And it works as Howie described with Fortress inverters, at least in my
only grid-tie Fortress. Only all pv inputs shut down, not the inverter.

On Thu, Oct 10, 2024 at 7:48 PM Howie Michaelson via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:

> Hi all,
> The response from Midnite:
>  * On a PV insulation fault, only the pv shuts down.  On other pv faults
> (I'm not sure what they would be) they say that it is required to shut off
> the AC.
> * In stacked systems, if one inverter errors off that does not bring down
> the other AIOs.
>
> Howie
>
>
> On Thu, Oct 10, 2024, 7:19 PM jay via RE-wrenches <
> re-wrenches@lists.re-wrenches.org> wrote:
>
>> Seems like this is a firmware setting and should be adjustable.  If lo
>>
>> On Oct 10, 2024, at 3:59 PM, Lou Russo via RE-wrenches <
>> re-wrenches@lists.re-wrenches.org> wrote:
>>
>> Aloha All,
>>
>> Thank you Jason. This is a huge and surprising issue. So much so that I
>> dropped what I was doing and called Sol-Ark to confirm. Mind you this was
>> level 1 support, but I was told this is what the Sol-Arks are supposed to
>> do and it is a feature not a bug. Their take is if there is any fault on
>> any one string, the Sol-Ark assumes the worst and shuts everything down.
>>
>> I wonder what solutions could be implemented on future installs to
>> prevent this from happening?
>>
>> Aloha,
>>
>> Lou Russo
>> Owner
>> l...@spreesolarsystems.com
>> Office - 808 345 6762
>> Spree Solar Systems LLC
>> CT-34322
>>
>>
>>
>> On Thu, Oct 10, 2024 at 11:45 AM Jason Szumlanski via RE-wrenches <
>> re-wrenches@lists.re-wrenches.org> wrote:
>>
>>> I think it's more likely water in a J-box or possibly physical damage,
>>> but someone passed by the property and did not observe any physical damage
>>> to the array.
>>>
>>> Jason Szumlanski
>>> Principal Solar Designer | Florida Solar Design Group
>>> NABCEP Certified Solar Professional (PVIP)
>>> Florida State Certified Solar Contractor CVC56956
>>> Florida Certified Electrical Contractor EC13013208
>>>
>>>
>>> On Thu, Oct 10, 2024 at 5:41 PM Jay <jay.pe...@gmail.com> wrote:
>>>
>>>> Jason
>>>> What’s the possibllity it was a lighting strike?
>>>>
>>>> Jay
>>>>
>>>> On Oct 10, 2024, at 2:57 PM, Jason Szumlanski via RE-wrenches <
>>>> re-wrenches@lists.re-wrenches.org> wrote:
>>>>
>>>> 
>>>> We have been talking a lot recently about all-in-ones. I just had a
>>>> massive fail during Hurricane Milton with a quad Sol-Ark 15K off-grid
>>>> system that deserves some discussion about whether AIO is a good idea if it
>>>> can't build in some resilience to errors. I'm not sure if the new Midnite
>>>> unit is better in this respect, but this is what happened to the Sol-Ark
>>>> system...
>>>>
>>>> Four inverters, each with 4 strings of PV paralleled to 2 MPPT per
>>>> inverter. One of the slave units developed some sort of PV DC fault during
>>>> the storm. This caused the slave inverter to shut down and throw an error,
>>>> which in turn caused a parallel fault across all four inverters. Power
>>>> output ceases at that point. Apparently the system keeps resetting because
>>>> I have a cell modem that uploads data to Sol-Ark, but that cell modem is
>>>> powered by the inverter outputs, so it must be getting power at least
>>>> intermittently. The rest of the loads are basically flatlined according to
>>>> the Sol-Ark data. It's mostly air conditioners, so they probably can't turn
>>>> on fast enough before the PV fault causes another shutdown.
>>>>
>>>> So, in essence, one of 16 strings of PV develops a fault, and that
>>>> causes all four inverters to malfunction? What is the point of redundancy
>>>> if a fault of one results in a fault of all?! If there is a true PV input
>>>> fault, shouldn't that just shut down that MPPT, or perhaps all of the PV DC
>>>> input to that inverter? And why can't this inverter continue to invert
>>>> power from the batteries and charge from a generator when there is a DC
>>>> input fault that could be programmatically isolated and ignored?
>>>>
>>>> This is a bad design in my opinion, and something I hadn't considered.
>>>> If the faulted inverter can't function with a DC input fault, it should
>>>> just take itself out of the game. (This is 120/240 split phase, BTW). Is
>>>> this how all AIO inverters work? One inverter fault on the DC side kills
>>>> all paralleled units' AC output? Not good.
>>>>
>>>> This is a completely off-grid system on a remote island with no vehicle
>>>> access, so it's not exactly easy to do a "truck roll" on this one,
>>>> especially post-hurricane. To make matters worse, the generator was running
>>>> at the time of the fault, as it was being signaled to run because the
>>>> battery had reached the assigned charge voltage. The fault also killed the
>>>> 2-wire start signal from the master, so the system also stopped passing
>>>> through generator power to the loads. The house is dark.
>>>>
>>>>
>>>> Jason Szumlanski
>>>> Florida Solar Design Group
>>>>
>>>> _______________________________________________
>>>> List sponsored by Redwood Alliance
>>>>
>>>> Pay optional member dues here: http://re-wrenches.org
>>>>
>>>> List Address: RE-wrenches@lists.re-wrenches.org
>>>>
>>>> Change listserver email address & settings:
>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>
>>>> There are two list archives for searching. When one doesn't work, try
>>>> the other:
>>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>
>>>> List rules & etiquette:
>>>> http://www.re-wrenches.org/etiquette.htm
>>>>
>>>> Check out or update participant bios:
>>>> http://www.members.re-wrenches.org
>>>>
>>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> Pay optional member dues here: http://re-wrenches.org
>>>
>>> List Address: RE-wrenches@lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> There are two list archives for searching. When one doesn't work, try
>>> the other:
>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org
>>>
>>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>>
>> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>

-- 

*Kirk Herander / **kirkh@vermont.solar <kirkh@vermont.solar>*

*Owner|Principal, VT Solar, LLC*

*Celebrating our 33st Anniversary 1991-2024!!*

dba Vermont Solar Engineering

802.559.1225
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to