y Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two
these outdated requirements or successfully push back?
Thanks!
Chris Sparadeo
VT Master Electrician # EM 08220
C_802-369-4458
___
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: RE-wrenches@lists.re
I fought with 8”x8” gutters for a while, then 10”x10”…and finally made the
switch to 12”x12” a few years ago and never looked back. Straight nipples
are cheaper and easier to install, and I think they look better as well.
With the Sol Ark 15K, the vertical fans require 6” of clearance at the
bottom
re-wrenches.org> wrote:
>
>> Hi James,
>>
>> I this case the cells on only 4 high so they are all low which is an
>> advantage, not so far to drop!
>>
>> I think I can build a platform just out of wood etc that I can slide them
>> out onto if
You can, just put the first battery cable lug on upside down then the
second one right side up. I have installed 2 Systems with a pair of
Midnite powerflo 16 batteries on a single Midnite AIO and they have worked
great.
Chris Lancaster
Earth&Sun Consulting
Sewanee Tn
On Wed, Jul 16, 202
www.members.re-wrenches.org
>>
>> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email ad
Jason,
I’ve installed several Sol-Ark inverters in off-grid applications with
induction cooktops and have had zero issue. On Thanksgiving last year, a
set of off-grid induction stoves pulled over 12 kW without flinching
(albeit with 2ea. Sol-Ark 15Ks and a hefty battery bank). I personally
don’t
My understanding of these mini splits is that there is also an AC input, so
you could potentially run an RSS Transmitter from that source panel and
install Tigos or something of the sort.
On Thu, Jun 19, 2025 at 10:28 AM William Miller via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
>
derate AC
input/output, but it sounded like the conversation went off line.
Any insight would be appreciated.
Best,
Chris
On Fri, Jun 13, 2025 at 7:36 AM Jason Szumlanski via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> I think there was a previous thread on this, but I can&
lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.
://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wr
or going
out of business, we’ve got to try new things from time to time. So far,
Sol-Ark and Enphase seem to be doing OK.
--Chris @ the Oasis Montana
From: jay
Sent: Wednesday, May 14, 2025 10:21 AM
To: RE-wrenches
Cc: ch...@oasismontana.com
Subject: Re: [RE-wrenches] EG4 inverter noise
The Discover Link II has AGS capability (much better than typical AIO
inverters), but it can only pair with Discover AES Rackmount and Helios.
On Wed, May 14, 2025 at 12:08 PM William Bryce via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> I "have been told" that you can do it with a
Hi folks:
I know I'm likely grasping at straws, but does anyone know of an inverter
repair shop in the Salt Lake City area? Or frankly, any Magnum repair shop
west of the Mississippi?
Please feel free t contact me off list.
Chris Daum
Oasis Montana Inc.
406-777-4309 or 4321
406-777
contact me off list.
Best,
Chris Daum
Oasis Montana Inc.
406-777-4309 or 4321
406-777-4309 fax
www.oasismontana.com <http://www.oasismontana.com/>
___
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List A
, but I also see the value in protecting energized
conductors in a raceway. Would love to hear your insights!
Best,
Chris Sparadeo
C_802-369-4458
___
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address
als.
On Thu, Mar 20, 2025 at 1:53 PM William Miller
wrote:
> Chris:
>
>
>
> 1:
>
> From Article 100 (2020 NEC): Free Air (as applied to conductors). Open or
> ventilated environment that allows for heat dissipation and air flow around
> an installed conductor. (I did no
Hi folks:
Does anyone have a generator start module for a Xantrex 5548+ inverter (circa
2006)?
Feel free to contact me off list.
Best,
Chris Daum
Oasis Montana Inc.
406-777-4309
406-777-4309 fax
www.oasismontana.com
___
List sponsored by Redwood
connections.
Use a torque wrench and crows foot wrenches.
Also you will need a vacuum pump to vacuum the lines. A lot of installers
don't and it will kill the compressor over time.
Chris Mason
Solar systems designer
Generac Generators Industrial technician
Comet Systems Ltd DBA Comet
If you want to avoid my rant, just go to the bolded, italicized,
underline question below. Thank you, Chris
We are in a situation with our island cooperative, where we have a
former Vermont Electric Coop person as our president. He has been for 8
years I believe. In my opinion based upon his
gs:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches
Hi folks:
Do you know of a remote battery monitor that tells cell voltages? We're
looking for a better way to monitor FLA batteries.
Chris Daum
Oasis Montana Inc.
406-777-4309 or 4321
406-777-4309 fax
www.oasismontana.com <http://www.oasismon
Hi folks:
I suspect I am wasting time.but is there any contact number for Magnum or
Sensata tech support? I think they are down the tubes.
