NFPA 291
from 2022 Fire Pump Handbook
4.4.6

I have used Google Earth Pro
It has Elevation  (not perfect  but close and you can get elevation Change
between hydrant(s))

Hose Monster has a Good 8 page PDF on
Hydrant Flow Testing

Chuck Bamford



On Fri, Apr 11, 2025 at 5:29 AM Fpdcdesign <[email protected]> wrote:

> What is the effective point of a hydrant flow test? By that, I mean the
> point you should design from. I was told from the beginning that it is at
> the intersection of flowing and non-flowing water (i.e the connection
> between the point of the flowing main with the branch to the hydrant where
> the pressures are read.) Am I doing something wrong?
>
> This comes from a test that a regional water company did and they will
> only tell me what hydrant was flowed. It could make a difference because of
> elevation.
>
> Todd G Williams, PE
> Fire Protection Design/Consulting
> Stonington, CT
> 860-535-2080 (ofc)
> 860-554-7054  (fax)
> 860-608-4559 (cell)
>
> _________________________________________________________
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> [email protected]
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to