Re: [RE-wrenches] Sol-Ark Gen Input

2024-10-28 Thread rick--- via RE-wrenches
Any decent meter will have a high input impedance on the Volts setting otherwise it would provide an inaccurate reading. Our customer, who first reported this, is an engineer with a well-known charge controller/inverter company. He used a cheap meter whereas I used a Fluke 87-5. Both had the same r

Re: [RE-wrenches] Sol-Ark Gen Input

2024-10-28 Thread Darryl Thayer via RE-wrenches
My first thought is what meter are you using? Some meter will have high input impedance and give false value On Tue, Oct 15, 2024 at 1:09 PM rick--- via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > Back on the Sol-Ark topic again. We have a customer whose 12kW is > measuring -195VDC

Re: [RE-wrenches] Sol-Ark Gen Input

2024-10-28 Thread rick--- via RE-wrenches
;>>>>> >>>>>> There’s no PV on this system. It’s AC coupled to an SMA SB5.0. >>>>>> >>>>>> As a test, we turned off the Grid input, Load output, and turned off the >>>>>> battery breaker. As expected, the hig

Re: [RE-wrenches] Sol-Ark Gen Input

2024-10-28 Thread Jay via RE-wrenches
CA 93422805-438-5600www.millersolar.comCA Lic. 773985  From: r...@solshineenergy.com [mailto:r...@solshineenergy.com] Sent: Tuesday, October 15, 2024 12:03 PMTo: will...@millersolar.com; RE-wrenchesSubject: Re: [RE-wrenches] Sol-Ark Gen Input William, There’s no PV on this system. It’s AC coupled to

Re: [RE-wrenches] Sol-Ark Gen Input

2024-10-28 Thread rick--- via RE-wrenches
ion that is producing the DC voltage on the Gen >>>> inputs. >>>> >>>> While you are at it, check DC voltages between the Sunny Boy DC inputs to >>>> ground and between the Sunny Boy Chassis and ground. >>>> >>>> Chec

Re: [RE-wrenches] Sol-Ark Gen Input

2024-10-16 Thread William Miller via RE-wrenches
between the Sunny Boy Chassis and ground. > > > Check your GEC, GEC bonding conductor and all of the system EGCs. > > > I would also check the GFDI fuse on the Sunny Boy. > > > William Miller > > > Miller Solar > 17395 Oak Road, Atascadero, CA 93422 > 805-438-5

Re: [RE-wrenches] Sol-Ark Gen Input

2024-10-16 Thread rick--- via RE-wrenches
PMTo: will...@millersolar.com; RE-wrenchesSubject: Re: [RE-wrenches] Sol-Ark Gen Input William, There’s no PV on this system. It’s AC coupled to an SMA SB5.0.  As a test, we turned off the Grid input, Load output, and turned off the battery breaker. As expected, the high voltage DC eventually bled to

Re: [RE-wrenches] Sol-Ark Gen Input

2024-10-16 Thread rick--- via RE-wrenches
shineenergy.com> > [mailto:r...@solshineenergy.com <mailto:r...@solshineenergy.com>] > Sent: Tuesday, October 15, 2024 12:03 PM > To: will...@millersolar.com <mailto:will...@millersolar.com>; RE-wrenches > Subject: Re: [RE-wrenches] Sol-Ark Gen Input > > Will

Re: [RE-wrenches] Sol-Ark Gen Input

2024-10-15 Thread William Miller via RE-wrenches
Oak Road, Atascadero, CA 93422 805-438-5600 www.millersolar.com CA Lic. 773985 *From:* r...@solshineenergy.com [mailto:r...@solshineenergy.com] *Sent:* Tuesday, October 15, 2024 12:03 PM *To:* will...@millersolar.com; RE-wrenches *Subject:* Re: [RE-wrenches] Sol-Ark Gen Input William

Re: [RE-wrenches] Sol-Ark Gen Input

2024-10-15 Thread rick--- via RE-wrenches
-wrenches.org > <mailto:re-wrenches-boun...@lists.re-wrenches.org>] On Behalf Of rick--- via > RE-wrenches > Sent: Tuesday, October 15, 2024 11:09 AM > To: RE-wrenches > Cc: r...@solshineenergy.com <mailto:r...@solshineenergy.com> > Subject: [RE-wrenches] Sol-Ark Gen

Re: [RE-wrenches] Sol-Ark Gen Input

2024-10-15 Thread William Miller via RE-wrenches
805-438-5600 www.millersolar.com CA Lic. 773985 *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *rick--- via RE-wrenches *Sent:* Tuesday, October 15, 2024 11:09 AM *To:* RE-wrenches *Cc:* r...@solshineenergy.com *Subject:* [RE-wrenches] Sol-Ark Gen Input

[RE-wrenches] Sol-Ark Gen Input

2024-10-15 Thread rick--- via RE-wrenches
Back on the Sol-Ark topic again. We have a customer whose 12kW is measuring -195VDC to ground from L1 and L2 with the Gen breaker open. L1 to L2 = 0V. I know the Gen input can be configured as an output, but reading a high DC voltage to ground is concerning. The generator has never been run. Sys