Brian,
Hang from the vertical portion of the purlin only. It is unlikely you will find 
a purlin that is designed to support sprinkler pipe from the bottom. The best 
way to accomplish this it to install the hanger prior to the vapor barrier. Use 
angle bracket type attachment put the bottom of the angle bracket flush with 
the bottom of the purlin and use two screws so the hangers do not get out of 
square. You will be able to locate the bracket easily after the vapor barrier 
is installed because it is mounted flush with the bottom of the purlin.



Christopher S. Wilson
Project Design Manager, SET


[cid:treasure-valley-350-1.0_4621d75e-0876-470c-a582-8a1a743b106c.png]          
(208) 362-1888<tel:(208)%20362-1888>
[email protected]<mailto:[email protected]>

Treasure Valley Fire Protection

2731 Saturn Way
Boise, ID 83709







www.tvfpinc.com<https://www.tvfpinc.com/>



From: Ed Kramer <[email protected]>
Sent: Wednesday, January 29, 2025 4:42 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Re: Hang From Bottom of Purlin


You don't often get email from 
[email protected]<mailto:[email protected]>. Learn why this is 
important<https://aka.ms/LearnAboutSenderIdentification>

We've had a lot of projects recently where 'simple saver' plastic liner (or 
something similar) is installed to the bottom of the purlins.  I still prefer 
attaching to the vertical part of the purlin, but that can get tricky, messy, 
and a bit ugly.  We've used a lot of the sammy-type products (there are other 
brands on the market) to hang from the bottom horizontal flange of the purlins 
- in particular the products that 'mushroom out' as they're tightened.

Yea, look at the listings carefully - there are limitations on size of pipe 
that can be hung, and minimum thickness of the purlin you're attaching to.  
Also check the PEMB drawings for any limitations they have for hanging.  The 
maximum point loads can be pretty small.  We're dealing with a couple projects 
now where we're installing multiple anchors for each hanger (kinda like a 
trapeze bar) to keep the PEMB people happy.  You can get really creative if 
you're willing to get the PE stamp on it.

Ed Kramer
Bamford Fire


From: Brian Harris <[email protected]<mailto:[email protected]>>
Sent: Wednesday, January 29, 2025 2:55 PM
To: 
[email protected]<mailto:[email protected]>
Subject: [Sprinklerforum] Hang From Bottom of Purlin

I've was always taught to hang from the vertical leg of a purlin. We have a 
case where there will be a barrier installed, and the bottom flange is the 
"only" place to hang. If I'm reading the data sheet for Sammy Sidewinders it 
looks like there are a couple options, 2" & 3" pipe. Thoughts?

Thank you,

Brian Harris, CET
BVS Systems Inc.
bvssystemsinc.com<http://bvssystemsinc.com/>
Phone: 704.896.9989
Fax: 704.896.1935

Disclaimer

This email may contain confidential and privileged material for the sole use of 
the intended recipient(s). Any review, use, distribution or disclosure by 
others is strictly prohibited. 
If you are not the intended recipient (or authorized to receive for the 
recipient), please contact the sender by reply email and delete all copies of 
this message.  PLEASE PRINT RESPONSIBLY.
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to