Drake,

I am the colleague that Jay was talking about. I have long believed that a 100% 
AC coupled system was a bad idea for fully off-grid systems, primarily because 
of the black start problem, but I'm not against doing some AC coupled, and some 
DC coupled. The way the Radian works, you should be able to use any PV 
inverter, as long as you can put a Frequency-Watt grid profile on it. I haven't 
done that with the Enphase yet, but it should work great. With the SMA SB, you 
put it in "Off-Grid" mode, and then it will put out 100% of its power as long 
as the frequency is below 61 Hz, then it tapers its output linearly from 100% 
at 61 Hz down to 0% at 62 Hz. Because of this programming, the frequency will 
never go above slightly over 62 Hz

This would be stated that the curtailment starting frequency of the SB is 61 
Hz, and that the ramp-down rate is 100% per Hz, but it is fully adjustable in 
the settings. Enphase has the ability to be programmed to the following 
specifications...
The following settings define the IQ Microinverter over frequency power limit

  *   Start frequency in Hz (min 60, max 65) - I would use a minimum of 61, but 
it shouldn't really matter at all for the operation of the equipment. You 
really don't want it too high because you don't want the loads in the house to 
have too high of a frequency.
  *   Start delay in milliseconds (min 0, max 10) - this should be 0
  *   Ramp down rate in %/Hz (min 40%/Hz, max 83.33%/Hz) - this shouldn't 
really matter either. I'd go close to the high end since the Sunny Boy is 
100%/Hz and it works well.

The Radian doesn't know what the curtailment starting frequency is, nor what 
the ramp down rate is, and it really doesn't care. It just knows that when the 
voltage gets to the absorb voltage (or the float voltage after the absorb timer 
is over) then it raises the frequency until it achieves the desired effect, so 
it doesn't matter if the PV inverter has a different power throttling curve, 
the Radian can simply adjust for however that inverter reacts. You do need to 
turn on the AC coupling mode.

Basically, it should work perfectly if you program it right, and since you 
already have the DC-coupled portion to prevent the black start problem, you 
should be set.




Michael Morningstar,

Looking back, I wasn't totally clear when I was talking to Jay. The system he 
was talking about is actually grid-tied, but I took it off-grid for a good long 
while just to test the taper charging and the reactions between the Radian and 
the Sunny Boys. I wanted to ensure that it was going to work the way I thought 
it would, and it worked flawlessly, but due to the black start issue, (dark 
start), I wouldn't design an off-grid system to be fully AC-coupled.

You would be correct about Murphy if it were an off-grid system, the dark start 
issue is something I wouldn't want to mess around with, but being grid-tied, I 
don't think it will be an issue (unless doomsday shows up).

I am caring for an orphaned system nearby that is solely AC coupled using Li 
batteries, and it's off-grid. I was very much opposed solely AC-coupling 
off-grid, and this orphaned system just confirms my leeriness to the idea, but 
it was also a bad selection of equipment for this purpose. They were using the 
Schneider XW platform, and the problem there is that the XW takes too long to 
shift frequency, so while it's lagging, the PV is still putting out full power, 
and then the battery system far overshoots the absorb voltage, and the Li 
batteries shut off, and then the voltage really spikes and shut the whole 
system off. I had to just tweak the absorb voltage lower and lower until I 
found a voltage low enough that by the time the XW shifted frequency, the 
battery voltage wouldn't be overshooting the correct absorb voltage. It's a 
functional workaround that's working okay for now.




And addressing Ray's statements, I couldn't agree with you more, but here's one 
other option that (somewhat) relieves the problem...

The other thing I've observed is that if you are going to have a solely AC 
coupled system off-grid, then at least have the low battery cutout on the 
inverter significantly higher than the low battery disconnect in the batteries, 
and then get a few external 48 V battery chargers that can charge a fully dead 
battery (make sure it is the kind that doesn't look for a live voltage before 
it powers up). Then permanently wire these chargers directly to the generator 
output so that it can charge the batteries even if the inverter isn't working 
at all. This will allow the generator to revive a black start scenario no 
matter what. I think this is still inferior to having part of the array DC 
coupled, since it does require firing up a generator, but it is a functional 
workaround that I have been using on the orphaned system and it really does 
work. That being said, I think I might be able to talk him into getting some 
DC-coupled PV next spring.


