Wrenches
Does not sound like there is an option to hard wire a shut down switch so here 
is an idea l have used. Program the genny to run at 58 Hz. not yp this will 
keep the inverters ftom starting up. None of the appliances will know but as 
long as the inverter programming does not allow for 58 Hz then it will work
Jerry

Sent via the Samsung Galaxy S™ III, an AT&T 4G LTE smartphone

<div>-------- Original message --------</div><div>From: Benn Kilburn 
<b...@skyfireenergy.com> </div><div>Date:09/08/2016  7:00 AM  (GMT-10:00) 
</div><div>To: RE-wrenches <re-wrenches@lists.re-wrenches.org> 
</div><div>Subject: [RE-wrenches] Back-up generator/inverter shut-down relay 
</div><div>
</div>Wrenches,
We are installing 2 SolarEdge SE7600A-US inverters in a grid-tied system that 
has a 15kw back-up generator on an auto transfer switch.

The generator is located in a shed about 300' or more away and the feeders to 
the house are underground.
Inverters are located in the house basement mechanial room along with the house 
electrical panelboard.

We are looking for relay options to shut down the inverters when there is a 
power interruption, before the generator kicks in.  This could be a manual 
reset.

What are some options you have seen/used for something like this?

Thanks,

Benn Kilburn 
CSA Certified Solar Photovoltaic Systems Electrician, SkyFire Energy Inc
14515 – 121A Ave NW | Edmonton, AB | T5L 2T2
P: 780-474-8992 | F: 888-405-5843 | www.skyfireenergy.com
    

WE HAVE MOVED! Please note our new address above.
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to