> On Nov 19, 2024 at 10:03 AM,  <Jeff Brickell (mailto:[email protected])>  
> wrote:
>   
>   
>           
>   
>
> A couple of points here:
>
>   
>
>   
>
>   
>
> 1. You do not say where the demand points are located. I have to make 
> assumptions that the garage is probably at the dry valve or whatever system 
> control. Is the 7th floor demand taken at the floor control on the 7th floor? 
> What is the actual demand at the BoR or location close the garage connection? 
> Correct, the garage is served by a dry valve in the fire pump room.    The 
> demands are at B.O.R.     The 7th  floor is a combination standpipe and the 
> demand is at the B.O.R. of the standpipe riser in the fire pump room on level 
> 1.    The actual demand is 385 GPM plus the 250 Hose Demand.
>
>   
>
>   
>
>   
>
> So based on this and your first email, your 7th floor sprinkler demand, with 
> hose stream, is 635 gpm at 66 psi at the manifold on the 1st floor. This 
> cannot be provided by the public water. However, the 1st floor garage demand 
> is 635 gpm at 61 psi at the manifold, which the city demand can provide. 
> Wouldn’t it be easier and cheaper to modify the 7th floor sprinklers so that 
> the demand can be met by the city?
>
>   
>
>
>
>
>   
>
>
>
>
>   
>
>     
>
>
>   
>   
>   
>
> Todd G Williams, PE
>
>   
>   
>
> Fire Protection Design/Consulting
>
>   
>   
>   
>
> Stonington, CT
>
>   
>   
>   
>
> 860-535-2080 (tel:860-535-2080)  (ofc)
>
>   
>   
>   
>
> 860-554-7054 (tel:860-554-7054)     (fax)
>
>   
>   
>   
>
> 860-608-4559 (tel:860-608-4559)  (cell)
>
>   
>   
>   
>   
>   
>   
>
>
>   
>   
>
>
>   
> >   
> >   
> >
> > On Nov 19, 2024 at 9:06 AM,  <Jeff Brickell (mailto:[email protected])>  
> > wrote:
> >
> >   
> >   
> >   
> >
> > I have a situation that’s unique to me and am looking for some guidance.
> >
> >   
> >
> >   
> >
> >   
> >
> > I have a 7-story building.    The first level contains a parking garage 
> > with a demand of 635 GPM @ 61 PSI.    The municipal supply  can  meet this 
> > demand.
> >
> >   
> >
> >   
> >
> >   
> >
> > The 7th  floor has a remote area with a demand of 285 GPM @ 66 PSI, which 
> > the municipal supply  cannot  meet.
> >
> >   
> >
> >   
> >
> >   
> >
> > NFPA 20 says to size a fire pump to meet the greatest demand.    If I can 
> > meet the level 1 demand without a pump, why would I need to size a fire 
> > pump for it?    There would be a drastic size reduction if I only had to 
> > meet the 7th  floor demand.   
> >
> >   
> >
> >   
> >
> >   
> >
> > I have reached out to a couple other people, and they have all said I need 
> > to size the pump to the garage demand, I am just curious as to why.   
> >
> >   
> >
> >   
> >
> >   
> >
> > If the contractor were to tee the underground and bring up a second supply 
> > for the first floor only would that be acceptable to then not use a pump?   
> >  Maybe there is something I’m not considering or thinking of since this is 
> > new to me.
> >
> >   
> >
> >   
> >
> >   
> >
> > Any advice, comments welcome, thank you.
> >
> >   
> >
> >   
> >
> >   
> >
> >   
> >
> >   
> >
> > Jeff Brickell, CET
> >
> >   
> >
> > Senior Estimator/Designer
> >
> >   
> >
> > NICET III CERTIFIED
> >
> >   
> >
> > CERT #147245
> >
> >   
> >
> >   
> >
> >   
> >
> > OREGON CERTIFIED COBID FIRM #13272
> >
> >   
> >
> > (EMERGING SMALL BUSINESS)
> >
> >   
> >
> >   
> >
> >   
> >
> > TRIAD FIRE PROTECTION
> >
> >   
> >
> >
> >
> >   
> >
> > OREGON . WASHINGTON . ARIZONA
> >
> >   
> >
> >   
> >
> >   
> >
> > OFFICE    503.856.6333
> >
> >   
> >
> >   CELL              602.550.4292
> >
> >   
> >
> >   FAX                866.766.8862
> >
> >   
> >
> >   
> >
> >   
> >
> > _________________________________________________________ SprinklerForum 
> > mailing list:   
> > https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org 
> >  To unsubscribe send an email to  
> > [email protected] 
> > (mailto:[email protected])
> >
> >   
> >   
>   
>   
>   
>  _________________________________________________________ SprinklerForum 
> mailing list: 
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org 
> To unsubscribe send an email to [email protected]
>   
  
     
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to