WrenchesHere is the math, well the answer at sea level your body has 14.70 PSI
exerted on it, at 10,000 feet you only have 10.163 PSI, reduced air pressure,
reduced cooling or heating ability adjusted for standard sea level temp or just
over 69%.I have done work in Hawaii on the big island up at
Current will pass through so just one hot leg to earth, be carefull not to
overload the diodes, l have never had an issue but you never know. JerrySent
from my Verizon, Samsung Galaxy smartphone
Original message From: drake.chamber...@redwoodalliance.org
Date: 4/10/19 3:07 PM
WrenchesYes HOA's might be able to restrict pv under state law depending on
your state, in Hawaii the rule is multi-family joined over 2 stories they can
say no, they can also restrict size to. You need to read the AOAO rules, know
the state law pertaining to your particular type of structure.
Christopher I have used a Cummins 200 amp generator/grid transfer switch, it
gives the gen start command, we used this so during normal operations we could
pass through the full load where in backup mode the inverters took overSent
from my Verizon, Samsung Galaxy smartphone
Original mes
KristopherEach box has it own set of bussing and breakers, not using a box how
would you protect the DC inputs and what would you do with the AC outputs,
bypass, that along with the DC wiring.I have installed 8 Radian in one location
all with the box under the inverter.JerrySent from my Verizon,
DarrylYou might want to look at Blue ion, have a bunch installed and they have
been great "Mars Mission Ready" great, had a customer that survived the Fires 2
years ago and all the time with no power these batteries kept up.Jerry
Sent from my Verizon, Samsung Galaxy smartphone
Original
You need to check with your distributor because we have been installing for
many months now, both master and slave batteriesJerry
Sent from my Verizon, Samsung Galaxy smartphone
Original message From: Kirk Herander
Date: 12/14/18 6:43 AM (GMT-08:00) To: re-wrenches@lists.re-
Peter/WrenchesLook at the Nlue Planet Blue Ion batteries with the BMU, Thdy
have a great Product designJerry
Sent from my Verizon, Samsung Galaxy smartphone
Original message From: Peter Parrish
Date: 12/10/18 7:49 AM (GMT-08:00) To:
RE-wrenches Subject: Re: [RE-wrenches]
WrenchesI have installed several in Hawaii in recent months and more in
California, l have not had any issues with either out of the box or pre-wired.
With the Shunts it may have been a batch but missing hardware is just that,
missing. I will keep an eye out and we will see.Jerry
Sent from my
WrenchesI have used Iron Edison Batteries and 12 volts is tough but l have had
no issues at 48, you can set the high side voltage enough to work well. They
are a very thirsty battery technology but may last for ever. Round trip
efficiency is 70% at best so a larger array is required and the batt
presented it.
How do you rotate strings? Where did you learn this? Is there an
online source that you can provide?
Thanks, Allan
On 11/20/2018 6:21 PM, jerrysgarage01
wrote:
Wrenches, Drake
You may consider contacting "Batcap"
Wrenches, DrakeYou may consider contacting "Batcap" and bank if they have a
best practice for the battery configuration, this might be it but at least a
starting point. I have had multi string batteries that seamed to like being
rotated through the bank, sounds like alot of work and it is but th
AndrewCorrect, its is all about time, temp cycles will all effect modules,
arial IR testing generally will not show new fractures.JerrySent from my
Verizon, Samsung Galaxy smartphone
Original message From: Andrew Truitt Date:
11/18/18 8:20 PM (GMT-08:00) To: RE-wrenches
Su
WrenchesI spoke to a senior manager at Outback at SPI and they said that there
they are an inverter company and regardless of ownership that would not change.
