Just catching up on this - thanks for the referral Brian!

The drain estimator is only calculating the *maximum *possible flow from
the orifice opening, for the purposes of accommodating the worst-case flow
for drain sizing. The calculation is only incorporating pressure at an
open-orifice (like the calc for the side outlet of a hydrant), but not the
constriction that the main drain pipe and fittings have, nor the conversion
from a total pressure to a normal pressure that the riser gauge is
measuring.

Coincidentally (truly, weird) posted on this topic today:
https://www.meyerfire.com/blog/the-trouble-with-estimating-main-drain-flow

The best way to verify the actual flow is to measure the flow itself (a
bucket test or a pitot measurement), unless we build something to account
for the main drain constriction and the conversion between normal and total
pressure.

Joe


*MEYERFIRE, LLC*
*D: *(636) 299-0339   *E: *[email protected]   *W:* MeyerFire.com /
MeyerFPE.com <http://www.MeyerFPE.com>
<http://www.MeyerFPE.com>
Licensed: AR, CA, FL, IA, IL, MO, WI



On Wed, Sep 11, 2024 at 11:14 AM, Craig Prahl <[email protected]>
wrote:

> Maybe, maybe not.  You can get 775 out of a 2.5” hydrant outlet.
>
>
>
> Craig Prahl | Jacobs | Fire Protection SME – Special Hazards | craig.
> [email protected] | www.jacobs.com
> <https://urldefense.com/v3/__http:/www.jacobs.com/__;!!KZTdOCjhgt4hgw!-_khxU8gU0_6jc895I7kRbnU8JghRDsWgqOblZ4jr7Qp2IVbR30VYw_hWvNFtphnl0uWpB9KIvbYi1pvZz4$>
>
> 1041 East Butler Road   Greenville, South Carolina  29606
>
> CONTACT BY: Phone 1-864-676-5252, Email or MS TEAMS
>
>
>
>
>
> *From:* Travis Mack <[email protected]>
> *Sent:* Wednesday, September 11, 2024 12:09 PM
> *To:* Discussion list on issues relating to automatic fire sprinklers <
> [email protected]>
> *Subject:* [Sprinklerforum] Re: [External]Re: main drain test
>
>
>
> 775 gpm seems quite high coming out of a 2" pipe.  I would be skeptical of
> that number.
>
>
>
>
>
> Travis Mack, SET
>
> *M.E.P.CAD* | Instructor / Support
>
> 181 N. Arroyo Grande Blvd. #105 I Henderson, NV 89074
>
> www.mepcad.com
> <https://urldefense.com/v3/__http:/www.mepcad.com/__;!!B5cixuoO7ltTeg!DESJQ7V4PW_ELv_hHW6JiceQ6AdeIMAcg5xv9AW6IjUapgf2gwOcv9FuTn62-0tbWDn4y7QS_JB0m0Qt$>
>  |
> *m: 480.547.9348*|* Whatspp: +14805479348*
>
> *Email: [email protected] <[email protected]>*
>
>
>
> *AutoSPRINK  |  AutoSPRINK FAB  |  AutoSPRINK RVT  |  AlarmCAD*
>
>
> ------------------------------
>
> *From:* Rocci 3 Cetani <[email protected]>
> *Sent:* Wednesday, September 11, 2024 9:07 AM
> *To:* Discussion list on issues relating to automatic fire sprinklers <
> [email protected]>
> *Subject:* [Sprinklerforum] Re: [External]Re: main drain test
>
>
>
> Thanks Brian that’s helpful! Based on that the main drain is flowing 775
> GPM
>
>
>
> *Rocci Cetani III, **CET*
>
> *Senior Designer*
>
> *Water-Based Fire Protections Systems Layout, Nicet Level III*
>
>
>
>
>
> *Northern California Fire Protection Services Inc.*
>
> 16840 Joleen Way Bldg. A
>
> Morgan Hill, CA 95037
>
> P-(408) 776-1580 EXT.1010
>
> F-(408) 776-1590
>
>
>
> To help better serve you. Please visit our new and improved website at:
>
> www.norcalfire.com
> <https://urldefense.com/v3/__http:/www.norcalfire.com/__;!!B5cixuoO7ltTeg!DESJQ7V4PW_ELv_hHW6JiceQ6AdeIMAcg5xv9AW6IjUapgf2gwOcv9FuTn62-0tbWDn4y7QS_Blgw98V$>
>
>
>
> CONFIDENTIALITY NOTICE: This message and any document accompanying it may
> contain confidential information belonging to the sender. The information
> is intended only for the use of individual or entity named above. If you
> are not the intended recipient, or the employee or agent responsible to
> deliver this message to the intended recipient, you are hereby notified
> that any disclosure, copying or taking of any action in reliance on the
