Interesting, because that has not been my experience, and Solark confirmed that when the inverter shuts down, the PV charging does too.  Maybe that has changed in a firmware update.  Or possibly, the inverter went through LBCO on the output as you mentioned, then dropped further through the night to shut down completely by the next morning.  Either way, the system has required manually resetting to start charging again.

Ray Walters

On 10/11/2024 3:57 PM, Chris Sparadeo wrote:
Hi Ray,

I don’t think your understanding of the Sol Ark’s PV and LBCO relationship reflects actual functionality. Technically, Sol Ark doesn’t have a formal LBCO, but it has a “shut down” setting that cuts out AC output and can be programmed to cut off and cut back in at selected SOC or voltage settings,  but as long as the battery is connected, the Sol Ark sees that voltage and PV production if available, solar production will recharge batteries, regardless of AC output.

But yes, I agrees that AIO’s could use a healthy dose of redundancy to allow for less fickle output.

-Chris

On Fri, Oct 11, 2024 at 5:26 PM Ray Walters via RE-wrenches <re-wrenches@lists.re-wrenches.org> wrote:

    Another reason to do separate charge controllers is Low battery.
    If the AIO inverter hits its LBCO, then it takes out the PV input
    as well. Then the draw of the BCM takes what's left in the
    battery, and you're into a dark start.  Generator won't even
    help.  AIOs are easy to install, but not as full proof as DC
    coupled PV systems.  Also, the inter communication is a major
    issue.  I've seen inter connected charge controllers take each
    other out, which really defeats the redundancy of having multiple
    units.  I'm sure many on the list will question my wisdom; but I
    usually don't interconnect any of the equipment from a comms stand
    point.  I use open loop charging based on voltage.

    I once had a pinched temp sensor, that thought the batteries were
    at 5000 deg Kelvin.  It shut all 4 inverters down.  My most
    reliable multiple inverter setup is a four SW4048 system that is
    now 24 years old. Each inverter feeds one leg of two load
    centers.  No comms, No 240 vac loads.  No shut downs.  That is the
    gold standard, and none of the AIO stuff, nor the module level
    rapid shutdown etc, can even get close to the level of reliability
    we had in the past.  In the off grid world, shut downs can be life
    threatening, and all the additional "safety" stuff added to the
    code since, has actually made my off grid customers less safe.

    You have to think what happens if the battery gets low, and no one
    is home?  Can it recover on its own, like a traditional DC coupled
    Lead acid system?  Basically, If the system can't hit LBCO,
    recharge the next day, and automatically turn loads back on, we've
    gone backwards in our designs, and equipment selection. AIOs are
    inferior if they can't achieve this basic functionality.  If UL
    standards are causing this, then those standards are incorrect for
    critical off grid and backup applications.

    Ray Walters
    Remote Solar

    On 10/10/2024 4:02 PM, Eric Smiley via RE-wrenches wrote:
    Install stand-alone charge controllers. That is the only way to
    get redundancy.

    Eric Smiley (he/him) - Design Manager
     250.703.6004
    e...@vecoop.ca
     888.386.0116
    3-4997 Polkey Rd, Duncan BC, V9L 6W3
    
<https://www.google.com/maps/search/4997+Polkey+Rd,%0D%0A++++++++++++++++++++++++++Duncan+BC,+V9L+6W3?entry=gmail&source=g>
    viridiansolar.ca
    
<https://www.google.com/url?q=https://viridiansolar.ca&source=gmail-html&ust=1702155901939000&usg=AOvVaw3SHpXB-WRSlzWmjpz4htqG>


                

    Viridian Solar honours the ancestral grounds on which we live and
    provide services, recognising that these lands are unceded
    Indigenous territory. We are steadfast in our commitment to
    reconciliation and acknowledge the rich history and traditions
    that characterise this land that we all consider home.



    On Thu, 10 Oct 2024 at 14:59, Lou Russo via RE-wrenches
    <re-wrenches@lists.re-wrenches.org> wrote:

        Aloha All,

        Thank you Jason. This is a huge and surprising issue. So much
        so that I dropped what I was doing and called Sol-Ark to
        confirm. Mind you this was level 1 support, but I was told
        this is what the Sol-Arks are supposed to do and it is a
        feature not a bug. Their take is if there is any fault on any
        one string, the Sol-Ark assumes the worst and shuts
        everything down.

        I wonder what solutions could be implemented on future
        installs to prevent this from happening?

        Aloha,

        Lou Russo
        Owner
        l...@spreesolarsystems.com
        Office - 808 345 6762
        Spree Solar Systems LLC
        CT-34322



        On Thu, Oct 10, 2024 at 11:45 AM Jason Szumlanski via
        RE-wrenches <re-wrenches@lists.re-wrenches.org> wrote:

            I think it's more likely water in a J-box or possibly
            physical damage, but someone passed by the property and
            did not observe any physical damage to the array.