Best,
Chris Daum
Oasis Montana Inc.
406-777-4309 or 4321
406-777-4309 fax
www.oasismontana.com <http://www.oasismontana.
protector. The
device has Bluetooth capability and also monitors power characteristics
(volts, amps, kW, kWh). It sounds like this is what you are looking for.
Around $300
Kindly,
Chris
On Wed, Nov 20, 2024 at 7:05 PM Jay via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
>
Also check out Thunderbird Solar, https://www.thunderbirdsolar.com/ -- and
catch up with Cody: Cody Burgdorff cody.burgdo...@thunderbirdsolar.com
<mailto:cody.burgdo...@thunderbirdsolar.com>
Their PICOCELL product moves a LOT of water!
TGIF,
Chris Daum
Oasis Montana Inc.
406-77
Genpro Energy (https://genproenergy.com/) also offers smallish racks where the
user provides the pole. FYI.
Chris Daum
Oasis Montana Inc.
406-777-4309 or 4321
406-777-4309 fax
www.oasismontana.com <http://www.oasismontana.com/>
From: RE-wrenches On Behalf Of Kent
via RE-wrenche
> Out of curiosity, what mode are you in and what are the respective set
> points for absorb, float, rebulk, etc. For PV vs inverter?
>
> Tyrone Houck
> Oregon Solarworks LLC
> LRT #076
> 541-787-1366
> tyr...@oregonsolarworks.com
>
>
>
>
> On Fri, Nov 8,
FM 100, so PV output wouldn’t be visible.
On Fri, Nov 8, 2024 at 4:14 PM jay via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> Hi Chris,
>
> Is this new or has it been always like this?
>
> jay
>
>
>
>
>
>
>
> > On Nov 8, 2024, a
!
Chris Sparadeo
___
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cg
s are always
appreciated.
Best,
Chris Daum
Oasis Montana Inc.
406-777-4309 or 4321
406-777-4309 fax
www.oasismontana.com <http://www.oasismontana.com/>
___
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenche
archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
Hi folks: Does anyone have a contact number or person for warranty issues
regarding Trojan batteries? We have an elderly customer who purchased some
this summer and we are getting the runaround, to put it mildly. Thanks in
advance!
Sincerely,
Chris Daum
Oasis Montana Inc.
406-777-4309
I’ve also noticed that the method of cutting the cable plays a big part in
how effectively it goes into the lug. When I use a bandsaw, loose jawed
cable cutters or even a really sharp circularity saw blade, strands get
slightly frayed and won’t fit properly. I’ve concluded that a long handled
and w
-Chris
On Tue, Oct 22, 2024 at 2:49 PM Sam Haraldson via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> Wrenches,
>
> We are embarking on a project in November that has enough battery cable
> and terminal crimps to justify researching and buying power tools specific
> t
ess & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org
We got caught once by this, the storage inverter was doing strange stuff,
tripping breakers, etc.
When I realized it was 120/208, we changed to a storage inverternwhich was
specified for the arrangement and never had another issue.
It's not just the voltage, the included angle between the cycles is
settings,
but as long as the battery is connected, the Sol Ark sees that voltage and
PV production if available, solar production will recharge batteries,
regardless of AC output.
But yes, I agrees that AIO’s could use a healthy dose of redundancy to
allow for less fickle output.
-Chris
On Fri
Wrenches,
If anyone has a working Schuco MPE225-PS-09 module they are willing to sell
me, please contact me off list.
Thanks and happy Friday!
-Chris Sparadeo
___
List sponsored by Redwood Alliance
Pay optional member dues here: http://re
Question for all you Homegrid installers…has anyone found a succinct way to
run conduit from the battery enclosure to the Sol Ark?
On Wed, Oct 9, 2024 at 7:39 PM Jason Szumlanski via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> Jay,
>
> I should mention I have a couple of customers w
Out of curiosity, what battery form factor i.e. FLA, Lithium and
manufacturer are your OB inverters running on?
Christopher
On Mon, Sep 30, 2024, 19:52 Wayne Irwin via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> Hurricane Helene has taught us the hard way that Enphase batteries wit
I can’t count how many times you wrenchers have saved me. Pay honor and
dues!
On Fri, Sep 27, 2024 at 9:34 PM Jesse Dahl via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> Paid. Great idea! Patreon for PV.
>
> Sent from my iPhone
>
> On Sep 27, 2024, at 3:56 PM, Dana Orzel via RE-wrenc
I've only used Enphase on roofs and ground mounts. I have no complaints.
