Oh brother, that 230.72(A) is a nightmare.
TVA and their 160 distributors are in the process of going to a line side feed 
in tariff from a load side production credit.
Actually they plan on letting the distributor offer either or both options at 
their discretion.
I'm laying out  a job today with a standalone rack mounted 100 amp 3 phase 480 
volt disconnect and feed thru meter out by the padmount transformer.
The existing service is 2500 amp and because the service was installed under 
the building slab (new building) there is no outdoor disconnect.
This means we would have to dig up a 2500 amp service and turn it up out by the 
padmount transformer. FORGET IT!  That's a huge switch with 4 four inch 
conduits full of 400 MCM going in and going out of that switch.

This is onerous.  Onerous I tell you!
I would submit that the exception to 230.72 (A) for water pumps be amended to 
add clean renewable PV systems.
John Wiles are you out there?

Steve Johnson
LightWave Solar Electric
Nashville, TN

From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of David Brearley
Sent: Tuesday, March 10, 2009 12:28 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Line Side Feed In and Disconnects

Wayne,

As you suggested, because this is a new service, a PV service disconnect is 
required. The question of whether a second disconnect is required, a new 
disconnect for the main service, is a Code issue, as far as I can tell. It is 
also an interpretation, but I'll get to that later.

It just so happens that the June/July issue of SolarPro magazine will have an 
extensive article on making PV interconnections. The authors are Ryan LeBlanc 
and Tarn Yates from SPG Solar. From their article, here are some Code articles 
that apply to selecting and locating a disconnect for a line side connection:

230.66 - Disconnect shall be listed for use as service equipment.
230.70(A)(1) - Disconnect shall be installed at a readily accessible location.
230.72(A) - All service disconnects shall be grouped together.

The last article is no doubt the one that the AHJ is referencing in this case.

The reason I feel that this extra expense and effort is an interpretation, as 
much as it is a Code issue, is that you could make a load side connection and 
still have the math work for the feed-in tariff program and for the revenue 
metering.

How is that?

Well, a meter on the inverter output circuits will read the total PV kWh for 
the feed-in tariff. A bi-directional meter for the revenue meter will read 
in-flow from the utility and out-flows to the utility. The difference between 
total PV kWh and the out-flow-kWh are the PV generated kWh that the customer 
used on site rather than export to the utility. Right? Whatever PV generated 
energy is not exported to the utility is used on site.

So for billing purposes the customer is charged as follows:

Total kWh for billing = In-flow kWh + (feed-in tariff kWh - out-flow kWh)

Theoretically, this can also be implemented affordably by the utility: move the 
exiting revenue meter to the PV system; add a $100 bi-directional meter to the 
original meter can. Finished.

Making a line-side connection is often difficult and expensive, especially when 
you now have to add a new service disconnect for the facility. At least in 
theory, it is also dangerous; the fault-currents there are higher. You have 
these implementation issues on the one hand. On the other hand you have a 
spreadsheet, or a one-time fix the the utility's billing software.

So I think the utility is making this more onerous than they need to. 
Especially for small generators, the cost of this service upgrade will kill the 
deal. The utility probably isn't interested in this solution, but we can still 
dream of the perfect fix.

David Brearley, Technical Editor
SolarPro magazine
NABCEP Certified PV Installer (tm)
david.brear...@solarprofessional.com
Direct: 541.261.6545
Fax:  541.512.0343

Visit our Web site at solarprofessional.com

On 3/9/09 5:25 PM, "Allan Sindelar" <al...@positiveenergysolar.com> wrote:
Wayne,
Use this as a tool: http://www.solarabcs.org/utilitydisconnect/
and this: http://www.nrel.gov/docs/fy08osti/42675.pdf


Allan Sindelar
allan(at)positiveenergysolar.com 
<mailto:al...@positiveenergysolar.com><mailto:al...@positiveenergysolar.com>
NABCEP Certified Solar PV Installer
Positive Energy, Inc.
3201 Calle Marie
Santa Fe NM 87507
505 424-1112
www.positiveenergysolar.com

Please consider the environment before printing this e-mail.

-----Original Message-----
From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Wayne Irwin
Sent: Monday, March 09, 2009 4:41 PM
To: re-wrenches@lists.re-wrenches.org
Subject: [RE-wrenches] Line Side Feed In and Disconnects

Hello Wrenches,

Here in Gainesville, Fla. we have recently adopted a Feed In Tariff.
So, now we are supposed to directly feed the line side of the utility meter 
(essentially a new service). No big deal.
As usual we use an AC disco between the inverter and the grid. However, the 
permit department is requiring that we install and additional disco between the 
existing service feed and the distribution panel to group all disco's in the 
same location. This especially adds an additional expense when dealing with 3 
phase systems as well as the raises the question, is this really the National 
Electrical Code or just an interpretation? Your thoughts?

Wayne Irwin, President
Pure Energy Solar International Inc.
Lic # CVC56695
 <mailto:pureenergyso...@hotmail.com><mailto:pureenergyso...@hotmail.com>


________________________________
Date: Mon, 9 Mar 2009 18:20:57 -0400
From: reelli...@gmail.com
To: re-wrenches@lists.re-wrenches.org
Subject: Re: [RE-wrenches] Small Torque Wrench

I got mine from "the knife and tool store" http://myworld.ebay.com/don19470/ on 
E bay. nice tool, adjustable 10 - 50 In Oz and he has others, just get the 
adapter that lets you use 1/4" drive bits and your good to go. It is a german 
tool and i use it on all breaker connections as well as others.

Later,
Bob

On Mon, Mar 9, 2009 at 12:10 PM, Peter Parrish <peter.parr...@calsolareng.com> 
wrote:


We have a great torque wrench for  snugging down module clamps, Sharp SRS 
bolts, etc. What do folks use to insure  that wire terminals are torqued to 
spec? We're talking 1.1 to 3.3 N-m (10-30  in-lbs). I'm imagining something 
compact like an over-sized screwdriver.

- Peter

Peter T. Parrish,  President
California Solar Engineering, Inc.
820 Cynthia Ave., Los  Angeles, CA 90065
Ph 323-258-8883, Mobile 323-839-6108, Fax  323-258-8885
CA Lic. 854779, NABCEP Cert. 031806-26
peter.parr...@calsolareng.com

_______________________________________________
List  sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:  
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List  rules & etiquette:
www.re-wrenches.org/etiquette.htm 
<http://www.re-wrenches.org/etiquette.htm><http://www.re-wrenches.org/etiquette.htm>

Check  out participant bios:
www.members.re-wrenches.org 
<http://www.members.re-wrenches.org/><http://www.members.re-wrenches.org/>



________________________________
Windows Live(tm) Groups: Create an online spot for your favorite groups to 
meet. Check it out. 
<http://windowslive.com/online/groups?ocid=TXT_TAGLM_WL_groups_032009><http://windowslive.com/online/groups?ocid=TXT_TAGLM_WL_groups_032009>
________________________________
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to