Martin, Micro inverters are the safest. Opening a string under load is dangerous. Having qualified personnel servicing the equipment is essential. My point is that an isolated incident is not statistical data. All technologies have their hazards. The number of electricians injured by various

Re: [RE-wrenches] Rapid Shutdown Compliance

2020-05-11 Thread Martin Herzfeld
Drake, I concur with your approach on this item - 1. Either the shock hazard was reduced by NEC 690.12 with MLPE for the workers *too* or folks have been qualified persons in accordance with NEC 690.4(C) to recognize and avoid the shock hazard for string inverters. 2. Specifically, there's this

Re: [RE-wrenches] Rapid Shutdown Compliance

2020-05-07 Thread cwarfel
I live in a small town, so our outreach probably has greater impact. We have gone to the FD meetings, we tell them about the system types and definitions, quiz them and follow up. So, I think depending upon training, which is not a one shot deal, it can have an impact. They seem relieved. On 202

Re: [RE-wrenches] Rapid Shutdown Compliance

2020-05-07 Thread Lones Tuss
FM100 has onboard AFCI http://www.outbackpower.com/products/charge-controllers/flexmax-100-afci I hope this helps. Take Care All From: RE-wrenches On Behalf Of Jerry Shafer Sent: Wednesday, April 29, 2020 11:34 PM To: RE-wrenches Subject: Re: [RE-wrenches] Rapid Shutdown Compliance Wrenches We

Re: [RE-wrenches] Rapid Shutdown Compliance

2020-05-07 Thread Brian Mehalic
I agree: utilize the formal process, ideally with a group of folks. If you are a SEIA member, get involved in their Codes and Standards process. The additional directory language you suggest is not likely to be valuable to many first responders without significant training and documentation, and

Re: [RE-wrenches] Rapid Shutdown Compliance

2020-05-07 Thread Christopher Warfel
To change this, we need to recognize we are "fighting City Hall", and I doubt the CMP will be motivated to make changes on their own.  Maybe this has always been more political than technical, but it seems that those who are opposed to the current requirements need to make it known through the

Re: [RE-wrenches] Rapid Shutdown Compliance

2020-05-07 Thread James Jarvis
If first responders are the point of all the rapid shutdown, there needs to be better exemptions. I personally have a 20kW solar array on a 100 year old unused barn at my farm. The roof is at 50 degrees slope and needs a 60ft boom lift to access. There was significant extra expense and effort for t

Re: [RE-wrenches] Rapid Shutdown Compliance

2020-05-07 Thread Christopher Warfel
I believe Rapid Shutdown was mostly a solution looking for a problem.   The only way I see this becoming "reasonable" is to present "grievances" to the Code Making Panel WITH a solution for their consideration.  Based on experience from being part of an outreach program that taught approximatel

Re: [RE-wrenches] Rapid Shutdown Compliance

2020-05-06 Thread Ray
Spending more time on the roof, while putting more equipment and parts to meet MLPE, means more trips up the ladder, which increases, not decreases the #1 worker safety danger: Falls. Please correct me if I have somehow misunderstood this, but MLPE is not making installers safer based on OSHA i

Re: [RE-wrenches] Rapid Shutdown Compliance

2020-05-06 Thread drake . chamberlin
Interestingly enough, the data on the link [9] provided shows accidents from gas explosions, falls, health problems and industrial injuries. None of these incidents could have been prevented by module level power electronics. This is typical of the data that I've seen so far. --- On 2020-05-0

Re: [RE-wrenches] Rapid Shutdown Compliance

2020-05-06 Thread Martin Herzfeld
There could be an issue of encouraging MLPE for worker safety? 1. This is data involving incidents with workers in the OSHA Fatalities and Catastrophe Investigation Summaries found here: https://www.osha.gov/pls/imis/AccidentSearch.search?p_logger=1&acc_description=&acc_Abstract=solar&acc_keyword