I chose them over SolarEdge and I think it has worked out. Chris
On 2024-09-25 14:00, August Goers via RE-wrenches wrote:
> I've noticed that the Enphase compatibility calculator needs some work - it
gi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & e
.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Addre
Has anyone had successful contact with Blue Planet in recent weeks? Jody
from their tech support division does not seem to be working there any more
and the company main phone number is giving a bizarre message loop that
doesn’t allow you to actually speak to anyone….
On Tue, Aug 6, 2024 at 10:33
Last time I spoke with Tesla, they did not support either fully off-grid or
installations not connect to the internet. Have they changed their policy
on this?
On Tue, Sep 10, 2024 at 8:19 PM Jason Szumlanski via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> Correct, but there are some
Which Mate are you using? I know the FM100 is only compatible with the Mate
3s. If you are using a Mate 3, this mismatch could possibly be the cause of
these issues.
On Sat, Sep 7, 2024 at 7:25 PM Maverick Brown via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> Dana
>
> I have always
Hi folks:
Is there any contact information for warranty issues on bum Kilovault
batteries (with unfortunate BMS issues)?
Best,
Chris Daum
Oasis Montana Inc.
406-777-4309 or 4321
406-777-4309 fax
www.oasismontana.com <http://www.oasismontana.
I had a similar experience with Discover warranty recently with a Link II.
I correctly installed internal jumpers and external comms cables, and
during the commissioning process I heard a popping sound from inside the
Link. The center relay board was visibly burnt. After creating a ticket and
corre
-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> h
t can provide a
direction will be appreciated. Generator is 20KW Generwreck...er...Generac.
The installer is the customer's electrician. Thanks so much!
Best,
Chris Daum
Oasis Montana Inc.
406-777- 4321
406-777-4309 fax
www.oasismontana.com
___
List
to in the
past.
Christopher
On Fri, Jul 19, 2024 at 12:30 PM jay via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> HI Chris,
>
> Can you give us more data?
>
> Like is this a new problem, or it only started after X?
>
> Since its not seeing the port ( NA) it could b
atible with residential units.
On Thu, Jul 18, 2024 at 11:51 AM Dan Lepinski, P.E. wrote:
> Chris,
>
> If the only goal is to avoid backfeeding the grid, in the configuration
> as described, the inverter will sense any outbound current and reduce its
> output accordingly.
>
&
Hey folks:
Who's a good person to recommend for an installation in Portland, OR?
Please feel free to contact me off-list.
Best,
Chris Daum
Oasis Montana Inc.
406-777-4309 or 4321
406-777-4309 fax
www.oasismontana.com <http://www.oasismon
e not always required. You would need them for power export limiting or
> grid peak shaving, but for straight grid-tied with or without battery
> backup, you don't need them.
>
> Jason Szumlanski
> Florida Solar Design Group
>
>
>
>
> On Wed, Jul 17, 2024, 8:41 PM
included 300A CTs
and I do know that they make a 600A CT, but its physical size and
rating aren't a good fit. Does anyone have experience with either a Sol Ark
or third party CT that might fit this 800A configuration?
Kindly,
Chris Sparadeo
___
Hi folks:
Does anyone happen to have three of the PV-MLE265HD modules available?
Please feel free to contact me off list.
Best,
Chris Daum
Oasis Montana Inc.
406-777-4309
406-777-4309 fax
www.oasismontana.com <http://www.oasismontana.
combination by
all means.
Kindly,
Chris
On Thu, May 23, 2024 at 7:18 PM Jeremy Rodriguez via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> Has anyone had issues with Tigo TS4AF rapid shut down devices along with
> their transmitter, causing arc fault codes with a Fronius Pr
Anybody know where a residential-sized floating array (for twelve Canadian
Solar 410W modules) might be had? All the companies I’m contacting say I’m too
small a fishie to lay out a line… Please feel free to contact me off-list.
Thanks.
Chris Daum
Oasis Montana Inc.
406-777-4309
406-777
Dave,
Just to play devils advocate, what are your reasons as to why high voltage
isn’t worthy of OG?
I say this being firmly stuck in 48VDC off-grid systems.
Kindly,
Chris
On Tue, May 14, 2024 at 8:42 PM William Miller via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
ure out exactly what his problems
are - but he's not ready to throw in the towel on his inverter.
Any takers? Please feel free to contact me off list.
Best,
Chris Daum
Oasis Montana Inc.
406-777-4309 or 4321
406-777-4309 fax
www.oasismontana.com <http
your generator frequency, voltage and THD. In my case, I found that the
generator behaved well in bypass and terribly when the inverters were
present.