> contents of this information is strictly prohibited. If you have received
> this transmission in error, please immediately notify us by telephone to
> arrange for return of the documents.
>
>
>
> *From:* Brian Harris <[email protected]>
> *Sent:* Wednesday, September 11, 2024 8:42 AM
> *To:* Discussion list on issues relating to automatic fire sprinklers <
> [email protected]>
> *Subject:* [Sprinklerforum] Re: [External]Re: main drain test
>
>
>
> Meyer Fire has an estimating tool for Main Drain test you might find
> helpful.
>
>
>
> Thank you,
>
>
>
> *Brian Harris, CET*
>
> BVS Systems Inc.
>
>
>
> *From:* Rocci 3 Cetani <[email protected]>
> *Sent:* Wednesday, September 11, 2024 11:38 AM
> *To:* Discussion list on issues relating to automatic fire sprinklers <
> [email protected]>
> *Subject:* [Sprinklerforum] Re: [External]Re: main drain test
>
>
>
> No clue but it gushes and its a lot of water….. To get that info we would
> have to put a PITOT on it
>
>
>
> *Rocci Cetani III, **CET*
>
> *Senior Designer*
>
> *Water-Based Fire Protections Systems Layout, Nicet Level III*
>
>
>
>
>
> *Northern California Fire Protection Services Inc.*
>
> 16840 Joleen Way Bldg. A
>
> Morgan Hill, CA 95037
>
> P-(408) 776-1580 EXT.1010
>
> F-(408) 776-1590
>
>
>
> To help better serve you. Please visit our new and improved website at:
>
> www.norcalfire.com
> <https://urldefense.proofpoint.com/v2/url?u=https-3A__linkprotect.cudasvc.com_url-3Fa-3Dhttps-253a-252f-252fwww.norcalfire.com-26c-3DE-2C1-2CmklhcZzHoZPvChftzTitLgSMovE7oiIrLcVJlji0PrQzj916CayrBN15afOxmaG7kQOQFIAuiV7o-5F4S6PXK2LUIkm3W28F5UfdxAZCfgXZ8QFQ-2C-2C-26typo-3D1-26ancr-5Fadd-3D1&d=DwMFAg&c=euGZstcaTDllvimEN8b7jXrwqOf-v5A_CdpgnVfiiMM&r=hLXh1DXRDwJ3oz4y7iNesSsetYhUUV0wawfPGfwmYxQ&m=4MgkwyfUkSqSH5EthDszEx6bxHotseuzJPrGd0B3SN54F7kWYQO0OjgjvIOUm5gX&s=BFMUf-8lHBk9imzNQGhrrjN2JKb5_XtpjVjUokZkiTM&e=>
>
>
>
> CONFIDENTIALITY NOTICE: This message and any document accompanying it may
> contain confidential information belonging to the sender. The information
> is intended only for the use of individual or entity named above. If you
> are not the intended recipient, or the employee or agent responsible to
> deliver this message to the intended recipient, you are hereby notified
> that any disclosure, copying or taking of any action in reliance on the
> contents of this information is strictly prohibited. If you have received
> this transmission in error, please immediately notify us by telephone to
> arrange for return of the documents.
>
>
>
> *From:* Kyle.Montgomery <[email protected]>
> *Sent:* Wednesday, September 11, 2024 8:26 AM
> *To:* Discussion list on issues relating to automatic fire sprinklers <
> [email protected]>
> *Subject:* [Sprinklerforum] Re: [External]Re: main drain test
>
>
>
> Do you think, at 37 psi, that you’re pushing more than 361 GPM through
> that 2” drain?
>
>
>
> *Kyle Montgomery*
>
>
>
> *Aero Automatic Sprinkler Co.*
>
> *21605 N. Central Ave.*
>
> *Phoenix, AZ 85024*
>
> *Direct: 623.580.7820*
>
> *Cell: 602.763.4736*
>
> [email protected]
>
>
>
>
>
>
>
> *From:* Rocci 3 Cetani <[email protected]>
> *Sent:* Wednesday, September 11, 2024 8:17 AM
> *To:* Discussion list on issues relating to automatic fire sprinklers <
> [email protected]>
> *Subject:* [Sprinklerforum] Re: [External]Re: main drain test
>
>
>
> 6” feed in the stairwell with a 4” sectional and 2” drain
>
>
>
> *Rocci Cetani III, **CET*
>
> *Senior Designer*
>
> *Water-Based Fire Protections Systems Layout, Nicet Level III*
>
>
>
>
>
> *Northern California Fire Protection Services Inc.*
>
> 16840 Joleen Way Bldg. A
>
> Morgan Hill, CA 95037
>
> P-(408) 776-1580 EXT.1010
>
> F-(408) 776-1590
>
>
>
> To help better serve you. Please visit our new and improved website at:
>
> www.norcalfire.com
> <https://urldefense.proofpoint.com/v2/url?u=https-3A__linkprotect.cudasvc.com_url-3Fa-3Dhttps-253a-252f-252fwww.norcalfire.com-26c-3DE-2C1-2Cwou81MxbTNFOb5Wrybk6hAM1TkdVtQn18-2DDS-5FMAvJT2hcqP7CydJobiIvDjYg2PpsvNscDJReCUEWlRWkvoSKX2sfg906Fxcig4N-5F4-5F4GicLUDc-2C-26typo-3D1-26ancr-5Fadd-3D1&d=DwMFAg&c=euGZstcaTDllvimEN8b7jXrwqOf-v5A_CdpgnVfiiMM&r=hLXh1DXRDwJ3oz4y7iNesSsetYhUUV0wawfPGfwmYxQ&m=4MgkwyfUkSqSH5EthDszEx6bxHotseuzJPrGd0B3SN54F7kWYQO0OjgjvIOUm5gX&s=vCmAO1iPPQj_ZKR0i-3jV35t8lPjv4qxQiEAuTfrZPM&e=>
>
>
>
> CONFIDENTIALITY NOTICE: This message and any document accompanying it may
> contain confidential information belonging to the sender. The information
> is intended only for the use of individual or entity named above. If you
> are not the intended recipient, or the employee or agent responsible to
> deliver this message to the intended recipient, you are hereby notified
> that any disclosure, copying or taking of any action in reliance on the
> contents of this information is strictly prohibited. If you have received
> this transmission in error, please immediately notify us by telephone to
> arrange for return of the documents.
>
>
>
> *From:* Kyle.Montgomery <[email protected]>
> *Sent:* Wednesday, September 11, 2024 8:12 AM
> *To:* Discussion list on issues relating to automatic fire sprinklers <
> [email protected]>
> *Subject:* [Sprinklerforum] Re: [External]Re: main drain test
>
>
>
> What size riser and drain?
>
>
>
> *From:* Rocci 3 Cetani <[email protected]>
> *Sent:* Wednesday, September 11, 2024 8:07 AM
> *To:* Discussion list on issues relating to automatic fire sprinklers <
> [email protected]>
> *Subject:* [External][Sprinklerforum] Re: main drain test
>
>
>
>
>
> Demand is 361 gpm  with 45 PSI @ BOR. Main drain test they are getting 37
> residual
>
> *Rocci Cetani III, **CET*
>
> *Senior Designer*
>
> *Water-Based Fire Protections Systems Layout, Nicet Level III*
>
>
>
>
>
> *Northern California Fire Protection Services Inc.*
>
> 16840 Joleen Way Bldg. A
>
> Morgan Hill, CA 95037
>
> P-(408) 776-1580 EXT.1010
>
> F-(408) 776-1590
>
>
>
> To help better serve you. Please visit our new and improved website at:
>
> www.norcalfire.com
> <https://urldefense.proofpoint.com/v2/url?u=https-3A__linkprotect.cudasvc.com_url-3Fa-3Dhttps-253a-252f-252fwww.norcalfire.com-26c-3DE-2C1-2Cypo-2DhmJif318ePaAIPvyejzM7sa42vkXcVSWq2hma8JCF-5FsYNcgOt9-2D58KHlgTq5dY4ZmdHUzWUmfQrxUZJ-5Fn6I1cvAMB-2DCvVk-2DH08hQ3FPMEdoavQ-2C-2C-26typo-3D1-26ancr-5Fadd-3D1&d=DwMFAg&c=euGZstcaTDllvimEN8b7jXrwqOf-v5A_CdpgnVfiiMM&r=hLXh1DXRDwJ3oz4y7iNesSsetYhUUV0wawfPGfwmYxQ&m=4MgkwyfUkSqSH5EthDszEx6bxHotseuzJPrGd0B3SN54F7kWYQO0OjgjvIOUm5gX&s=4epqfbB5mlpZ6nuXQESD6qKK1XFs9Rqt7bblZ_Tb_lE&e=>
>
>
>
> CONFIDENTIALITY NOTICE: This message and any document accompanying it may
> contain confidential information belonging to the sender. The information
> is intended only for the use of individual or entity named above. If you
> are not the intended recipient, or the employee or agent responsible to
> deliver this message to the intended recipient, you are hereby notified
> that any disclosure, copying or taking of any action in reliance on the
> contents of this information is strictly prohibited. If you have received
> this transmission in error, please immediately notify us by telephone to
> arrange for return of the documents.
>
>
>
> *From:* Steve Leyton <[email protected]>
> *Sent:* Wednesday, September 11, 2024 7:55 AM
> *To:* Discussion list on issues relating to automatic fire sprinklers <
> [email protected]>
> *Subject:* [Sprinklerforum] Re: main drain test
>
>
>
> Assuming that the demand from the calc area is for OH 1or 2 (and no inside
> hose), your demand is somewhere between 250 and 300 gpm If you modeled a