At that time it was only a rumor and they may have been down playing the entire
idea even after l said that they would be.Jerry
Sent fr
WrenchesEnphase now has a call back feature which has greatly improved
responce1-877-797-4743Have site ID ready when you callJerry
Sent from my Verizon, Samsung Galaxy smartphone
Original message
From: Bill Hennessy
Date: 6/13/18 8:44 AM (GMT-10:00)
To: RE-wrenches
The Radian has 2, 4k, 240 volt inverters, so its different but the way the
computer works it makes the same from the load side of thingsJerry
Sent from my Verizon, Samsung Galaxy smartphone
Original message
From: frenergy
Date: 5/29/18 5:51 PM (GMT-10:00)
To: re-wre
I had a meeting with Pika at SPI 2017 it might have been all the other meetings
but l was not impressed, no technical information on programming or true
applications but thats just me.Jerry
Sent from my Verizon, Samsung Galaxy smartphone
Original message
From: jay
Dat
Ray I have never (yet) had a wire failure in any of my trackers, l have always
used PVC flex tubing connected at both ends with a long line that at any given
point does not move much. I mainly use zomeworks passive sonhle axes trackers
but have done it the same way with array technologes d
DrakeWe have used 40 to 80 gallon water heaters mainly the Rheem Marathon
electric units, we used 15 minutes per person twice a day on the timer, we did
use 7 day timers to have different start times on the weekends. We had great
success with that as a base line.Jerry
Sent from my Verizo
DarrelI put a request to allow the data to be released, expect to have an
answer soonJerry
Sent from my Verizon, Samsung Galaxy smartphone
Original message
From: Darryl Thayer
Date: 2/21/18 10:28 AM (GMT-10:00)
To: RE-wrenches
Subject: Re: [RE-wrenches] Li+ System
WrenchesI think its in the inverter or battery but somewhere before it leaves
the inverter flickering lights indicates the inverter is seeing the issue up
close, a 4 k inverter is 33 amps AC but Over 166 from the 24 volt batteries if
the load if half that with lights and inverter is strugl
KirpalWe have used tge solid state contactors but have not been happy with
there reliability as they ofen have failed in the open position, the old coil
contactors have been far better over time and seam to cost less. FYI, the solid
state high amp contactors live longer with a heat sink.Je
JayNo there is no communication between the battery BMS and the inverterJerry
Sent from my Verizon, Samsung Galaxy smartphone
Original message
From: jay
Date: 1/4/18 8:35 AM (GMT-10:00)
To: RE-wrenches
Subject: [RE-wrenches] blue planet batteries
While we are tal
JayOur office has done research on quit a gew batteries, the Blue Ion Blue
Planets battery has been very good in our testing. Feel free to talk off
listJerry
Sent from my Verizon, Samsung Galaxy smartphone
Original message
From: jay
Date: 1/4/18 8:35 AM (GMT-10:00)
WrenchesTake a look at Fastenall, thats all they doJerry
Sent from my Verizon, Samsung Galaxy smartphone
Original message
From: Glenn Burt
Date: 6/10/17 9:38 AM (GMT-10:00)
To: RE-wrenches , Jerry Caldwell
Subject: Re: [RE-wrenches] Goofy roofing
Mudge Fasteners
WrenchesOur parent company does roofing and works with firestone, l do not know
of any such rule BUT its safe to have the roofer do that and everyone is
protected then why not. Remember it all about the customer and if they feel
happy then we all are happy. But thats just me.Jerry.
Sent
WrenchesAs a matter of practice, we always use conduite, never direct burial,
always copper too, we have had AC and DC in the same trench but with space
seperating the conduits and have had no issues with noise or JHA. As a safety
issue we would not risk direct burial of high voltage DC re
HowieI here in Hawaii, we are slow to approve new inverters and it takes a very
long time to get through permits so l can't say much about the SMA -40
Inverter. Regarding wifi vs hard line, maybe for one unit it would be easy but
we just installed 27 of the SMA 24K -22 at one location and
DaveDid you make your MC Cables, are there any jumpers used, l have seen
crimped terminals cause faults and over time will overheat and fail open. Just
a thought.Jerry
Sent from my Verizon, Samsung Galaxy smartphone
Original message
From: Matthew Sirum
Date: 11/14/16
Wrenches
Does not sound like there is an option to hard wire a shut down switch so here
is an idea l have used. Program the genny to run at 58 Hz. not yp this will
keep the inverters ftom starting up. None of the appliances will know but as
long as the inverter programming does not allow for 58
Wrenches
You can do a carbon pile test but the best way is testing under several
conditions. Here is an option real easy and maybe faster, put a volt meter on
each battery under constant charge conditions, higher volts on one battery
meens high resistance in battery, low volts meens low resistan
Wrenches
We have done transformers for issues just like this with good results, the cost
vs the new wire, conduit and trenching must be done to make sure which
direction. We have had to use paired mcm 300 to make residentual so run the
numbers
Jerry
Sent via the Samsung Galaxy S™ III, an AT&T
Can you use the S-5 brass clamps
Jerry
Sent via the Samsung Galaxy S™ III, an AT&T 4G LTE smartphone
Original message From: Daniel Tittmann
Date:08/09/2016 10:53 AM (GMT-10:00)
To: RE-wrenches
Subject: [RE-wrenches] Standing seam metal roof attachments for
copper roof
W
Wrenches
We have allot of enphase and ya sometimes it a little hard to get them on the
line but we always do. I request the re-inbursments, l dont ever see them as
they end up in the admin office. We have looked at and used a few other
mico-inverters at customer request but they all seem to go o
Wrenches
Make an artificial head by a valve to reduce flow on the outlet side, it might
increase watt demand. They will voltage compensate so reducing volts will not
do it. I have to ask why thats a problem anyway, the pump will turn off if the
level gets to low anyway.
