Just another thought. Is it possible that the designer used the pressure required at the source as the BOR? That could be the reason for the reason for the pressure difference. 

Chase

On Sep 11, 2024, at 1:03 PM, Rocci 3 Cetani <[email protected]> wrote:



Upper floor

 

Rocci Cetani III, CET

Senior Designer

Water-Based Fire Protections Systems Layout, Nicet Level III

 

 

Northern California Fire Protection Services Inc.

16840 Joleen Way Bldg. A

Morgan Hill, CA 95037

P-(408) 776-1580 EXT.1010

F-(408) 776-1590

 

To help better serve you. Please visit our new and improved website at:

www.norcalfire.com

 

CONFIDENTIALITY NOTICE: This message and any document accompanying it may contain confidential information belonging to the sender. The information is intended only for the use of individual or entity named above. If you are not the intended recipient, or the employee or agent responsible to deliver this message to the intended recipient, you are hereby notified that any disclosure, copying or taking of any action in reliance on the contents of this information is strictly prohibited. If you have received this transmission in error, please immediately notify us by telephone to arrange for return of the documents.

 

From: Steve Leyton <[email protected]>
Sent: Wednesday, September 11, 2024 9:58 AM
To: Discussion list on issues relating to automatic fire sprinklers <[email protected]>
Subject: [Sprinklerforum] Re: main drain test

 

Are you measuring at the base of the main building riser or on an upper floor?

 

From: Rocci 3 Cetani <[email protected]>
Sent: Wednesday, September 11, 2024 9:54 AM
To: Discussion list on issues relating to automatic fire sprinklers <[email protected]>
Subject: [Sprinklerforum] Re: main drain test

 

MDT

Static 62 (auto sprink says it should be 63.2 so its within a comfortable range)

Residual-  37

 

Flow test

Static 89

Residual 87

GPM 750

Rocci Cetani III, CET

Senior Designer

Water-Based Fire Protections Systems Layout, Nicet Level III

 

 

Northern California Fire Protection Services Inc.

16840 Joleen Way Bldg. A

Morgan Hill, CA 95037

P-(408) 776-1580 EXT.1010

F-(408) 776-1590

 

To help better serve you. Please visit our new and improved website at:

www.norcalfire.com

 

CONFIDENTIALITY NOTICE: This message and any document accompanying it may contain confidential information belonging to the sender. The information is intended only for the use of individual or entity named above. If you are not the intended recipient, or the employee or agent responsible to deliver this message to the intended recipient, you are hereby notified that any disclosure, copying or taking of any action in reliance on the contents of this information is strictly prohibited. If you have received this transmission in error, please immediately notify us by telephone to arrange for return of the documents.

 

From: Steve Leyton <[email protected]>
Sent: Wednesday, September 11, 2024 9:33 AM
To: Discussion list on issues relating to automatic fire sprinklers <[email protected]>
Subject: [Sprinklerforum] Re: main drain test

 

Sorry, I misstated something extremely important:  I referred to residual pressure instead of PITOT pressure in my mention of theoretical flows.   Management regrets the error and the committee has authorized a second cup of coffee.

 

Steve L.

 

 

From: Steve Leyton
Sent: Wednesday, September 11, 2024 9:25 AM
To: Discussion list on issues relating to automatic fire sprinklers <[email protected]>
Subject: RE: [Sprinklerforum] Re: main drain test

 

Respectfully disagree that this is a slam-dunk misunderstanding.   I have experienced two residual-pressure-at-BOR conflicts in my career and both went back to the water supply data.   One of them had to do with a  flow test that was taken from the address-side public main, but the system was supplied from a side street and it turned out that the POC was downstream of a regulating station installed at the branch to that leg of the system, so available pressure was 20 psi lower than the test data.   The other had to do with a flow test taken by a third party contractor hired by the project owner, and they used an old riser gauge on the hydrant.   Turns out that gauge was shot and the residual value was corrupt (reading high).   When the water supply was tested again, the flow rate was nearly identical but the residual was 8 or 9 or 10 psi lower using a calibrated gauge with ≤1% error.    As Chris noted, residual of 9-10 psi renders a theoretical flow equivalent to the demand through a 2” orifice per NFPA 291, Table 4.12.1(a), so the AHJ might be onto something.

 

What is are the static and residual readings on the riser gauge during the MDT, and what were the flow test values?  And memo to everyone citing NFPA 25, it is a requirement of NFPA 13, §29.2.3.4 that a main drain test be undertaken as part of acceptance testing.

