[RE-wrenches] ESS and Calculated Load in Texas

2025-08-02 Thread Chris Sparadeo via RE-wrenches
Hi all, I’m finding out that some jurisdictions in Texas are requiring ESS output to be equal to or greater than the calculated load of a dwelling. For example, if backing up the whole home, and the service load is calculated at 150A, the ESS would require to continuously output 150A OR EMS is req

Re: [RE-wrenches] Knockouts far from the backplane.

2025-07-25 Thread Chris Sparadeo via RE-wrenches
I fought with 8”x8” gutters for a while, then 10”x10”…and finally made the switch to 12”x12” a few years ago and never looked back. Straight nipples are cheaper and easier to install, and I think they look better as well. With the Sol Ark 15K, the vertical fans require 6” of clearance at the bottom

Re: [RE-wrenches] Induction Cooktops Off-Grid

2025-06-30 Thread Chris Sparadeo via RE-wrenches
Jason, I’ve installed several Sol-Ark inverters in off-grid applications with induction cooktops and have had zero issue. On Thanksgiving last year, a set of off-grid induction stoves pulled over 12 kW without flinching (albeit with 2ea. Sol-Ark 15Ks and a hefty battery bank). I personally don’t

Re: [RE-wrenches] EG4 Mini Split

2025-06-19 Thread Chris Sparadeo via RE-wrenches
My understanding of these mini splits is that there is also an AC input, so you could potentially run an RSS Transmitter from that source panel and install Tigos or something of the sort. On Thu, Jun 19, 2025 at 10:28 AM William Miller via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: >

Re: [RE-wrenches] Wire Sizing - Inverter Outputs with Generator Pass Through

2025-06-17 Thread Chris Sparadeo via RE-wrenches
Jason, This is a great question. I was waiting for responses, because I’ve thought this as well. Typically I have sized load conductors to either Sol Ark output or gen output, depending on which was higher, but you are absolutely right that with grid assist programmed, this number could be higher

Re: [RE-wrenches] Midnite AIO Generator Functionality

2025-05-14 Thread Chris Sparadeo via RE-wrenches
The Discover Link II has AGS capability (much better than typical AIO inverters), but it can only pair with Discover AES Rackmount and Helios. On Wed, May 14, 2025 at 12:08 PM William Bryce via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > I "have been told" that you can do it with a

[RE-wrenches] Battery Conductors and the NEC

2025-04-05 Thread Chris Sparadeo via RE-wrenches
Hey everyone, I’m looking for some clarification on conductor ampacity ratings as they relate to battery cables. My understanding is that the term ‘free air’ wasn’t actually defined in the NEC until 2020 and that conductors installed in a nipple, wire trough, conduit body, or enclosure don’t quali

Re: [RE-wrenches] Battery Conductors and the NEC

2025-03-20 Thread Chris Sparadeo via RE-wrenches
olar > > 17395 Oak Road, Atascadero, CA 93422 > > 805-438-5600 > > www.millersolar.com > > CA Lic. 773985 > > > > > > *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On > Behalf Of *Chris Sparadeo via RE-wrenches > *Sent:* Thursday, M

Re: [RE-wrenches] Measuring an RV for load

2024-11-20 Thread Chris Sparadeo via RE-wrenches
I’ve been drooling over the Fluke 1732 Power Measurement Logger for the past few year but can’t bring myself to spend that kind of money. Have any wrenchers used it? Jay, it looks like there is a product called the Power Watchdog PWD50EPO that is specifically designed for RVs and acts as a surge p

Re: [RE-wrenches] OB Charging/Comms Issues

2024-11-08 Thread Chris Sparadeo via RE-wrenches
> Out of curiosity, what mode are you in and what are the respective set > points for absorb, float, rebulk, etc. For PV vs inverter? > > Tyrone Houck > Oregon Solarworks LLC > LRT #076 > 541-787-1366 > tyr...@oregonsolarworks.com > > > > > On Fri, Nov 8,