Thanks,
Kienan


Maxfield Solar
maxfieldso...@hotmail.com<mailto:maxfieldso...@hotmail.com>
(801) 631-5584
________________________________
From: RE-wrenches <re-wrenches-boun...@lists.re-wrenches.org> on behalf of 
drake.chamber...@redwoodalliance.org <drake.chamber...@redwoodalliance.org>
Sent: Friday, November 1, 2019 10:33 AM
To: RE-wrenches <re-wrenches@lists.re-wrenches.org>
Subject: Re: [RE-wrenches] Off Grid Optimizers

I agree completely that AC coupled systems are far better off if they have a 
battery charging method completely independent of the off-grid inverter. Some 
DC coupled solar is the best way to go. The system I'm considering already has 
2820 W of DC coupled PV.

Drake



----- Original Message -----
From:
"RE-wrenches" <re-wrenches@lists.re-wrenches.org>

To:
<re-wrenches@lists.re-wrenches.org>
Cc:

Sent:
Thu, 31 Oct 2019 19:33:11 -0600
Subject:
Re: [RE-wrenches] Off Grid Optimizers



We've discussed AC coupled many times.   Aside from the issues Michael brought 
up, I need to remind that not having at least some DC  PV charging means that 
when the AC system shuts down for any reason, so does all the PV charging.  If 
Li+ batteries get discharged to their low voltage shut off:  Dark Starts 
anyone?   With lead acid, DC coupled PV is just as critical to keep the battery 
from sulfating.

Which would you want?

Scenario 1:Come back to trouble shoot a system shutdown,  try to reboot, only 
to find no battery voltage to even test with. or

Scenario 2:  You will have a battery that is being charged, if not already at 
full charge.

For GTB?, you decide how important this issue is,  but for Off grid you are 
putting your customer in serious jeopardy without power. Unless they have a 
manual bypass, the generator won't pass through to the loads, or charge the 
battery either.  This is not theory, We've had to fix these, and in some cases 
replace the battery bank that was damaged after sitting dead too long.

My previous post in favor of AC coupling was only as a supplement to a solid DC 
PV system, or for module level optimization in partial shade conditions.

Ray Walters



Remote Solar



303 505-8760

On 11/1/19 1:08 PM, Michael Morningstar wrote:
You know Murphy? That is Murphy of Murphy’s Law?  He’s gotta just love the idea 
of AC coupled off-grid systems. The OB, SB, Li system Jay described is going to 
keep him (Murphy) and the installer very busy at some point. The further away 
the system is from civilization, the higher the odds of chicanery and 
headaches. Systems that need backup safety controls seem inherently risky too.



On Oct 31, 2019, at 11:06 AM, jay 
<jay.pe...@gmail.com<mailto:jay.pe...@gmail.com>> wrote:

HI Drake,

I was just talking with a colleague the other day about a project he did.
New Radian, AC coupling, lithium batteries, SB inverters.  Everything is 
working just as it should with the GT inverters tapering during AC coupling 
frequency shift mode.


I would say you are fine, and while I can’t say for sure if the Enphase will 
work that way, they should as they are all designed to the same parameters rule 
21.

I always do recommend a aux relay for backup/shutoff  should there be some kind 
of issue.

With the Envoy you’ll be able to see that tapering as well.

Seems like a good option for your application

jay





On Oct 31, 2019, at 9:49 AM, Drake 
<drake.chamber...@redwoodalliance.org<mailto:drake.chamber...@redwoodalliance.org>>
 wrote:

Hi Jay,

Between 2160 and 2880 Watts of added array. We will be using a new Radian.

Drake

At 11:49 AM 10/31/2019, you wrote:
How many watts are you adding as ac coupling?
And presuming its an older 8k radian?


Jay

_______________________________________________
List sponsored by Redwood Alliance

List Address: 
RE-wrenches@lists.re-wrenches.org<mailto:RE-wrenches@lists.re-wrenches.org>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>

Check out or update participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org>

_______________________________________________
List sponsored by Redwood Alliance

List Address: 
RE-wrenches@lists.re-wrenches.org<mailto:RE-wrenches@lists.re-wrenches.org>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>

Check out or update participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org>


_______________________________________________
List sponsored by Redwood Alliance

List Address: 
RE-wrenches@lists.re-wrenches.org<mailto:RE-wrenches@lists.re-wrenches.org>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>

Check out or update participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org>





Michael Morningstar

      Morningstar Electric
PO Box 1494
Mount Shasta, California 96067
530-921-0560
CSLB 949635





_______________________________________________



List sponsored by Redwood Alliance




List Address: 
RE-wrenches@lists.re-wrenches.org<mailto:RE-wrenches@lists.re-wrenches.org>




Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org




List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html




List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>




Check out or update participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org>

_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to