This is incorrect. From the 2019 Edition of NFPA 13D: 7.6* Alarms. Local waterflow alarms shall be provided on all sprinkler systems in homes not equipped with smoke alarms or smoke detectors in accordance with NFPA 72.
Chris Dorn [cid:[email protected]] From: Jeff Brickell <[email protected]> Sent: Tuesday, February 11, 2025 5:01 PM To: Discussion list on issues relating to automatic fire sprinklers <[email protected]> Subject: [Sprinklerforum] Re: Fdc help NFPA 13D does not require a bell. It doesn’t even require a waterflow detector, however, many local jurisdictions do. Jeff Brickell, CET Senior Estimator/Designer NICET III CERTIFIED CERT #147245 OREGON CERTIFIED COBID FIRM #13272 (EMERGING SMALL BUSINESS) TRIAD FIRE PROTECTION [cid:[email protected]] OREGON . WASHINGTON . ARIZONA OFFICE 503.856.6333 CELL 602.550.4292 FAX 866.766.8862 From: Jeff Werre <[email protected]<mailto:[email protected]>> Sent: Tuesday, February 11, 2025 2:38 PM To: Discussion list on issues relating to automatic fire sprinklers <[email protected]<mailto:[email protected]>> Subject: [Sprinklerforum] Re: Fdc help I cannot get my question to post on the page I want it to post so I am going to try it here- Does NFPA 13D REQUIRE a local alarm (bell)? If you say yes, where are you getting that requirement? Thank you- Jeff Werre Fire Plan Reviewer/Fire Inspector Building/Development Services Department City of Goodyear 1900 North Civic Square Goodyear, AZ 85395 o 602 316-0704 w goodyearaz.gov e [email protected]<mailto:[email protected]> From: Tim Easter <[email protected]<mailto:[email protected]>> Sent: Tuesday, February 4, 2025 7:44 AM To: Discussion list on issues relating to automatic fire sprinklers <[email protected]<mailto:[email protected]>> Subject: [Sprinklerforum] Re: Fdc help ⚠ This email arrived from an external source - Please exercise caution when opening any attachments or clicking on links 7 FDC total. 6 risers and 6 out 7 FDC feed these risers. On Tue, Feb 4, 2025, 9:03 AM Fpdcdesign <[email protected]<mailto:[email protected]>> wrote: How many systems in the building? Todd Williams Fire Protection Design/Consulting Stonington, CT 860-608-4559 On Feb 4, 2025 at 8:20 AM, <Tim Easter<mailto:[email protected]>> wrote: Can't find any piping above ceiling. May have been abandoned, but can't prove it. What's steps to find system fdc belongs to? Thks On Tue, Feb 4, 2025, 7:31 AM Mike Watts <[email protected]<mailto:[email protected]>> wrote: Follow fdc piping or pump in fdc and see what system flows water. Add sign once done. Mike Watts Sprinkler Service Manager Firetrol Protection Systems 4616 W. Howard Lane, Suite 700<https://www.google.com/maps/search/4616+W.+Howard+Lane,+Suite+700+%0D%0A+Austin,+TX.+78728?entry=gmail&source=g> Austin, TX. 78728<https://www.google.com/maps/search/4616+W.+Howard+Lane,+Suite+700+%0D%0A+Austin,+TX.+78728?entry=gmail&source=g> 512-687-0115 Office 512‐660-4411 Cell [email protected]<mailto:[email protected]> ________________________________ From: Tim Easter <[email protected]<mailto:[email protected]>> Sent: Tuesday, February 4, 2025 6:27:13 AM To: [email protected]<mailto:[email protected]> <[email protected]<mailto:[email protected]>> Subject: [Sprinklerforum] Fdc help We have a fdc on building. No sign. How do we test the fdc to determine what it supplies? Looking for procedure. Thanks. We have a fdc on building. No sign. How do we test the fdc to determine what it supplies? Looking for procedure. Thanks. _________________________________________________________ SprinklerForum mailing list: https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org To unsubscribe send an email to [email protected]<mailto:[email protected]> _________________________________________________________ SprinklerForum mailing list: https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org To unsubscribe send an email to [email protected]<mailto:[email protected]> _________________________________________________________ SprinklerForum mailing list: https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org To unsubscribe send an email to [email protected]<mailto:[email protected]>
_________________________________________________________ SprinklerForum mailing list: https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org To unsubscribe send an email to [email protected]