Re: [RE-wrenches] OB Charging/Comms Issues

2024-11-08 Thread Chris Sparadeo via RE-wrenches
FM 100, so PV output wouldn’t be visible. On Fri, Nov 8, 2024 at 4:14 PM jay via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > Hi Chris, > > Is this new or has it been always like this? > > jay > > > > > > > > > On Nov 8, 2024, a

[RE-wrenches] OB Charging/Comms Issues

2024-11-08 Thread Chris Sparadeo via RE-wrenches
Hey wrenchers, I have an off-grid customer with a pair of VFX 3648 inverters, a FM 100 charge controller and two eVault classics in open loop. The issue is when the generator is charging the batteries, incoming amperage is all over the place and periodically, gradually drops to 0A then ramps back

Re: [RE-wrenches] Power Crimper and Stripper Recommendations and Questions

2024-10-23 Thread Chris Sparadeo via RE-wrenches
I’ve also noticed that the method of cutting the cable plays a big part in how effectively it goes into the lug. When I use a bandsaw, loose jawed cable cutters or even a really sharp circularity saw blade, strands get slightly frayed and won’t fit properly. I’ve concluded that a long handled and w

Re: [RE-wrenches] Power Crimper and Stripper Recommendations and Questions

2024-10-22 Thread Chris Sparadeo via RE-wrenches
Hi Sam, I purchased the Milwaukee Force Logic crimper a few years ago and it’s been worth every penny. The cutting attachment doesn’t work so well on fine stranded, but the crimper attachment has worked flawlessly. I use it almost every day. https://www.milwaukeetool.com/Products/2679-600C -Chri

Re: [RE-wrenches] All-In-Ones / Sol-Ark fail

2024-10-11 Thread Chris Sparadeo via RE-wrenches
Hi Ray, I don’t think your understanding of the Sol Ark’s PV and LBCO relationship reflects actual functionality. Technically, Sol Ark doesn’t have a formal LBCO, but it has a “shut down” setting that cuts out AC output and can be programmed to cut off and cut back in at selected SOC or voltage se

[RE-wrenches] Schuco 225 Module

2024-10-11 Thread Chris Sparadeo via RE-wrenches
Wrenches, If anyone has a working Schuco MPE225-PS-09 module they are willing to sell me, please contact me off list. Thanks and happy Friday! -Chris Sparadeo ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.or

Re: [RE-wrenches] sol ark battery

2024-10-09 Thread Chris Sparadeo via RE-wrenches
Question for all you Homegrid installers…has anyone found a succinct way to run conduit from the battery enclosure to the Sol Ark? On Wed, Oct 9, 2024 at 7:39 PM Jason Szumlanski via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > Jay, > > I should mention I have a couple of customers w

Re: [RE-wrenches] I sent in my Wrench List dues, have you?

2024-09-27 Thread Chris Sparadeo via RE-wrenches
I can’t count how many times you wrenchers have saved me. Pay honor and dues! On Fri, Sep 27, 2024 at 9:34 PM Jesse Dahl via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > Paid. Great idea! Patreon for PV. > > Sent from my iPhone > > On Sep 27, 2024, at 3:56 PM, Dana Orzel via RE-wrenc

Re: [RE-wrenches] Blue Planet Energy

2024-09-16 Thread Chris Sparadeo via RE-wrenches
Has anyone had successful contact with Blue Planet in recent weeks? Jody from their tech support division does not seem to be working there any more and the company main phone number is giving a bizarre message loop that doesn’t allow you to actually speak to anyone…. On Tue, Aug 6, 2024 at 10:33 

Re: [RE-wrenches] Powerwall 3

2024-09-10 Thread Chris Sparadeo via RE-wrenches
Last time I spoke with Tesla, they did not support either fully off-grid or installations not connect to the internet. Have they changed their policy on this? On Tue, Sep 10, 2024 at 8:19 PM Jason Szumlanski via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > Correct, but there are some

Re: [RE-wrenches] Fm100’s stuck at full charge

2024-09-07 Thread Chris Sparadeo via RE-wrenches
Which Mate are you using? I know the FM100 is only compatible with the Mate 3s. If you are using a Mate 3, this mismatch could possibly be the cause of these issues. On Sat, Sep 7, 2024 at 7:25 PM Maverick Brown via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > Dana > > I have always

Re: [RE-wrenches] discover lithium warranty issues.

