On Tue, Nov 23, 2010 at 6:31 PM, Brad Knowles <[email protected]> wrote:
> On Nov 23, 2010, at 2:24 PM, Dustin Puryear wrote:
>
>> What are your thoughts on our A/C and airflow needs? How do I calculate our 
>> needs the best? And should we look into a rack/cabinet that has some type of 
>> A/C and airflow solution built into it?
>
> It's been a while since I looked at this stuff, but I thought that TOPSANA 
> had a chapter on this subject, no?

In the 2nd edition this is chapter 6, Data Centers.  (By the way...
2nd edition is available on www.safaribooksonline.com even though it
is not an O'Reilly book).

There is a typo in the first printing and I'm not sure if the
correction has made it into production.  "Five tons of cooling for
every 1,000 square feet" is the rule of thumb from 2001 (the text says
per 5,000 sq ft).  That is a 2001 number... machine density has gotten
a lot better since then.  (Updates anyone?)

A good rack salesperson will help you work out the A/C, cabling and
other issues.  I found this because no matter what goes wrong people
blame the racks, so the rack salespeople try to get everything set up
right to reduce the blame.

Also remember that in general the amount of power you use for cooling
will equal the amount of power you use for your computers and other
equipment.  Often the cooling will require more power than the
equipment due to loss.

Tom

-- 
http://EverythingSysadmin.comĀ  -- my blog (new posts Mon and Wed)
http://www.TomOnTime.com -- my advice (more videos coming soon)