This section refers to 7.2.3.6 which has to do with options when using the 
Approved calculation program SprinkFDT to determine delivery time of water to 
the test station upon activation of the PA valve.  The direction is to assume 
in the calculation procedure that there is no programmed delay between 
detection system alarm and activation of the PA valve.  This is not speaking to 
real time system functionality.

There is additional text in the NFPA 13 Handbook for this section.

Basically, this section is addressing delivery time requirements similar for 
Dry pipe systems based on system size.

There are numerous conditions where a detection system could go into alarm and 
there be a varying amount of time before fire growth would activate a 
sprinkler.  Electrical related fires for example can be slow smoldering fires 
with considerable smoke release but often times, low heat release causing a 
varying time delay between detection and sprinkler activations.

The delay between detection system activation and sprinkler discharge is one of 
the primary functions of a DIPA system that is desired by owners of areas which 
are water sensitive and immediate sprinkler discharge is not desired.

If a DIPA system discharged immediately upon simultaneous detection and 
sprinkler fusing, you might as well have a wet pipe system or standard dry pipe 
system.



Craig Prahl | Jacobs | Fire Protection SME – EV, AM, DC, Special Hazards
[email protected]<mailto:[email protected]> | 
www.jacobs.com<https://urldefense.com/v3/__http:/www.jacobs.com/__;!!KZTdOCjhgt4hgw!-_khxU8gU0_6jc895I7kRbnU8JghRDsWgqOblZ4jr7Qp2IVbR30VYw_hWvNFtphnl0uWpB9KIvbYi1pvZz4$>
1041 East Butler Road   Greenville, South Carolina  29606
CONTACT BY: Phone 1-864-676-5252, Email or MS TEAMS


From: Anthony Carrizosa <[email protected]>
Sent: Tuesday, September 24, 2024 11:45 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [EXTERNAL] [Sprinklerforum] Re: Double Interlock Pre-Action Systems

Ken,
NFPA 13 does mention that due to the double interlock of the system the water 
delivery is required within 60 seconds. This requirement would necessitate the 
detection system and the sprinkler operating simultaneously to achieve this 
time limit.
See [cid:[email protected]]
One could use the RTI of the fire sprinkler and compare that to the detection 
system RTI to see if they are compatible.
Now the potter PFC 4410RC does mention it has some built in discharge timers 
for the releasing circuits.
[cid:[email protected]]
Given that NFPA 13 requires the 60 second water delivery time it would behoove 
the sprinkler designer to verify with the alarm design to assure that the RTI 
and these delay timers do not affect the water delivery time.

Just my two cents.

Anthony Carrizosa
Project Manager | Fire Protection
7855 S 206th St Kent, WA 98032
Cell: 206-679-5283 | Office Dir: 253-341-4593
[cid:[email protected]]






From: Ken Wagoner 
<[email protected]<mailto:[email protected]>>
Sent: Tuesday, September 24, 2024 7:33 AM
To: 
[email protected]<mailto:[email protected]>
Subject: [Sprinklerforum] Re: Double Interlock Pre-Action Systems

Kyle,

What Craig said.

There is no text in -13 or -72 of which I'm aware that specifies time 
requirements for electrical detection to send a signal to the releasing panel, 
or that it must be received by that panel prior to the fire sprinkler 
operating.  Additionally, there is no text I'm aware of which specifies a 
sequence of which detection has to occur first.

There may indeed be a built-in delay in the LHD.  Is it listed for use in 
support of a preaction fire sprinkler system?

sincerely,
Ken Wagoner, SET
Parsley Consulting
500 West Mechanic Street
Harrisonville, Missouri 64701-2235
Phone: (760) 745-6181
Visit the 
website<https://urldefense.com/v3/__https:/linkprotect.cudasvc.com/url?a=http*3a*2f*2fwww.parsleyconsulting.com*2f&c=E,1,Y5zKJKPEh1mBEBqSR-VE9cUKl5y-eyP8BpvmE_5j9ZqW2eJbNphYzrCMBZ-2YuX6d-RRkHI4gQ1FV-cvOeCfRC58uZS9NiToZv2mx7909oCqLvCW_n5hDHeK&typo=1__;JSUlJQ!!B5cixuoO7ltTeg!AFRluP0yE_54TuPOowQ3g7_AbfbdehEAWBWlEFWZw8UDT3GGEiwEQUF1T7s_pzFD87Rz5IqwciME0gml0TJ-u64ml1c$>



On 9/24/2024 8:37 AM, Prahl, Craig wrote:
In a DIPA system you HAVE to have both a sprinkler open and a detection device 
go into alarm.  It doesn’t matter in what order that would occur.  The DIPA 
system is more for prevention of discharge until it’s glaringly obvious that a 
fire is in progress.  Typical for freezers, Data Centers, sometimes electrical 
rooms when the sparky guys are really paranoid,  etc.