2024-08-19 Thread Chris Sparadeo via RE-wrenches
I had a similar experience with Discover warranty recently with a Link II. I correctly installed internal jumpers and external comms cables, and during the commissioning process I heard a popping sound from inside the Link. The center relay board was visibly burnt. After creating a ticket and corre

Re: [RE-wrenches] Sol-Ark with 800A Service

2024-07-18 Thread Chris Sparadeo via RE-wrenches
they specify in their > documentation. > > > > > > > > > > Jason > > > > > > > > > > > > > > > > > > > > On Thu, Jul 18, 2024, 7:23 AM Chris Sparadeo < > sparadeo.ch...@gmail

Re: [RE-wrenches] Sol-Ark with 800A Service

2024-07-18 Thread Chris Sparadeo via RE-wrenches
e not always required. You would need them for power export limiting or > grid peak shaving, but for straight grid-tied with or without battery > backup, you don't need them. > > Jason Szumlanski > Florida Solar Design Group > > > > > On Wed, Jul 17, 2024, 8:41 PM

[RE-wrenches] Sol-Ark with 800A Service

2024-07-17 Thread Chris Sparadeo via RE-wrenches
Hey there wrenchers, I am working on a larger project with 6 Sol-Ark 15K units and an 800A service. The main service conductors are 3 parallel runs of 400 kcmil. I am wondering how to CT these conductors from the master inverter. Sol Ark tech support has not been very helpful so far. I have the in

Re: [RE-wrenches] Primo with tigos Arc fault issue

2024-05-23 Thread Chris Sparadeo via RE-wrenches
Hi Jeremy! We have encountered this his issue years ago with the AO and Fronius suggested we deactivate the arc fault setting. It works, but in order to do so, they give you a special passcode to input. Not an ideal solution. Arc fault detection is not worth compromising . IMO avoid this combinati

Re: [RE-wrenches] Fortress Avalon

2024-05-14 Thread Chris Sparadeo via RE-wrenches
Dave, Just to play devils advocate, what are your reasons as to why high voltage isn’t worthy of OG? I say this being firmly stuck in 48VDC off-grid systems. Kindly, Chris On Tue, May 14, 2024 at 8:42 PM William Miller via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > Dave: > > H

Re: [RE-wrenches] XW Pro Firmware 2.04 melting devices

2024-04-25 Thread Chris Sparadeo via RE-wrenches
Hi Kevin, Let me chime in here. Last year I experienced something nearly identical to what you are describing. 3 ea. XW pros in an off-grid application. Things were working fine, but wanted to upgrade firmware for a comms issue I was having with closed loop BMS and Insight. After the 2.04 upgrade,

Re: [RE-wrenches] Sol-Ark 15K AC Output

2024-03-27 Thread Chris Sparadeo via RE-wrenches
Hi Jason, I talked through this scenario with Sol-Ark tech support a while back. The take away was that grid peak shaving does exist but ONLY on the grid port. If this is an off-grid installation, then land the conductors from the generator on the grid port and select “gen connected to grid port”

Re: [RE-wrenches] EG4 Equipment

2024-02-16 Thread Chris Sparadeo via RE-wrenches
Howie, The EG4 18K and the Fortress Envy are both made by the same manufacturer, LuxPower. Google the LXP 12K and it will all make sense. I can’t speak for EG4, but I know that Fortress has progressed from simply white labeling this unit to doing a significant amount of programming and additional

Re: [RE-wrenches] AC Coupling

2023-10-28 Thread Chris Sparadeo via RE-wrenches
And just to muddy the waters a little, 2023 NEC uses AC Connected and DC connected wording in place of coupled. Same concept, new name. On Sat, Oct 28, 2023 at 5:01 PM Roland - RES via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > Agreed and we'll understand the differences, all of ou