Jerry
Sent via the Sams
Wrenches
We got one, takes a long time to set up, it works great but it seams either we
got a 1 story or a high rise. We also have a crane which is a little costly to
deploy but sure looks cool. Something else we use up to 3 stories is a sizzer
truck, the whole box lifts up to the height, picked
WrenchesI have built 5 solar event trailers, for contractors, promotors, ect.
We can talk off line. call if interested 7078882701Jerry
Sent from my Verizon Wireless 4G LTE smartphone
Original message
From: Chris Schaefer
Date: 5/9/2016 11:55 AM (GMT-10:00)
To: RE-
Have you looked at Cummins, we have have great luck and no programming issues
but battery charging needs to be added foroff grid
Jerry
Sent via the Samsung Galaxy S™ III, an AT&T 4G LTE smartphone
Original message From: Ray Walters
Date:04/28/2016 7:28 AM (GMT-10:00)
To:
What about an SMA Tri Power inverter
Jerry
Sent via the Samsung Galaxy S™ III, an AT&T 4G LTE smartphone
Original message From: Chris Mason
Date:04/28/2016 8:52 AM (GMT-10:00)
To: RE-wrenches
Subject: Re: [RE-wrenches] 480 single phase delta
You will use a 240:480v step
You may want to check the ac voltage with a good "true RMS" meter and see what
the results are, some (most) new Freq Drives, and soft start drives may have an
issue with a high RMSJerry
Sent from my Verizon Wireless 4G LTE smartphone
Original message
From: Roy Butler
ChrisA few questionsAre you drawing from both AC legs from the genny, at max of
2200 watts per leg then the genny should not have an issue but if you upsized
the batteries and as stated by Mike the fuel delivery system cant keep up
because the inverter charge load is higher, steady and for
Can you get a meter main with only one breaker and then get a distribution
panel and put all all loads there
Sent via the Samsung Galaxy S™ III, an AT&T 4G LTE smartphone
Original message From: Gregory Seelhorst
Date:02/17/2016 6:23 AM (GMT-10:00)
To: RE-wrenches
Subject
WrenchesWe have been using nema 3 metal, stainless or even pvc 4x4 boxes with
plastic outdoor rated strain releafs, (same as sma has) also works on enphase,
good wire splice point. Some onspectors like them under modules some like them
exposed, l perfer under looks cleanerJerry
Sent from
We have used Schletter, it was spected on a project and i was not that
impressed, took to long to get what we needed and when it was all done it works
but l like what we have better. I have no reason to stock another product
line.Jerry
Sent from my Verizon Wireless 4G LTE smartphone
-
I have done stuff like this in the past, I would suggest talking to your local
battery distributors and explain what you are doing they may be able to go to
bat with there manufactures for you.
