This is the way. You could do it with a test pump instead of utilizing the 
pumper truck if that is easier. As a contractor, that’s what I would do, since 
we don’t own a firetruck.

Tricky part will be if something starts leaking due to the increased pressure, 
who is responsible for the repair? Repairing the leak is one thing, repairing 
water damage is the bigger concern.

Kyle Montgomery


From: Jackie Ward <[email protected]>
Sent: Tuesday, February 4, 2025 7:36 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [External][Sprinklerforum] Re: Fdc help


  1.  Identify static system pressure on your six risers.
  2.  Adapt from your FDC inlet to a ¼” nipple and see if FDC will hold air 
pressure with a portable compressor.  Apply 20 psi, valve off and see if it 
bleeds off.  If it bleeds off, I would NOT apply water.  It may have been 
abandoned.  Building occupant would then need to review with past building 
architects/engineers, contractors to find history of FDC.  Employee local 
sprinkler contractor to further investigate.
  3.  If it holds air, Connect pumper truck to FDC.  Gently apply water at 
below system static pressure, monitoring for leaks.
  4.  If system static pressure is reached without leaks, increase pressure 
10-15 psi at the pumper truck and see which riser gauge(s) increase.



Thank you,

Jackie “JW” Ward
1-405-240-7076

From: Tim Easter <[email protected]<mailto:[email protected]>>
Sent: Tuesday, February 4, 2025 6:27 AM
To: 
[email protected]<mailto:[email protected]>
Subject: [Sprinklerforum] Fdc help

We have a fdc on building. No sign. How do we test the fdc to determine what it 
supplies? Looking for procedure. Thanks. ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ 
‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ 
‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ 
‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍ ‍

We have a fdc on building. No sign. How do we test the fdc to determine what it 
supplies? Looking for procedure. Thanks.