7.6* Alarms. Local waterflow alarms shall be provided on all
sprinkler systems in homes not equipped with smoke alarms or
smoke detectors in accordance with NFPA 72.

Chris

[cid:[email protected]]



From: Jeff Werre <[email protected]>
Sent: Tuesday, February 11, 2025 4:38 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Re: Fdc help

I cannot get my question to post on the page I want it to post so I am going to 
try it here-

Does NFPA 13D REQUIRE a local alarm (bell)?

If you say yes, where are you getting that requirement?

Thank you-

Jeff Werre
Fire Plan Reviewer/Fire Inspector
Building/Development Services Department

City of Goodyear
1900 North Civic Square
Goodyear, AZ 85395

o 602 316-0704
w goodyearaz.gov
e [email protected]<mailto:[email protected]>


From: Tim Easter <[email protected]<mailto:[email protected]>>
Sent: Tuesday, February 4, 2025 7:44 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Re: Fdc help

⚠ This email arrived from an external source - Please exercise caution when 
opening any attachments or clicking on links

7 FDC total. 6 risers and 6 out 7 FDC feed these risers.

On Tue, Feb 4, 2025, 9:03 AM Fpdcdesign 
<[email protected]<mailto:[email protected]>> wrote:
How many systems in the building?

Todd Williams
Fire Protection Design/Consulting
Stonington, CT
860-608-4559


On Feb 4, 2025 at 8:20 AM, <Tim Easter<mailto:[email protected]>> wrote:
Can't find any piping above ceiling. May have been abandoned, but can't prove 
it. What's steps to find system fdc belongs to? Thks

On Tue, Feb 4, 2025, 7:31 AM Mike Watts 
<[email protected]<mailto:[email protected]>> wrote:
Follow fdc piping or pump in fdc and see what system flows water. Add sign once 
done.

Mike Watts
Sprinkler Service Manager
Firetrol Protection Systems
4616 W. Howard Lane, Suite 
700<https://www.google.com/maps/search/4616+W.+Howard+Lane,+Suite+700+%0D%0A+Austin,+TX.+78728?entry=gmail&source=g>
Austin, TX. 
78728<https://www.google.com/maps/search/4616+W.+Howard+Lane,+Suite+700+%0D%0A+Austin,+TX.+78728?entry=gmail&source=g>
512-687-0115 Office
512‐660-4411 Cell
[email protected]<mailto:[email protected]>

________________________________
From: Tim Easter <[email protected]<mailto:[email protected]>>
Sent: Tuesday, February 4, 2025 6:27:13 AM
To: 
[email protected]<mailto:[email protected]>
 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Fdc help

We have a fdc on building. No sign. How do we test the fdc to determine what it 
supplies? Looking for procedure. Thanks. ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ 
‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ 
‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ 
‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍
We have a fdc on building. No sign. How do we test the fdc to determine what it 
supplies? Looking for procedure. Thanks.

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to 
[email protected]<mailto:[email protected]>
_________________________________________________________ SprinklerForum 
mailing list: 
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org To 
unsubscribe send an email to 
[email protected]<mailto:[email protected]>

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to 
[email protected]<mailto:[email protected]>
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to