Thank you for your feedback Jason. These are essential functions we must 
implement to comply with UL1741 standards. If this were to be changed then this 
could affect our status of being compliant with this standard and will limit 
the markets we could offer the Sol-Ark inverter. If you haven't already, I 
recommend calling our support line for assistance with this issue. You can 
reach our technical support team at 972-575-8875, Ext. 2, or email us at 
[email protected]. I’m not certain which fault code was triggered, but some 
PV-related faults can be in relation to the AC side as well, which could 
potentially lead to further damage to the installation.

As a side note, you can disconnect the PV of the affected inverter by opening 
the circuit using the DC disconnect. If the fault is coming from one of the 
inverters related to the PV, the system should function normally once you 
disconnect the affected string from the inverter. After experiencing multiple 
faults consecutively, the inverters may require a manual power cycle to return 
to normal operation. Again, I am not certain what fault was triggered or if you 
were able to reach our support line, but this should resume activity for the 
inverters until you are able to make it to the site.


Best Regards,

Jharen Poole
Applications Engineer II
972-575-8875
[cid:4fc04000-1e1e-4b96-b9a2-4422dddacb70]
________________________________
From: RE-wrenches <[email protected]> on behalf of jay 
via RE-wrenches <[email protected]>
Sent: Thursday, October 10, 2024 6:17 PM
To: RE-wrenches <[email protected]>
Cc: jay <[email protected]>; Lou Russo <[email protected]>
Subject: Re: [RE-wrenches] All-In-Ones / Sol-Ark fail

Caution: This email is from an external source.


Seems like this is a firmware setting and should be adjustable.  If lo

On Oct 10, 2024, at 3:59 PM, Lou Russo via RE-wrenches 
<[email protected]<mailto:[email protected]>> 
wrote:

Aloha All,

Thank you Jason. This is a huge and surprising issue. So much so that I dropped 
what I was doing and called Sol-Ark to confirm. Mind you this was level 1 
support, but I was told this is what the Sol-Arks are supposed to do and it is 
a feature not a bug. Their take is if there is any fault on any one string, the 
Sol-Ark assumes the worst and shuts everything down.

I wonder what solutions could be implemented on future installs to prevent this 
from happening?

Aloha,

Lou Russo
Owner
[email protected]<mailto:[email protected]>
Office - 808 345 6762
Spree Solar Systems LLC
CT-34322



On Thu, Oct 10, 2024 at 11:45 AM Jason Szumlanski via RE-wrenches 
<[email protected]<mailto:[email protected]>> 
wrote:
I think it's more likely water in a J-box or possibly physical damage, but 
someone passed by the property and did not observe any physical damage to the 
array.

Jason Szumlanski
Principal Solar Designer | Florida Solar Design Group
NABCEP Certified Solar Professional (PVIP)
Florida State Certified Solar Contractor CVC56956
Florida Certified Electrical Contractor EC13013208


On Thu, Oct 10, 2024 at 5:41 PM Jay 
<[email protected]<mailto:[email protected]>> wrote:
Jason
What’s the possibllity it was a lighting strike?

Jay

On Oct 10, 2024, at 2:57 PM, Jason Szumlanski via RE-wrenches 
<[email protected]<mailto:[email protected]>> 
wrote:


We have been talking a lot recently about all-in-ones. I just had a massive 
fail during Hurricane Milton with a quad Sol-Ark 15K off-grid system that 
deserves some discussion about whether AIO is a good idea if it can't build in 
some resilience to errors. I'm not sure if the new Midnite unit is better in 
this respect, but this is what happened to the Sol-Ark system...

Four inverters, each with 4 strings of PV paralleled to 2 MPPT per inverter. 
One of the slave units developed some sort of PV DC fault during the storm. 
This caused the slave inverter to shut down and throw an error, which in turn 
caused a parallel fault across all four inverters. Power output ceases at that 
point. Apparently the system keeps resetting because I have a cell modem that 
uploads data to Sol-Ark, but that cell modem is powered by the inverter 
outputs, so it must be getting power at least intermittently. The rest of the 
loads are basically flatlined according to the Sol-Ark data. It's mostly air 
conditioners, so they probably can't turn on fast enough before the PV fault 
causes another shutdown.

So, in essence, one of 16 strings of PV develops a fault, and that causes all 
four inverters to malfunction? What is the point of redundancy if a fault of 
one results in a fault of all?! If there is a true PV input fault, shouldn't 
that just shut down that MPPT, or perhaps all of the PV DC input to that 
inverter? And why can't this inverter continue to invert power from the 
batteries and charge from a generator when there is a DC input fault that could 
be programmatically isolated and ignored?

This is a bad design in my opinion, and something I hadn't considered. If the 
faulted inverter can't function with a DC input fault, it should just take 
itself out of the game. (This is 120/240 split phase, BTW). Is this how all AIO 
inverters work? One inverter fault on the DC side kills all paralleled units' 
AC output? Not good.

This is a completely off-grid system on a remote island with no vehicle access, 
so it's not exactly easy to do a "truck roll" on this one, especially 
post-hurricane. To make matters worse, the generator was running at the time of 
the fault, as it was being signaled to run because the battery had reached the 
assigned charge voltage. The fault also killed the 2-wire start signal from the 
master, so the system also stopped passing through generator power to the 
loads. The house is dark.


Jason Szumlanski
Florida Solar Design Group

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org<http://re-wrenches.org/>

List Address: 
[email protected]<mailto:[email protected]>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org<http://www.members.re-wrenches.org/>

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org<http://re-wrenches.org/>

List Address: 
[email protected]<mailto:[email protected]>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org<http://www.members.re-wrenches.org/>

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: 
[email protected]<mailto:[email protected]>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org


_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to