            Jason Szumlanski
            Principal Solar Designer | Florida Solar Design Group
            NABCEP Certified Solar Professional (PVIP)
            Florida State Certified Solar Contractor CVC56956
            Florida Certified Electrical Contractor EC13013208


            On Thu, Oct 10, 2024 at 5:41 PM Jay <jay.pe...@gmail.com>
            wrote:

                Jason
                What’s the possibllity it was a lighting strike?

                Jay

                On Oct 10, 2024, at 2:57 PM, Jason Szumlanski via
                RE-wrenches <re-wrenches@lists.re-wrenches.org> wrote:

                
                We have been talking a lot recently about
                all-in-ones. I just had a massive fail during
                Hurricane Milton with a quad Sol-Ark 15K off-grid
                system that deserves some discussion about whether
                AIO is a good idea if it can't build in some
                resilience to errors. I'm not sure if the new
                Midnite unit is better in this respect, but this is
                what happened to the Sol-Ark system...

                Four inverters, each with 4 strings of PV paralleled
                to 2 MPPT per inverter. One of the slave units
                developed some sort of PV DC fault during the storm.
                This caused the slave inverter to shut down and
                throw an error, which in turn caused a parallel
                fault across all four inverters. Power output ceases
                at that point. Apparently the system keeps resetting
                because I have a cell modem that uploads data to
                Sol-Ark, but that cell modem is powered by the
                inverter outputs, so it must be getting power at
                least intermittently. The rest of the loads are
                basically flatlined according to the Sol-Ark data.
                It's mostly air conditioners, so they probably can't
                turn on fast enough before the PV fault causes
                another shutdown.

                So, in essence, one of 16 strings of PV develops a
                fault, and that causes all four inverters to
                malfunction? What is the point of redundancy if a
                fault of one results in a fault of all?! If there is
                a true PV input fault, shouldn't that just shut down
                that MPPT, or perhaps all of the PV DC input to that
                inverter? And why can't this inverter continue to
                invert power from the batteries and charge from a
                generator when there is a DC input fault that could
                be programmatically isolated and ignored?

                This is a bad design in my opinion, and something I
                hadn't considered. If the faulted inverter can't
                function with a DC input fault, it should just take
                itself out of the game. (This is 120/240 split
                phase, BTW). Is this how all AIO inverters work? One
                inverter fault on the DC side kills all paralleled
                units' AC output? Not good.

                This is a completely off-grid system on a remote
                island with no vehicle access, so it's not exactly
                easy to do a "truck roll" on this one, especially
                post-hurricane. To make matters worse, the generator
                was running at the time of the fault, as it was
                being signaled to run because the battery had
                reached the assigned charge voltage. The fault also
                killed the 2-wire start signal from the master, so
                the system also stopped passing through generator
                power to the loads. The house is dark.


                Jason Szumlanski
                Florida Solar Design Group

                _______________________________________________
                List sponsored by Redwood Alliance

                Pay optional member dues here: http://re-wrenches.org

                List Address: RE-wrenches@lists.re-wrenches.org

                Change listserver email address & settings:
                
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

                There are two list archives for searching. When one
                doesn't work, try the other:
                https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
                
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

                List rules & etiquette:
                http://www.re-wrenches.org/etiquette.htm

                Check out or update participant bios:
                http://www.members.re-wrenches.org

            _______________________________________________
            List sponsored by Redwood Alliance

            Pay optional member dues here: http://re-wrenches.org

            List Address: RE-wrenches@lists.re-wrenches.org

            Change listserver email address & settings:
            http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

            There are two list archives for searching. When one
            doesn't work, try the other:
            https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
            http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

            List rules & etiquette:
            http://www.re-wrenches.org/etiquette.htm

            Check out or update participant bios:
            http://www.members.re-wrenches.org

        _______________________________________________
        List sponsored by Redwood Alliance

        Pay optional member dues here: http://re-wrenches.org

        List Address: RE-wrenches@lists.re-wrenches.org

        Change listserver email address & settings:
        http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

        There are two list archives for searching. When one doesn't
        work, try the other:
        https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
        http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

        List rules & etiquette:
        http://www.re-wrenches.org/etiquette.htm

        Check out or update participant bios:
        http://www.members.re-wrenches.org


    _______________________________________________
    List sponsored by Redwood Alliance

    Pay optional member dues here:http://re-wrenches.org

    List Address:RE-wrenches@lists.re-wrenches.org

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    There are two list archives for searching. When one doesn't work, try the 
other:
    https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
    http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

    List rules & etiquette:
    http://www.re-wrenches.org/etiquette.htm

    Check out or update participant bios:
    http://www.members.re-wrenches.org

    _______________________________________________
    List sponsored by Redwood Alliance

    Pay optional member dues here: http://re-wrenches.org

    List Address: RE-wrenches@lists.re-wrenches.org

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    There are two list archives for searching. When one doesn't work,
    try the other:
    https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
    http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

    List rules & etiquette:
    http://www.re-wrenches.org/etiquette.htm

    Check out or update participant bios:
    http://www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to