 

 

Steve L.

 

From: Travis Mack <[email protected]>
Sent: Wednesday, September 11, 2024 8:24 AM
To: Discussion list on issues relating to automatic fire sprinklers <[email protected]>
Subject: [Sprinklerforum] Re: main drain test

 

A main drain test does not correlate to a BOR demand.  You have to flow the exact same demand to make them correlate.  So just educate the inspector.  This happens all the time in residential systems.

 

 

Travis Mack, SET

M.E.P.CAD | Instructor / Support

181 N. Arroyo Grande Blvd. #105 I Henderson, NV 89074

www.mepcad.com | m: 480.547.9348| Whatspp: +14805479348

Email: [email protected]

 

AutoSPRINK  |  AutoSPRINK FAB  |  AutoSPRINK RVT  |  AlarmCAD

 


From: Rocci 3 Cetani <[email protected]>
Sent: Wednesday, September 11, 2024 8:07 AM
To: Discussion list on issues relating to automatic fire sprinklers <[email protected]>
Subject: [Sprinklerforum] Re: main drain test

 

 

Demand is 361 gpm  with 45 PSI @ BOR. Main drain test they are getting 37  residual

Rocci Cetani III, CET

Senior Designer

Water-Based Fire Protections Systems Layout, Nicet Level III

 

 

Northern California Fire Protection Services Inc.

16840 Joleen Way Bldg. A

Morgan Hill, CA 95037

P-(408) 776-1580 EXT.1010

F-(408) 776-1590

 

To help better serve you. Please visit our new and improved website at:

www.norcalfire.com

 

CONFIDENTIALITY NOTICE: This message and any document accompanying it may contain confidential information belonging to the sender. The information is intended only for the use of individual or entity named above. If you are not the intended recipient, or the employee or agent responsible to deliver this message to the intended recipient, you are hereby notified that any disclosure, copying or taking of any action in reliance on the contents of this information is strictly prohibited. If you have received this transmission in error, please immediately notify us by telephone to arrange for return of the documents.

 

From: Steve Leyton <[email protected]>
Sent: Wednesday, September 11, 2024 7:55 AM
To: Discussion list on issues relating to automatic fire sprinklers <[email protected]>
Subject: [Sprinklerforum] Re: main drain test

 

Assuming that the demand from the calc area is for OH 1or 2 (and no inside hose), your demand is somewhere between 250 and 300 gpm If you modeled a full 1,500 sq ft, no? And what is the residual pressure required?

 

 

Steve Leyton

 

Sent from my "Smart" Phone, so apologies for any typos or voice-to-text corruptions.

 

 

 

-------- Original message --------

From: Rocci 3 Cetani <[email protected]>

Date: 9/11/24 7:19 AM (GMT-08:00)

Subject: [Sprinklerforum] main drain test

 

We have a jurisdiction that failed our final inspection because the residual pressure during the main drain test doesn’t match our BOR residual pressure from the hydraulic calcs for and OH extended coverage system.  Am I missing something? I don’t see how the residual pressure on a main drain test has anything to do with the residual pressure  from our calcs…..I was always under the impression main drain tests were to verify there hasn’t been a been a drastic change to the supply . This was an existing parking garage where they added solar panels on the top level so we added a sectional riser @ the top floor and added the new system. The fire department just keeps saying to upsize the riser from the 1st floor to the 4th floor which literally does nothing to my calcs. The building owner has spent 10’s of thousands of dollars flushing the UG, inspecting the UG for obstructions, paid for additional flow test  and serviced the back flow.  We are at a complete loss on what else to do as the fire department is adamant that’s the main drain test has to match the hydraulic calcs…..anyone ever come across a situation like this with a jurisdiction? Any suggestions?

 

Rocci Cetani III

 

Northern California Fire Protection Services Inc.

16840 Joleen Way Bldg. A

Morgan Hill, CA 95037

P-(408) 776-1580 EXT.1010

F-(408) 776-1590

 

To help better serve you. Please visit our new and improved website at:

www.norcalfire.com

 

CONFIDENTIALITY NOTICE: This message and any document accompanying it may contain confidential information belonging to the sender. The information is intended only for the use of individual or entity named above. If you are not the intended recipient, or the employee or agent responsible to deliver this message to the intended recipient, you are hereby notified that any disclosure, copying or taking of any action in reliance on the contents of this information is strictly prohibited. If you have received this transmission in error, please immediately notify us by telephone to arrange for return of the documents.

 


_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to