Shut the systems down and drain them - open the fdc, either by removing a plug, 
or removing the check valve,  and crack the control valves individually until 
you get water. Once you get water from one, keep trying the others in case it 
feeds more than one.

If you cant do that, pump water into the fdc with the systems drain until you 
get water coming out a main drain.



Greg McGahan

Genesis Fire Services, LLC.




________________________________
From: Tim Easter <[email protected]>
Sent: Tuesday, February 4, 2025 7:19 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Re: Fdc help

Can't find any piping above ceiling. May have been abandoned, but can't prove 
it. What's steps to find system fdc belongs to? Thks

On Tue, Feb 4, 2025, 7:31 AM Mike Watts 
<[email protected]<mailto:[email protected]>> wrote:
Follow fdc piping or pump in fdc and see what system flows water. Add sign once 
done.

<https://www.google.com/maps/search/4616+W.+Howard+Lane,+Suite+700+%0D%0A+Austin,+TX.+78728?entry=gmail&source=g>
Mike Watts
Sprinkler Service Manager
Firetrol Protection Systems
4616 W. Howard Lane, Suite 
700<https://www.google.com/maps/search/4616+W.+Howard+Lane,+Suite+700+%0D%0A+Austin,+TX.+78728?entry=gmail&source=g>
Austin, TX. 
78728<https://www.google.com/maps/search/4616+W.+Howard+Lane,+Suite+700+%0D%0A+Austin,+TX.+78728?entry=gmail&source=g>
512-687-0115 Office
512‐660-4411 Cell
[email protected]<mailto:[email protected]>

________________________________
From: Tim Easter <[email protected]<mailto:[email protected]>>
Sent: Tuesday, February 4, 2025 6:27:13 AM
To: 
[email protected]<mailto:[email protected]>
 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Fdc help

We have a fdc on building. No sign. How do we test the fdc to determine what it 
supplies? Looking for procedure. Thanks. ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ 
‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ 
‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ 
‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍
We have a fdc on building. No sign. How do we test the fdc to determine what it 
supplies? Looking for procedure. Thanks.

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to 
[email protected]<mailto:[email protected]>
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to