Re: [RE-wrenches] XW Drop in replacement inverter

2023-10-25 Thread Chris Sparadeo via RE-wrenches
Dave, Aren’t AC 1 and AC 2 technically interchangeable? You can set AC priority, Hz and voltage parameters on both inputs. Best, Chris On Wed, Oct 25, 2023 at 3:07 PM Dave Angelini Offgrid Solar via RE-wrenches wrote: > Not getting this Kevin, AC2 has always been the generator input as it > a

Re: [RE-wrenches] Sunny Island AC-Coupled system integration with Fortress E-Vault

2023-10-24 Thread Chris Sparadeo via RE-wrenches
Hi William, That’s an interesting idea to have close loop comms with two separate manufacturers at the same time. In theory I think this could work, but unfortunately, I don’t think SMA and Schneider share the same protocol # for the eVault. I believe SMA uses protocol #2 and Schneider uses #5.

Re: [RE-wrenches] Need a hand with Sunny Island/Sunny boy AC couple

2023-10-22 Thread Chris Sparadeo via RE-wrenches
Hi William, You will want to make sure that the eVaults are all running that same firmware and that terminator switches and battery ID #s are set correctly. High SOC and large incoming current could definitely be the reason why voltage skyrocketed up. Best, Chris On Sat, Oct 21, 2023 at 9:39 PM

Re: [RE-wrenches] Well pump with Sol-Ark

2023-10-11 Thread Chris Sparadeo via RE-wrenches
Hi Bill, I have yet to have an issue with the Sol Ark 12K and water pumps. We have numerous off-grid installations with 3/4 HP well pumps with no issues. I tend to find that compressors and inductive motor loads like chop saws are often an issue. Hope this helps, Chris On Wed, Oct 11, 2023 at 1

Re: [RE-wrenches] sol ark AGS question

2023-09-16 Thread Chris Sparadeo via RE-wrenches
Michael, Sol Ark does not have an explicit or adjustable cool down setting, but it has fixed the problem of dropping the AGS signal under full load. dus...@sol-ark.com can you confirm this? On Fri, Sep 15, 2023 at 5:41 PM Michael Morningstar via RE-wrenches < re-wrenches@lists.re-wrenches.org> w

Re: [RE-wrenches] sol ark AGS question

2023-09-15 Thread Chris Sparadeo via RE-wrenches
In an off-grid scenario I would suggest utilizing the grid connect timer as a Gen warm up. I typically set this qualification time to 30 or 60 seconds. Sol Ark fixed the problem with dropping the 2 wire start under full load, so if this is an issue for you, I would update the firmware. On Fri, Sep

Re: [RE-wrenches] Mojave/ESS

2023-09-01 Thread Chris Sparadeo via RE-wrenches
Bill, My understanding of the Mojave is that it is specifically designed to be paired with AC coupled , grid-interactive inverters. It does not allow for closed loop communications via RS485 or CAN with third party manufacturers and cannot be paralleled with multiple units. Because of these limita

Re: [RE-wrenches] Iron Edison Lithiums

2023-08-29 Thread Chris Sparadeo via RE-wrenches
It’s my understanding that Iron Edison went out of business earlier this year. I did have an issue with a few bad cells in a RB48V300, but after the RMA, no issues to date. And certainly nothing explosive in nature, although I do remember a previous thread about an RB cover blowing off. The take aw

Re: [RE-wrenches] Tech Support Issues with Sensata

2023-05-31 Thread Chris Sparadeo via RE-wrenches
eform. >> >> Stuff like clocks not keeping time, or certain digital controls on >> certain appliances not functioning, is not a warranty claim. Lights >> dimming, or LEDs flickering is not a warranty claim. These are normal >> living off grid, and the only thing

[RE-wrenches] Tech Support Issues with Sensata

2023-05-31 Thread Chris Sparadeo via RE-wrenches
Hi all, I have a client with a Magnum MS 4024- PAE inverter. There are some serious issues with power output quality and according to the client, another installer had started the RMA process while the inverter was still under warranty, however Sensata has not been responsive and has lost track of