> full 1,500 sq ft, no? And what is the residual pressure required?
>
>
>
>
>
> Steve Leyton
>
>
>
> Sent from my "Smart" Phone, so apologies for any typos or voice-to-text
> corruptions.
>
>
>
>
>
>
>
> -------- Original message --------
>
> From: Rocci 3 Cetani <[email protected]>
>
> Date: 9/11/24 7:19 AM (GMT-08:00)
>
> To: [email protected]
>
> Subject: [Sprinklerforum] main drain test
>
>
>
> We have a jurisdiction that failed our final inspection because the
> residual pressure during the main drain test doesn’t match our BOR residual
> pressure from the hydraulic calcs for and OH extended coverage system.  Am
> I missing something? I don’t see how the residual pressure on a main drain
> test has anything to do with the residual pressure  from our calcs…..I was
> always under the impression main drain tests were to verify there hasn’t
> been a been a drastic change to the supply . This was an existing parking
> garage where they added solar panels on the top level so we added a
> sectional riser @ the top floor and added the new system. The fire
> department just keeps saying to upsize the riser from the 1st floor to
> the 4th floor which literally does nothing to my calcs. The building
> owner has spent 10’s of thousands of dollars flushing the UG, inspecting
> the UG for obstructions, paid for additional flow test  and serviced the
> back flow.  We are at a complete loss on what else to do as the fire
> department is adamant that’s the main drain test has to match the hydraulic
> calcs…..anyone ever come across a situation like this with a jurisdiction?
> Any suggestions?
>
>
>
> *Rocci Cetani III*
>
>
>
> *Northern California Fire Protection Services Inc.*
>
> 16840 Joleen Way Bldg. A
>
> Morgan Hill, CA 95037
>
> P-(408) 776-1580 EXT.1010
>
> F-(408) 776-1590
>
>
>
> To help better serve you. Please visit our new and improved website at:
>
> www.norcalfire.com
> <https://urldefense.proofpoint.com/v2/url?u=https-3A__linkprotect.cudasvc.com_url-3Fa-3Dhttps-253a-252f-252fwww.norcalfire.com-26c-3DE-2C1-2C7zy7IWDFl7WhyVO2rc-5FfD2Qggpjudq9RY4UToa1lNX4cxZxcKfz-2D4g6Y3tjr6DoY84Hj-5F0-5F2DEaJ2Fj8xllC3pU-5FgdVH7kji7IxBk0jTQTv8T1utM-2DI15Q-2C-2C-26typo-3D1-26ancr-5Fadd-3D1&d=DwMFAg&c=euGZstcaTDllvimEN8b7jXrwqOf-v5A_CdpgnVfiiMM&r=hLXh1DXRDwJ3oz4y7iNesSsetYhUUV0wawfPGfwmYxQ&m=4MgkwyfUkSqSH5EthDszEx6bxHotseuzJPrGd0B3SN54F7kWYQO0OjgjvIOUm5gX&s=cw5j8NI1AgErRaOjhotqF82eM7CWpuwjoiSoRZP13Go&e=>
>
>
>
> CONFIDENTIALITY NOTICE: This message and any document accompanying it may
> contain confidential information belonging to the sender. The information
> is intended only for the use of individual or entity named above. If you
> are not the intended recipient, or the employee or agent responsible to
> deliver this message to the intended recipient, you are hereby notified
> that any disclosure, copying or taking of any action in reliance on the
> contents of this information is strictly prohibited. If you have received
> this transmission in error, please immediately notify us by telephone to
> arrange for return of the documents.
>
>
>
> ------------------------------
>
> NOTICE - This communication may contain confidential and privileged
> information that is for the sole use of the intended recipient. Any
> viewing, copying or distribution of, or reliance on this message by
> unintended recipients is strictly prohibited. If you have received this
> message in error, please notify us immediately by replying to the message
> and deleting it from your computer.
>
> _________________________________________________________ SprinklerForum
> mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.
> org To unsubscribe send an email to sprinklerforum-leave@lists.
> firesprinkler.org
>
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to