Good luck on this one!
Chris Sparadeo
On Thu, Apr 25, 2024 at 1:51 PM Ray Walters via RE-wrenches <
re-wrenches@lists.re-wrenches.org>
the system. Yeah, good planning, right?
In terms of getting AC power out of his 'new' 6X array, Enphase won't work
since he doesn't have an Enphase system. We're looking at perhaps SMA or
Chilcon (so the size of the wire run won't be so astronomical). Any
sug
tp://www.members.re-wrenches.org
>>>
>>> ___
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
&
Hi Jason,
I talked through this scenario with Sol-Ark tech support a while back. The
take away was that grid peak shaving does exist but ONLY on the grid port.
If this is an off-grid installation, then land the conductors from the
generator on the grid port and select “gen connected to grid port”
Hear hear! www.mtsolar.us <http://www.mtsolar.us> Great folks with whom to
do business.
Chris Daum
Oasis Montana Inc.
406-777-4309 or 4321
406-777-4309 fax
www.oasismontana.com <http://www.oasismontana.com/>
From: RE-wrenches On Behalf Of Dave
Tedeyan via RE-wrenches
m not dying on
the hill of LFP, but I will say that I am firmly in support of the
measurable improvements they have made for my customers. Paired with remote
monitoring, the truck rolls a lot less.
Kindly,
Chris
On Fri, Feb 16, 2024 at 4:33 PM Dan Fink via RE-wrenches <
re-wrenches@
re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.o
mber dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one do
are under consideration.
Best,
Chris Daum
Oasis Montana Inc.
406-777-4309 or 4321
406-777-4309 fax
www.oasismontana.com <http://www.oasismontana.com/>
___
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrench
ing. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update
Hi folks:
I have a fellow looking for six of the Solarworld 260s. If you got ‘em and
wish to part with them, please contact me off list.
Happy new year!
Chris Daum
Oasis Montana Inc.
406-777-4309 or 4321
406-777-4309 fax
www.oasismontana.com <http://www.oasismontana.
e any information of use. Happy
holidays!
Sincerely,
Chris Daum
Oasis Montana Inc.
406-777-4309 or 4321
406-777-4309 fax
www.oasismontana.com <http://www.oasismontana.com/>
___
List sponsored by Redwood Alliance
Pay optional member dues here
lready set 03E Max Charge Rate
up to 100% I reckon. If not give it a shot and see if it will approach the 60
Amps DC per inverter rating. Anyway these RTR menus are from 2014 +/- so I
don't know if you have the same menus. Hope this helps. Chris Worcester
chris@solarwindworks.com530-448-9
e-wrenches.org
>
>
>
> <https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient>
> Virus-free.www.avast.com
> <https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-emai
Dear people:
I’ve got a fella looking for three each of the Sunmodule Plus 260 panels or
Solarworld SW 260 mono panels. Got anything? I suspect used would be fine.
Please feel free to contact me off list.
Thanks and stay warm!
Chris Daum
Oasis Montana Inc.
406-777-4309 or 4321
406-777
And just to muddy the waters a little, 2023 NEC uses AC Connected and DC
connected wording in place of coupled. Same concept, new name.
On Sat, Oct 28, 2023 at 5:01 PM Roland - RES via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> Agreed and we'll understand the differences, all of ou
Dave,
Aren’t AC 1 and AC 2 technically interchangeable? You can set AC priority,
Hz and voltage parameters on both inputs.
Best,
Chris
On Wed, Oct 25, 2023 at 3:07 PM Dave Angelini Offgrid Solar via RE-wrenches
wrote:
> Not getting this Kevin, AC2 has always been the generator input as
.
Kindly,
Chris
On Tue, Oct 24, 2023 at 10:40 AM MDElectricSolar via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> I would tear all the sunny boys and sunny islands out and install two 15
> kW Sol-Arks, problem solved. DC coupled. I've done this several times n
Hi William,
You will want to make sure that the eVaults are all running that same
firmware and that terminator switches and battery ID #s are set correctly.
High SOC and large incoming current could definitely be the reason why
voltage skyrocketed up.
Best,
Chris
On Sat, Oct 21, 2023 at 9:39
Hi folks:
I have a customer looking for an older (10 year?) GS8048 inverter – to match up
with one they’ve got. If you have such a beast available, please feel free to
contact me off list.
Best,
Chris Daum
Oasis Montana Inc.
406-777-4309 or 4321
406-777-4309 fax
www.oasismontana.com <h
Hi Bill,
I have yet to have an issue with the Sol Ark 12K and water pumps. We have
numerous off-grid installations with 3/4 HP well pumps with no issues. I
tend to find that compressors and inductive motor loads like chop saws are
often an issue.
