Hi folks:
 
So, we have a customer (equipment not acquired from us)  with an older OUTBACK 
VFX3524, charging their 3 X RB24V200 ReLion LFP batteries vis a vis one leg of 
their generator.  The battery is capable of up to 200A recharge though the 
manufacturer recommends 10~100A.  The customer has a 240VAC generator with two 
120VAC legs; customer wants to bump up the charging to over 22.5A, preferably 
more; they’re running their gennie a lot to get a rather slow rate of charge 
from the inverter’s charger. Presently the customer has the Inverter/charger 
connected through the FLEXware 250 enclosure. There is not a busbar in place.  
The idea presented is to use an external battery charger that would pull from 
the other leg of the 240VAC gen set to supplement the charging capability.   
The question becomes: can we use a busbar with disparate amps charging to bump 
up the charging rate for the LiFePo4 battery?  Outback techs are saying the 
VFX3524 is not LiFePo4 compatible, but they also say they need to stack another 
inverter. I think we are looking at letting the smoke out of the 
least-producing charger by pushing amperages back.   What do y’all think?  Any 
and all ideas are under consideration.
 
Best,
 
Chris Daum
Oasis Montana Inc.
406-777-4309 or 4321
406-777-4309 fax
www.oasismontana.com <http://www.oasismontana.com/>  
 
 
 
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to