Re: [RE-wrenches] Sol-ark without batteries

2023-04-11 Thread Chris Sparadeo via RE-wrenches
Hi William, I think my opinion would be yes, but why? We have a few no-battery installs, but they don’t preform well in grid outage scenarios. If the client is looking for future battery back-up, but not ready to invest just yet, it’s an option. Don’t expect seamless grid forming output with an ou

Re: [RE-wrenches] Phased out Schneider Electric SCP

2023-04-05 Thread Chris Sparadeo via RE-wrenches
Dave, It looks like the dedicated tablet would occupy the Ethernet port of the gateway/facility. That would mean the installer would have to choose between having local system interface OR a solid Ethernet connection. I get that in many cases, the WiFi connection could allow for remote monitoring,

Re: [RE-wrenches] Phased out Schneider Electric SCP

2023-04-04 Thread Chris Sparadeo via RE-wrenches
I don’t like the idea of a system being dependent on the functionality of the insight home/facility or the battery life of a smart device / AC output of the inverter to be able to change settings. As limited as the SCP is, I think it serves a very important function in system operation. I’m all for

Re: [RE-wrenches] Attaching Array To or Through Ply

2023-03-30 Thread Chris Sparadeo via RE-wrenches
In high uplift scenarios, I have used both IronRidge Camo clips on the bottom frame of the module and UFO clips on the top. More expensive, but definitely an all around rock solid approach. -Chris On Thu, Mar 30, 2023 at 9:45 PM Ray Walters via RE-wrenches < re-wrenches@lists.re-wrenches.org> wro

Re: [RE-wrenches] Solark-Fortress Com? (was Fortress Battery Heater)

2023-02-10 Thread Chris Sparadeo via RE-wrenches
to bring the batteries >> up higher every now and then. >> >> So far, things have worked better. >> >> Howie Michaelson >> Sun Catcher >> >> >> On Thu, Feb 9, 2023, 8:10 PM Chris Sparadeo via RE-wrenches < >> re-wrenches@lists.re-wrenche

Re: [RE-wrenches] Solark-Fortress Com? (was Fortress Battery Heater)

2023-02-09 Thread Chris Sparadeo via RE-wrenches
Ray, Establishing CAN is straightforward. Most important steps: -Pins 1,2,3 on eVault go to pins 4,5,6 in that order - Update the eVault with CAN firmware -Use protocol 6 on the battery and protocol 00 on the Sol Ark Closed loop is an important feature that I personally wouldn’t want to pass up.

Re: [RE-wrenches] Low Frequency transformer off-grid inverter options

2023-01-13 Thread Chris Sparadeo via RE-wrenches
I have a client with a large woodworking shop…cabinet table saw, large 20” 240V bench planer, chop saws, compressors and a vacuum system. A single Sol Ark 15K takes care of these loads flawlessly. It seems that that inductive load snag with the smaller models has been resolved with the 15K. Best,

[RE-wrenches] 24V Multi Mode Inverter Options

2023-01-03 Thread Chris Sparadeo via RE-wrenches
Hey there, I have a client with a dead 24V Xantrex SW…It had a good 20+ year run with a few rebuilds. The customer is looking to upgrade their inverter, but keep their 24V battery bank. My first thoughts were Outback FX or Victron Quattro, but I am curious what others are using out there. It seems

Re: [RE-wrenches] Sola-ark cold morning

2022-12-04 Thread Chris Sparadeo via RE-wrenches
Hi Dana, If the battery is in closed loop with the inverter and the battery is cold, it might be limiting charge due to cold temps. Best, Chris On Sun, Dec 4, 2022 at 8:21 AM Dana Orzel via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > Hey Now All Wise ones! > > > > An of gird clie

Re: [RE-wrenches] SolArk and Tigo compatibility

2022-11-16 Thread Chris Sparadeo via RE-wrenches
Sol-Ark user area to power the Tigo > Optimizer TX transmitter) > > I too had to confirm with Sol-Ark to clarify these details. I’ve not > looked at any of their newer manuals to see if some of these notes have > changed. > > Enjoy your day, Nick > > > > On Nov