Re: [RE-wrenches] Rapid Shutdown Compliance Secure Power

2020-05-05 Thread don
off by the RS system that needs AC to activate it firstDon BarchEnergy Solar Date: Tue, 5 May 2020 08:35:51 -0400 From: Tump <t...@swnl.net> To: RE-wrenches <re-wrenches@lists.re-wrenches.org> Subject: Re: [RE-wrenches] Rapid Shutdown Compliance Message-ID: <7273560e-f55b-4007-8

Re: [RE-wrenches] Rapid Shutdown Compliance

2020-05-05 Thread Eric Smiley
We are running into the same problem with battery back-up, grid-tie systems. Many Rapid Shutdown solutions turn off the array when utility power is off, which isn't desirable. We have one client with an underground service and the local AHJ wants the RS initiating device near the meter (as our Cana

Re: [RE-wrenches] Rapid Shutdown Compliance

2020-05-05 Thread Tump
How about a SPDT switch, all one is doing is supplying AC voltage from the utility, (powering the MLPE box's Ac to Dc converter) their utility or SSP from the SB’s utility. > On May 4, 2020, at 8:04 PM, > wrote: > > Many customers ask about keeping power alive when the grid is down. Besides

Re: [RE-wrenches] Rapid Shutdown Compliance

2020-05-04 Thread don
Many customers ask about keeping power alive when the grid is down. Besides battery backup, I advocate the Secure Power feature of SunnyBoy inverters. But the problem with MLPE is that it is incompatible with Secure Power. When the grid goes down the MLPE disconnect each solar module's DC feed. So

Re: [RE-wrenches] Rapid Shutdown Compliance

2020-04-30 Thread Martin Herzfeld
1. I use a MLPE residential ground-mounted solution - rapid shutdown or not. w/Accessible MLPE. 2. There is a maximum physical string length for me to keep in mind, for instance, found here: "In the context of this document, string length refers to the number of optimizers and modules in the str

Re: [RE-wrenches] Rapid Shutdown Compliance

2020-04-30 Thread Dave Tedeyan
I was told at a training a couple years ago that there were going to be some modules coming out soon that had a microchip in the module junction box which would replace the diodes and effectively work as MLPE. I have not heard anything about that recently though. Does anyone know what I am talking

Re: [RE-wrenches] Rapid Shutdown Compliance

2020-04-30 Thread Dan Fink
Since I only work with off-grid systems, I find the 690.12 exception starting in NEC 2017 for ground-mounted systems with DC equipment in a separate structure intended only for PV components, is very useful for avoiding expensive, unneeded RSS equipment. Many folks don't like the idea of a battery

Re: [RE-wrenches] Rapid Shutdown Compliance

2020-04-30 Thread drake . chamberlin
I would like to see real data on the fire risk of string inverters. Anecdotal problems are not data. The industry is definitely heading toward MLPE due to the rapid shutdown requirements. In many cases MLPE makes sense, in other cases it doesn't. Systems that are more cost effective and relia

Re: [RE-wrenches] Rapid Shutdown Compliance

2020-04-30 Thread Tump
I agree w/ Ray as most of my work is Off grid. Incorporating addition failure points ( RSD modules. optimizers ect.) for a system that is usually quite a distance from service, be it my service or the fire departments, I find the justification very hard. Ive replaced your micro inverters at 0* d

Re: [RE-wrenches] Rapid Shutdown Compliance

2020-04-30 Thread August Goers
All - Ray has a good point, the discussion here is really about two different types of systems - mainstream ongrid PV, and small scale (and a relatively small market) offgrid PV. It's really tough to design a small offgrid system (especially DC coupled) with rapid shutdown. I think it's just a case

Re: [RE-wrenches] Rapid Shutdown Compliance

2020-04-30 Thread Brian Mehalic
Deadline for 2023 NEC® public input is in September. Brian > On Apr 30, 2020, at 7:12 AM, Ray wrote: > >  > Hi Jerry; > > This isn't about us not being willing to learn the tech. All of us are > constantly learning about new code changes, new inverters, and solar modules > that change spe

