Unless there is an amendment to the building code, you will be at a high rise 
and automatic standpipe if your top floor is >75' above lowest level of fire 
department access.





Travis Mack, SET

M.E.P.CAD | Instructor / Support

181 N. Arroyo Grande Blvd. #105 I Henderson, NV 89074

www.mepcad.com<http://www.mepcad.com/> | m: 480.547.9348| Whatspp: +14805479348

Email: [email protected]



AutoSPRINK  |  AutoSPRINK FAB  |  AutoSPRINK RVT  |  AlarmCAD



Academy of Fire Sprinkler Technology | Director, Engineering Technology

101 S Main Street, Suite 001, Decatur, IL 62523

________________________________
From: Jeff Brickell <[email protected]>
Sent: Tuesday, November 19, 2024 9:02 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Re: Fire Pump Sizing


A couple of points here:



1. You do not say where the demand points are located. I have to make 
assumptions that the garage is probably at the dry valve or whatever system 
control. Is the 7th floor demand taken at the floor control on the 7th floor? 
What is the actual demand at the BoR or location close the garage connection? 
Correct, the garage is served by a dry valve in the fire pump room.  The 
demands are at B.O.R.  The 7th floor is a combination standpipe and the demand 
is at the B.O.R. of the standpipe riser in the fire pump room on level 1.  The 
actual demand is 385 GPM plus the 250 Hose Demand.



2. Are the sprinklers fed from a separate riser or a combination 
sprinkler/standpipe?  Combination sprinkler standpipe on level 7, and separate 
riser for the dry valve off manifold level 1.



3. If you install a 350 gpm pump on the system, is that going to impact the 
fire department’s ability to pump to the standpipe demand? No, the FDC enters 
the system after the pump bypass loop and before the (3) riser manifolds.  I 
have a level 1 wet, level 1 dry, and standpipe riser.



4. 7 floors seems like a tall building for a manual wet standpipe. I assume 
there are at least 2. City of Portland can deliver standpipe demand much higher 
than 7 stories.  I believe their cut-off is around 12.



Thank you  for your response.





Jeff Brickell, CET

Senior Estimator/Designer

NICET III CERTIFIED

CERT #147245



OREGON CERTIFIED COBID FIRM #13272

(EMERGING SMALL BUSINESS)



TRIAD FIRE PROTECTION

[cid:[email protected]]

OREGON . WASHINGTON . ARIZONA



OFFICE  503.856.6333

CELL       602.550.4292

FAX        866.766.8862



From: Fpdcdesign <[email protected]>
Sent: Tuesday, November 19, 2024 7:50 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Re: Fire Pump Sizing



A couple of points here:



1. You do not say where the demand points are located. I have to make 
assumptions that the garage is probably at the dry valve or whatever system 
control. Is the 7th floor demand taken at the floor control on the 7th floor? 
What is the actual demand at the BoR or location close the garage connection?



2. Are the sprinklers fed from a separate riser or a combination 
sprinkler/standpipe?



3. If you install a 350 gpm pump on the system, is that going to impact the 
fire department’s ability to pump to the standpipe demand?



4. 7 floors seems like a tall building for a manual wet standpipe. I assume 
there are at least 2.



Todd G Williams, PE

Fire Protection Design/Consulting

Stonington, CT

860-535-2080<tel:860-535-2080> (ofc)

860-554-7054<tel:860-554-7054>  (fax)

860-608-4559<tel:860-608-4559> (cell)




On Nov 19, 2024 at 9:06 AM, <Jeff Brickell<mailto:[email protected]>> wrote:

I have a situation that’s unique to me and am looking for some guidance.



I have a 7-story building.  The first level contains a parking garage with a 
demand of 635 GPM @ 61 PSI.  The municipal supply can meet this demand.



The 7th floor has a remote area with a demand of 285 GPM @ 66 PSI, which the 
municipal supply cannot meet.



NFPA 20 says to size a fire pump to meet the greatest demand.  If I can meet 
the level 1 demand without a pump, why would I need to size a fire pump for it? 
 There would be a drastic size reduction if I only had to meet the 7th floor 
demand.



I have reached out to a couple other people, and they have all said I need to 
size the pump to the garage demand, I am just curious as to why.



If the contractor were to tee the underground and bring up a second supply for 
the first floor only would that be acceptable to then not use a pump?  Maybe 
there is something I’m not considering or thinking of since this is new to me.



Any advice, comments welcome, thank you.





Jeff Brickell, CET

Senior Estimator/Designer

NICET III CERTIFIED

CERT #147245



OREGON CERTIFIED COBID FIRM #13272

(EMERGING SMALL BUSINESS)



TRIAD FIRE PROTECTION

[cid:[email protected]]

OREGON . WASHINGTON . ARIZONA



OFFICE  503.856.6333

CELL       602.550.4292

FAX        866.766.8862



_________________________________________________________ SprinklerForum 
mailing list: 
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org To 
unsubscribe send an email to 
[email protected]<mailto:[email protected]>
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to