Hi Mark,

I will talk to the installer to get more details.


At 02:06 PM 9/21/2009, you wrote:

Hi Drake,

I had not heard about this battery incident you mention below...do you have any other details? So far there has not been any record of battery problems on the XW that I know of and we obviously would like to hear if there is something we should be looking in to.

Hi Peter - as far as I recall we resolved the issue you mention below back in January, and from our records the customer has been happy with the results. It was a pretty unusual condition that our tech support team had not seen before, and it took the senior designer of the XW product to finally be able to understand what was going on. A learning "opportunity" for all.

Cheers,

Mark

_____________________________________________________________________________________

Mark Edmunds | Schneider Electric | Renewable Energies Business | CANADA | Senior Director, Engineering
Phone: +1-604-422-2609  |   Mobile: +1-604-613-3285
Email: <mailto:mark.edmu...@ca.schneider-electric.com>mark.edmu...@ca.schneider-electric.com | Site: www.xantrex.com | Address: 8999 Nelson Way, Burnaby, BC V5A 4B5, CANADA

*** Please consider the environment before printing this e-mail



From: Drake Chamberlin <drake.chamber...@redwoodalliance.org>
To: RE-wrenches <re-wrenches@lists.re-wrenches.org>
Date: 09/20/2009 05:10 PM
Subject: Re: [RE-wrenches] XW6048 parts problem
Sent by: re-wrenches-boun...@lists.re-wrenches.org




Hi Peter,

Do you need the extra fan? The VFX has an internal fan. Are there a lot of heavy loads that push the limits of the Outback? If not, take out the fan or swap it for a cover with no fan. Many VFX inverters didn't come with cover fans. I don't know if they are standard now, or not.

Or, have the fan go on whenever the direct grid tie inverter is being called on to charge batteries instead of feed the grid. If loads are not real heavy, battery charging, by back feeding the AC Out, may be the time when the fan is needed the most.

Before inverters started controlling generators, we used a device called the Simple Switch, which was a voltage controlled contact. (We'd use it with a GenWiz). I'm not sure what is out there these days. You could use the Atkinson GSCM, generator start module, which senses the voltage. If you need this solution, I'd call AEE.

Thanks for the heads up on the Xantrex. I just heard another horror story about the Xantrex 6024 system. According to the installer, the owner shut off an AC switch and the array cooked a bank of Surrette 25CS 25 PS batteries. I don't know the new Xantrex line and don't understand how this could happen. Is this really possible?

-Drake

At 06:43 PM 9/20/2009, you wrote:
Hi Drake (and everyone else interested in this thread),

Armed with the information from my esteemed colleagues, we went ahead and purchased a SunWise “Solar Ready-Grid Tie Battery System”, a SRB3.6 to be exact. The heart of the system is a GVFX3648. I ordered it without the Charge controller and purchased a SB3000 and 3150 Wdc of PV to go with it.

I also purchased a Grainger 2P2T relay with a 12 V coil in a NC configuration (to disconnect the SB when the batteries are fully charged in off-grid mode) and an Outback PSX-240 to transform the 240 Vac to 120 Vac (in order to interface with the GVFX3648.

When we looked into hooking the relay up to the AUX-OUT of the GVFX3648, we discovered that it was already dedicated to the fan…

So it looks like we will need to put something together to sense the battery voltage and energize the relay coil, when we exceed the threshold. Any recommendations for a add-on HVD? And exactly what threshold voltage should we use for 8ea 6V 305 Ah (C/24) AGM batteries?

And for Drake: I gravitated away from Xantrex because of a very unsatisfactory experience with a XW6048. The system failed to work properly and Xantrex “hemmed and hawed” for over six months. Bottom line: we made six service calls, two firmware upgrades and probably two dozen calls to largely clueless group tech supporters. Through it all, I lost the customer’s confidence and he chose another integrator to do a follow on commercial project. The last part of course was the worst part of the experience.

- Peter

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Drake Chamberlin
Athens Electric
OH License 44810
CO License 3773
NABCEP TM  Certified PV Installer
Office - 740-448-7328
Mobile - 740-856-9648  
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to