Re: [RE-wrenches] Rapid Shutdown Compliance

2020-04-30 Thread Ray
Hi Jerry; This isn't about us not being willing to learn the tech.  All of us are constantly learning about new code changes, new inverters, and solar modules that change specs every few months.  We are voluntarily adopting new technology (like Lithium Ion batteries) when that technology is co

Re: [RE-wrenches] Rapid Shutdown Compliance

2020-04-29 Thread Jerry Shafer
Wrenches We are taking two very different issues and mixing them together. RSD and Arc-fault are different, arc fault will and does prevent fires, RSD was brought out of the need to vent a roof that even with the meter pulled have 500 volts and resulted shocks to fire fighters by cutting into roofs

Re: [RE-wrenches] Rapid Shutdown Compliance

2020-04-29 Thread drake . chamberlin
Rapid Shutdown does not prevent fires; it was originally drafted to allow firefighters to vent a roof without being hindered by energized PV arrays. This rule was expanded to include other DC wiring from PV sources. As for PV safety, I'd like to see some significant, statistical evidence that s

Re: [RE-wrenches] Rapid Shutdown Compliance

2020-04-29 Thread Jason Szumlanski
"Rapid Shutdown does not prevent fires." Not true. If the effect of RS is to steer the market to MLPE, I believe it has a significant impact on reducing fire risk. As one who has watched a DC conductor fire smolder out of control, I am sold on an AC module or microinverter architecture. While RS o

Re: [RE-wrenches] Rapid Shutdown Compliance

2020-04-29 Thread Jason Szumlanski
I have been to several PV fires for string inverter systems, both commercial and residential, and have seen many DC systems at serious risk of fires or in various stages of melted insulation and connectors. Most of these systems have exhibited good to excellent workmanship. Things just went wrong.

Re: [RE-wrenches] Rapid Shutdown Compliance

2020-04-29 Thread Darryl Thayer
my two cents worth, 690.11 says turn off from all arcs, that means serial and parallel that means module lwevel shutdown ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: h

Re: [RE-wrenches] Rapid Shutdown Compliance

2020-04-29 Thread Ray
I agree, 690.12 should have exemptions for lower voltage, lower power systems, and shorter runs; especially off grid.  10 years ago, I was promoting some type of remote controlled disconnect at the array, but that was for voltages over 400v, with unprotected conduit runs over a 100 ft long, on

Re: [RE-wrenches] Rapid Shutdown Compliance

2020-04-29 Thread Dave Angelini Offgrid Solar
My 2 cents are related to the very few times I have had to do RS for offgrid. My advice is to install whatever the inspector wants, assuming he can't be convinced of the mindless requirement. Complete the installation. Do the right thing after by abandoning it. Have the client remove the RS signi

Re: [RE-wrenches] Rapid Shutdown Compliance

2020-04-29 Thread Jay
Hi Drake I will disagree, there have been many roof top fires. But regardless we have to do these new regulations and I for one welcome the safety. The main issue is accessing the faulty/suspect component under the module possibly requiring removing multiple modules, a slow and expensive pr

Re: [RE-wrenches] Rapid Shutdown Compliance

2020-04-29 Thread drake . chamberlin
Clearly, rapid shutdown increases cost and reduces reliability. Given the excellent safety record of PV, prior to rapid shutdown being required, it is unnecessary. The few anecdotal incidents of PV fires were not enough to justify the requirement, especially on smaller systems. According to a f

Re: [RE-wrenches] Rapid Shutdown Compliance

2020-04-29 Thread August Goers
Hi Corey - As we've grown, and as our fleet of installed systems has grown, I've become increasingly interested in choosing an inverter solution that shows per-module production data. I realize that you specifically asked not to consider optimizers or microinverters, but I wonder if that will be a

Re: [RE-wrenches] Rapid Shutdown Compliance

2020-04-29 Thread Sky Sims