Hope this helps,
Chris
On Wed, Oct 11, 2023 at
G'day All,
Having a difficult time locating a distributor for Schneider BTS cables for
a twin set of XW Pro 6848's. Schneider will not sell these to installers.
Please provide me with a source/supplier.
Much Appreciated,
Christopher-
Chris Schaefer’s
*Tel 585-229-2083 or Cell 58
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>
(2 wire start) generator more load responsive?
Thanks for any and all advice!
Chris Daum
Oasis Montana Inc.
406-777-4309 or 4321
www.oasismontana.com <http://www.oasismontana.com>
___
List sponsored by Redwood
org> wrote:
> Chris,
> Just so that I understand correctly, are you saying that new firmware
> allows for generator cool down?
>
>
> On Fri, Sep 15, 2023 at 2:33 PM Jason Szumlanski via RE-wrenches <
> re-wrenches@lists.re-wrenches.org> wrote:
>
>> I saw that
In an off-grid scenario I would suggest utilizing the grid connect timer as
a Gen warm up. I typically set this qualification time to 30 or 60 seconds.
Sol Ark fixed the problem with dropping the 2 wire start under full load,
so if this is an issue for you, I would update the firmware.
On Fri, Sep
or 'line tamer' available that will
work for this appliance's operation? Any ideas would be greatly
appreciated. He's rather loathe to replace his inverter if he doesn't need
to.
Best,
Chris Daum
Oasis Montana Inc.
406-777-4309 or 4321
406-777-4309 fax
www.oasis
limitations,
I have not yet used this product. I would be interested in hearing any
first hand experience as well.
Kindly,
Chris
On Fri, Sep 1, 2023 at 12:24 PM frenergy via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> Wrenchers,
>
> We haven't done any
It’s my understanding that Iron Edison went out of business earlier this
year. I did have an issue with a few bad cells in a RB48V300, but after the
RMA, no issues to date. And certainly nothing explosive in nature, although
I do remember a previous thread about an RB cover blowing off. The take
aw
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wre
Hi Folks:
I’m looking for a Fronius PRIMO 6.0-1 inverter; used but in good working order
would be OK too. If you have access to one, please contact me off list.
THANKS.
Best,
Chris Daum
Oasis Montana Inc.
406-777-4309
___
List sponsored by
Hi folks:
Anybody got one of these, or know where I can get one? Please contact me off
list.
Have a happy and safe 4th!
Chris Daum
Oasis Montana Inc.
406-777-4309
406-777-4309 fax
www.oasismontana.com <http://www.oasismontana.com/>
__
Hi folks:
Any chance one of you has this auto gen start module they can part with? I do
NOT need the one with the network option…those are readily available. Please
contact me off list if you have one.
Best,
Chris Daum
Oasis Montana Inc.
406-777-4309
406-777-4309 fax
,
but I haven’t put in the head banging against the wall effort to track down
tech support that the previous installer had.
I agree, a THD would be a good next step.
Kindly,
Chris
On Wed, May 31, 2023 at 5:06 PM Bradley Bassett via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
>
of the
case. They are asking for a new case to be initiated, but the inverter is
now out of warranty. Has anyone out there had similar lack luster support
issues with Sensata?
Best,
Chris
--
Chris Sparadeo
C_802-369-4458
H_802-728-3059
___
List
We haven’t sold these modules, but here’s some information:
https://www.mitsubishielectricsolar.com/warranty-information/
Good luck!
Chris Daum
Oasis Montana Inc.
406-777-4309 or 4321
406-777-4309 fax
www.oasismontana.com <http://www.oasismontana.com/>
From: RE-wrenches On Beh
Hey folks: On a stacked Outback Radian system, has anyone encountered a HUB 53
fault as noted on the MATE3s?
Thanks in advance!
Best,
Chris Daum
Oasis Montana Inc.
406-777-4309 or 4321
406-777-4309 fax
www.oasismontana.com <http://www.oasismontana.
Hi folks:
If anyone’s got one to part with, please contact me off list. I do NOT need
the AGS-N…
Chris Daum
outage. Also, don’t expect to connect a generator via Sol Ark for pass
through during and outage.
My $0.02 is to convince the client to tag on a battery, albeit minimal
capacity.
Kindly,
Chris
On Tue, Apr 11, 2023 at 4:22 PM Christopher Warfel via RE-wrenches <
re-wrenches@lists.re-wrenches.
1 - 100 of 1102 matches