Re: [RE-wrenches] Fortress Battery Problems

2022-11-16 Thread Chris Sparadeo via RE-wrenches
Hi Ray, I would suggest pushing the latest firmware update to both units. https://www.fortresspower.com/firmware/ re: tech support… I have had good luck speaking directly to Tom: Thomas Honey Fortress Power Applications Engineering (215) 613-4318 x4318 t...@fortresspower.com I agree that Fort

Re: [RE-wrenches] SolArk and Tigo compatibility

2022-11-16 Thread Chris Sparadeo via RE-wrenches
Hi Chris, I echo Ronald’s experience. I wasn’t aware of any memo from Sol Ark suggesting pins 15 and 16 should not be used for the Tigo RSS Transmitter. The 12K and 15K manuals both refrence a 12vdc RSS transmitter to achieve rapid shut down. Best, Chris On Wed, Nov 16, 2022 at 11:21 AM Roland

Re: [RE-wrenches] Simpliphi with SW inverters

2022-10-13 Thread Chris Sparadeo via RE-wrenches
William, I have paired a handful of Trace SW inverters with SimpliPhi batteries. I most often run into this with clients that have 24vdc systems and for whatever reason can’t/won’t make the leap to 48vdc. In my opinion, SimpliPhi’s 24 volt offering is the best in its class. With the older version

Re: [RE-wrenches] sol ark reliability question

2022-10-04 Thread Chris Sparadeo via RE-wrenches
Hi Jay, We have 50+ Sol Ark’s deployed and have just recently RMA’d our first unit for a failed grid input relay. Only failure so far and tech support was awesome throughout the process. I have been very impressed with the 15K unit. We have dropped some serious inductive motor loads on it with no

Re: [RE-wrenches] Discover AES Wall Mount Considerations

2022-09-06 Thread Chris Sparadeo via RE-wrenches
tps://assets.discoverbattery.com/documents/03_aes/805_product_manual/gui-aes-wall-mount-bracket-installation-guide.pdf > > Jason Szumlanski > Florida Solar Design Group > > > > On Tue, Sep 6, 2022, 8:59 AM Chris Sparadeo via RE-wrenches < > re-wrenches@lists.re-wrenches

[RE-wrenches] Discover AES Wall Mount Considerations

2022-09-06 Thread Chris Sparadeo via RE-wrenches
Hi all, I have a project where I am contemplating hanging 9 Discover AES batteries on a wall. Each battery is around 200 lbs, and although the stud wall is a bulky 2”x6” with 16” OC…I have apprehensions that hanging almost a ton of battery on the wall is a good idea. I’ve seen it done in other ins

Re: [RE-wrenches] Do Sunny Islands and Fortress batteries play well together?

2022-09-02 Thread Chris Sparadeo via RE-wrenches
https://learn.fortresspower.com/external/manual/sma/article/copy-of-unpacking-the-batteries?p=dc8b9a9c1b3f410556835193e66f2257c662403dfb3da4056e618e954e8381d2 According to Fortress, they have estables closed loop. However, I don’t have experience with this match up. On Fri, Sep 2, 2022 at 6:16 P

Re: [RE-wrenches] Battery Monitor for Li

2022-09-02 Thread Chris Sparadeo via RE-wrenches
Hi Matt, I typically like to keep battery monitors consistent with inverter manufacturers. Outback and Schneider Electric and Magnum offer good native battery monitors that, when tuned in correctly, work well with LFP. That being said, I have definitely used the Victron BMV 712 paired with Simpli

Re: [RE-wrenches] Magnum inverter/generator integration problems

2022-07-25 Thread Chris Sparadeo via RE-wrenches
Hi Chris, Might sound simple, but I always start by verifying that the generator is NOT in Eco-mode and that it is correctly set to the desired voltage output (seems like in this case that would be 120/240VAC). If those check out, verify that the cord is properly made up and correctly seated in th

