris Worceste
Dear, all, If you have one or two of these gathering dust, contact me off-line.Thanks a ton!Andrew KoyaanisqatsiPresidentSolar Energy Solutions, Inc.The BRIGHT CHOICESince 1987, helping you and your Portland neighbors move towards an environmentally sustainable future.503-238-4502www.SolarEnergyOre
On Oct 24, 2024, at 4:40 PM, Jay wrote:That one cell you have a picture of sure looks suspicious to me. Especially given the good IR picture. It looks it’s physically broken, right about where a hard hat would rest while moving it. That level of hot spot can’t be good. There are two kinds of thin
One of the unfortunate changes from the SW to FX /FXR inverter architecture was
the elimination of two AC inputs. The whole point of a battery based inverter
is for backup power, so this becomes a huge issue when a grid tied system has a
grid outage long enough to necessitate generator charging
Hi Jeremy
There are two issues I think.
1 is that the inverter won’t connect.
And I don’t have an answer why the inverter won’t in sell mode but will in gen
mode. Maybe the generator is slightly out of the more narrow window for grid. I
presume you’ve checked hz and volts and they are in spec
I have switched to Radians to get back to where we were with SW4048’s.
Also split phase and Optics make a good package. Heavy and wiring are a
nuisance but reliability has been good and the few issues solved with board
or module swaps. BUT with Outback in Limbo ?