We've discussed AC coupled many times. Aside from the issues Michael
brought up, I need to remind that not having at least some DC PV
charging means that when the AC system shuts down for any reason, so
does all the PV charging. If Li+ batteries get discharged to their low
voltage shut off: Dark Starts anyone? With lead acid, DC coupled PV is
just as critical to keep the battery from sulfating.
Which would you want?
Scenario 1:Come back to trouble shoot a system shutdown, try to reboot,
only to find no battery voltage to even test with. or
Scenario 2: You will have a battery that is being charged, if not
already at full charge.
For GTB?, you decide how important this issue is, but for Off grid you
are putting your customer in serious jeopardy without power. Unless they
have a manual bypass, the generator won't pass through to the loads, or
charge the battery either. This is not theory, We've had to fix these,
and in some cases replace the battery bank that was damaged after
sitting dead too long.
My previous post in favor of AC coupling was only as a supplement to a
solid DC PV system, or for module level optimization in partial shade
conditions.
Ray Walters
Remote Solar
303 505-8760
On 11/1/19 1:08 PM, Michael Morningstar wrote:
You know Murphy? That is Murphy of Murphy’s Law? He’s gotta just love
the idea of AC coupled off-grid systems. The OB, SB, Li system Jay
described is going to keep him (Murphy) and the installer very busy at
some point. The further away the system is from civilization, the
higher the odds of chicanery and headaches. Systems that need backup
safety controls seem inherently risky too.
On Oct 31, 2019, at 11:06 AM, jay <jay.pe...@gmail.com
<mailto:jay.pe...@gmail.com>> wrote:
HI Drake,
I was just talking with a colleague the other day about a project he
did.
New Radian, AC coupling, lithium batteries, SB inverters. Everything
is working just as it should with the GT inverters tapering during AC
coupling frequency shift mode.
I would say you are fine, and while I can’t say for sure if the
Enphase will work that way, they should as they are all designed to
the same parameters rule 21.
I always do recommend a aux relay for backup/shutoff should there be
some kind of issue.
With the Envoy you’ll be able to see that tapering as well.
Seems like a good option for your application
jay
On Oct 31, 2019, at 9:49 AM, Drake
<drake.chamber...@redwoodalliance.org
<mailto:drake.chamber...@redwoodalliance.org>> wrote:
Hi Jay,
Between 2160 and 2880 Watts of added array. We will be using a new
Radian.
Drake
At 11:49 AM 10/31/2019, you wrote:
How many watts are you adding as ac coupling?
And presuming its an older 8k radian?
Jay
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches@lists.re-wrenches.org
<mailto:RE-wrenches@lists.re-wrenches.org>
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches@lists.re-wrenches.org
<mailto:RE-wrenches@lists.re-wrenches.org>
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches@lists.re-wrenches.org
<mailto:RE-wrenches@lists.re-wrenches.org>
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
*
*
*Michael **Morningstar*
*
*
*/Morningstar Electric/*
PO Box 1494
Mount Shasta, California 96067
530-921-0560
CSLB 949635
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org