Re: [RE-wrenches] WATER COOLED - 1800 RPM - 13KW GENERATORS INQUIRY

2022-07-11 Thread Chris Sparadeo via RE-wrenches
We are desperate for a dependable liquid cooled generator in the 12-16 kW range. If quality is there, I could see us installing 10+ a year. -Chris On Mon, Jul 11, 2022 at 10:45 AM Christopher Warfel via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > The more our local utility tries t

Re: [RE-wrenches] Micro inverter module direct to electric hot water heater

2022-07-04 Thread Chris Sparadeo via RE-wrenches
Hi John, Check out Sun Bandit's offering: https://sunbandit.us/solutions/ -Chris On Thu, Jun 30, 2022 at 9:48 PM John Blittersdorf via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > Glen, You are correct. It is an electric tank water heater according to > Home Depot. > > Thanks for

[RE-wrenches] Eguana Technologies ESS

2022-05-30 Thread Chris Sparadeo via RE-wrenches
Hi Wrenches, Has anyone had experience with the Eguana Technologies Evolve LFP battery storage system? I have only every seen their cut sheet, but am aware that they are partnering (being acquired by?) GM. If anyone has first hand experience with Eguana I’d love to hear it! Kindly, Chris -- Ch

Re: [RE-wrenches] Step up charge controllers?

2022-05-12 Thread Chris Sparadeo via RE-wrenches
Just like Jerry mentioned, I’ve gotten out of similar situations by manipulating the multiple strings in the combiner box to conform to string voltage requirements. Instead of having 2 strings of 3 modules, with one well placed burndy connector, you now have a single string of 6. It can become mor

Re: [RE-wrenches] Sol-Ark 15k

2022-05-07 Thread Chris Sparadeo via RE-wrenches
enches.org> wrote: >>> >>>> That's what I'm thinking. You would need to use a 200A conductor to a >>>> separate load out OCPD before downsizing the wire. I guess there are pros >>>> and cons, but it seems this is geared toward whole house backup f

Re: [RE-wrenches] AC Coupled Tesla system

2022-04-28 Thread Chris Sparadeo via RE-wrenches
Hi William, Each Powerwall can accept 5 kW of continuous charge and 7 kW peak for 10 seconds. These values increase respectively with additional units (i.e. 10kW continuous for 2 units, 15kW for 3 etc). It’s my understanding that each unit can accept 7.6 kW of AC coupled PV. If PV is generating mo

Re: [RE-wrenches] Sol-Ark 15k

2022-04-16 Thread Chris Sparadeo via RE-wrenches
2/0 as it will never meet >> that rating. Just remember its whatever the max output can be plus your >> margin. >> >> On Fri, Apr 15, 2022, 5:44 PM Chris Sparadeo via RE-wrenches < >> re-wrenches@lists.re-wrenches.org> wrote: >> >>> Hi Jason,

Re: [RE-wrenches] Sol-Ark 15k

2022-04-15 Thread Chris Sparadeo via RE-wrenches
Hi Jason, You bring up a valid point….in an off-grid scenario with the 15k do you size the conductors to the continuous capacity, surge capacity or the OCPD of the unit? -Chris On Fri, Apr 15, 2022 at 4:01 PM Jason Szumlanski via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > P.S. IC

Re: [RE-wrenches] Outdoor LiPO batteries

2022-04-06 Thread Chris Sparadeo via RE-wrenches
Hi Jason, Storz Power has a new wall mounted NEMA 3R enclosure that can fit 2 of their 5.12 kWh battery modules and can be stacked up to 80 kWh. Might be worth looking into. -Chris On Wed, Apr 6, 2022 at 3:47 PM frenergy via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > You can easi

Re: [RE-wrenches] Sol-Ark grid tie question

2022-04-01 Thread Chris Sparadeo via RE-wrenches
Hi Jason, If he removes the battery bank, then the battery mode setting would need to be changed to “no battery”. Luckily, very easy setting to access either in front of the unit or remotely. Best, Chris On Fri, Apr 1, 2022 at 2:52 PM Jason Szumlanski via RE-wrenches < re-wrenches@lists.re-wre