Good luck
Jerry
Sent via the Samsung Galaxy S™ III, an AT&T 4G LTE smartphone
Original mes
can you be more specific as to what fishy means?
jay
On Oct 11, 2015, at 4:04 PM, jerrysgarage01 wrote:
Sounds a little fishy to me, is it a big residential or real small
Jerry
Sent via the Samsung Galaxy S™ III, an AT&T 4G LTE smartphone
Original message
From: Jay
Dat
Sounds a little fishy to me, is it a big residential or real small
Jerry
Sent via the Samsung Galaxy S™ III, an AT&T 4G LTE smartphone
Original message From: Jay
Date:10/11/2015 9:13 AM (GMT-10:00)
To: RE-wrenches
Subject: [RE-wrenches] Pg&e meter reading
I have a clien
WrenchesCheck and confirm that the OB is not set in search, yhis will cause
issues like this.Jerry
Sent from my Verizon Wireless 4G LTE smartphone
Original message
From: jay
Date: 09/21/2015 6:58 AM (GMT-10:00)
To: RE-wrenches
Subject: [RE-wrenches] AC-coupling En
Wrenches
Its been a few years but I have gotten top plates from unirac UL- A racking
that was tilited give them a call or even have them fab-ed up your self.
Jerry
Sent via the Samsung Galaxy S™ III, an AT&T 4G LTE smartphone
Original message From: frenergy
Date:08/21/2015 3
Wrenches
The ability for proper charging has always been an issue way back befor ac
coupling was a thing. Its near an uncontrolled charge and if you tank the
batteries and shut down that's it no charging from the ac coupling component
Jerry
Sent via the Samsung Galaxy S™ III, an AT&T 4G LTE sm
Wrenches
This may should a little like a old wives tail but I used to see the same cell
and or artery failure over the years. Its all about resistance so I started
rotating the batteries, this improved acid levels, life span and capacity.
Just try it out before you laugh it off. One thought i
WrenchesWe stay away from anything with a rubber type boot as it will shrink over time in the shade of the array or not. You all night want to look at the sunmodo out of Washington. Have had no leak issues or installation issues, there is no exposed rubber and the flashing is malleable and can be s
WrenchesI see this working south of the tropic of cancer but at 1000 watts per
meter squared tilted north might work for a month a year but I don't think the
tax credits were proposed for poor performance module installations. I see
enphase annual readings prove the point. Jerry
Sent fr
Wrenchesthe VD is 105 VDC into a charge controller, the engineer is looking
good at it like it a grid tie running at wide open all the time, he will not
listen to sugestions, that's the problem I haveJerry
Sent from my Verizon Wireless 4G LTE smartphone
Original message ---
WrenchesI have had good experiences with these batteries and with the same
issues with the magnum on 12 volts, don't seam to have any issues with my 48
volt systems. We did double up the cables to reduce the high load (overdriving)
the radians with no issues. It's just the cost, but it sho
ower
How do you get around the code requirement for the use of PV wire with a
TL inverter on the existing array?
Sincerely,
Glenn Burt
Sent from my 'smart' phone so please excuse grammar and typos.
From: jerrysgarage01
Sent: 7/24/2015 12:57
To: RE-wrenches
Subject: Re: [RE-wrenches]
SMA used to to do repairs but last I heard they no longer have replacement
parts. I have used the new SMA TL-22 because of the low voltage dc input. If
you added some additional modules to the "B" input it might qualify for the tax
credit (I did say might)
Good luck
Jerry
Sent via the Samsung
Wrenches
We used to use Sharp but now its Trina, containers of 250 watt modules, data
logging has not shown any abnormal power loss. Now that I say this Trina as the
story goes debates there data so that is true it softens the blow a little. I
have seen some another brand that are cracking p
Completely agree, slate brakes if you look at it wrong and that being said who
is responsible to remove the modules to replace the tiles for the next how
many years Jerry
Sent from my Verizon Wireless 4G LTE smartphone
Original message
From: August Goers
Date: 07/08/
Wrenches
We always try to minimize in connection cables as well as home run cables to
the shorted length possible, restating batteries to aid this should always be
considered as well as positive and negative runs
Jerry
Sent via the Samsung Galaxy S™ III, an AT&T 4G LTE smartphone
Orig
Wrenches
For the more traditional roofs we use unitary products but we use the iron ridge
Sent via the Samsung Galaxy S™ III, an AT&T 4G LTE smartphone
Original message From: Dana
Date:06/24/2015 12:09 PM (GMT-10:00)
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] SnapNrack
61 matches