One thing that I didn't see people mention..
The actual amount of energy you need to spend to remove that heat will 
very dramatically (drastically even) depending upon your cooling 
arrangement. If you are just dumping cool air into the roomt and mixing 
it in with the warm and and have no separation between cooling and the 
hot air, you will probably need to spend up to about $2 to cool for 
every $1 in server power (worst case).

On the other hand, if you have clear separation, you may be able get 
this below $1 depending upon how you are doing your cooling.

You might want to talk to Chatsworth. They have a very efficient rack 
design with a chimney that will allow you to cool very efficiently, and 
with minimal cost. Whether this will work depends a lot upon how much 
room you have in your space to engineer the solution properly. You would 
want a false ceiling of appropriate size of the amount of airflow you 
need to maintain, which is dependent upon your servers and how you are 
loading the CPUs. (heavily CPU intensive jobs, particularly floating 
point, generate the most heat). How many disks also makes a significant 
impact. In the end, heating/cooling engineers can size your ducts 
appropriately based upon the air flow and differential temperature. This 
number varies widely between normal 1U rack mount and 2U and also blade 
servers, also vendor. The chatsworth chimney rack can do 8KW without 
much problem, and higher with the proper cooling infrastructure.

There are many other ways to do it, all with different efficiency and 
impact.