So, if the Linear Heat Detection (LHD) goes into alarm, it will transmit a 
signal to the DIPA releasing panel but nothing more is going to happen until a 
sprinkler opens.  Only when the LHD is in alarm AND a sprinkler opens is the PA 
valve going to open,

Any delay in the LHD signal is not going to be of any great relevance if the 
system is operating properly.  There is no calculation or specified time frame 
in any code or Standard.

Craig Prahl | Jacobs | Fire Protection SME – Special Hazards | 
[email protected]<mailto:[email protected]> | 
www.jacobs.com<https://urldefense.com/v3/__http:/www.jacobs.com/__;!!KZTdOCjhgt4hgw!-_khxU8gU0_6jc895I7kRbnU8JghRDsWgqOblZ4jr7Qp2IVbR30VYw_hWvNFtphnl0uWpB9KIvbYi1pvZz4$>
1041 East Butler Road   Greenville, South Carolina  29606
CONTACT BY: Phone 1-864-676-5252, Email or MS TEAMS


From: Kyle.Montgomery 
<[email protected]><mailto:[email protected]>
Sent: Monday, September 23, 2024 7:48 PM
To: 
[email protected]<mailto:[email protected]>
Subject: [EXTERNAL] [Sprinklerforum] Re: Double Interlock Pre-Action Systems

I guess what I’m really asking is what is the difference in response time for 
linear heat detection versus my sprinkler heads? In this case, it’s protecting 
cold storage, so it’s a standard-response, high-temperature sprinkler.

-Kyle M

From: Kyle.Montgomery
Sent: Monday, September 23, 2024 4:45 PM
To: 
[email protected]<mailto:[email protected]>
Subject: Double Interlock Pre-Action Systems

It’s my understanding that the premise behind double interlock pre-action 
systems is that they should be designed in such a way that, in the event of a 
fire, the detection (heat detector, flame detector, smoke detector, linear heat 
detection, etc.) should activate before a sprinkler head activates. Is there 
any formula or rule of thumb about how long the detection should take to 
activate versus how long the sprinkler should take to activate?

I’m working on a project and the alarm guy is telling me that there is a 
built-in activation delay in the releasing panel between when the linear heat 
detection sends a signal and when the releasing panel activates the solenoid 
valve. Is that normal? I’m wondering if that delay will actually delay the 
activation time of my pre-action valve, or if the delay is short enough that it 
is less than the normal time delta between linear heat detection activation and 
sprinkler head activation.

For example, if the built-in delay in the releasing panel is 15 seconds, but 
the delta between LHD activation and sprinkler head activation is normally more 
than 15 second, then there wouldn’t be any tangible delay in the activation 
(opening) of the pre-action valve.

Kyle Montgomery
 [cid:[email protected]]
Aero Automatic Sprinkler Co.
21605 N. Central Ave.
Phoenix, AZ 85024
Direct: 623.580.7820
Cell: 602.763.4736
[email protected]<mailto:[email protected]>


________________________________

NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.




_________________________________________________________

SprinklerForum mailing list:

https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org<https://urldefense.com/v3/__https:/linkprotect.cudasvc.com/url?a=https*3a*2f*2flists.firesprinkler.org*2flist*2fsprinklerforum.lists.firesprinkler.org&c=E,1,eHipl0cwH_1C-oYfggBLyrHSw1521Prhda8PdRco6wdYg1tdbZN-BiqQZLxyqNhLuhGg4pmHzLC2DMYSuO4C9hl_5-4dTY91uf2-V6geHEBv6CUcNrQ,&typo=1&ancr_add=1__;JSUlJSU!!B5cixuoO7ltTeg!AFRluP0yE_54TuPOowQ3g7_AbfbdehEAWBWlEFWZw8UDT3GGEiwEQUF1T7s_pzFD87Rz5IqwciME0gml0TJ-diLi2EY$>

To unsubscribe send an email to 
[email protected]<mailto:[email protected]>


________________________________

NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to