drain ties into a gang drain and run down to the ground level. We are up on the 
4th floor

Rocci Cetani III, CET
Senior Designer
Water-Based Fire Protections Systems Layout, Nicet Level III


Northern California Fire Protection Services Inc.
16840 Joleen Way Bldg. A
Morgan Hill, CA 95037
P-(408) 776-1580 EXT.1010
F-(408) 776-1590

To help better serve you. Please visit our new and improved website at:
www.norcalfire.com<http://www.norcalfire.com/>

CONFIDENTIALITY NOTICE: This message and any document accompanying it may 
contain confidential information belonging to the sender. The information is 
intended only for the use of individual or entity named above. If you are not 
the intended recipient, or the employee or agent responsible to deliver this 
message to the intended recipient, you are hereby notified that any disclosure, 
copying or taking of any action in reliance on the contents of this information 
is strictly prohibited. If you have received this transmission in error, please 
immediately notify us by telephone to arrange for return of the documents.

From: Kyle.Montgomery <[email protected]>
Sent: Wednesday, September 11, 2024 9:13 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Re: [External]Re: main drain test

Is the water discharging directly from the drain at the riser? Or does the 
drain tie into a gang drain and run down to the ground level? The Meyer Fire 
calculator does not appear to account for the length of pipe between the gauge 
and the drain outlet, which can make a big difference. At that flow, a 2" pipe 
is losing like 1 psi per foot.

-Kyle M

From: Rocci 3 Cetani <[email protected]<mailto:[email protected]>>
Sent: Wednesday, September 11, 2024 9:07 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Re: [External]Re: main drain test

Thanks Brian that's helpful! Based on that the main drain is flowing 775 GPM

Rocci Cetani III, CET
Senior Designer
Water-Based Fire Protections Systems Layout, Nicet Level III


Northern California Fire Protection Services Inc.
16840 Joleen Way Bldg. A
Morgan Hill, CA 95037
P-(408) 776-1580 EXT.1010
F-(408) 776-1590

To help better serve you. Please visit our new and improved website at:
www.norcalfire.com<https://urldefense.proofpoint.com/v2/url?u=http-3A__www.norcalfire.com_&d=DwMFAg&c=euGZstcaTDllvimEN8b7jXrwqOf-v5A_CdpgnVfiiMM&r=hLXh1DXRDwJ3oz4y7iNesSsetYhUUV0wawfPGfwmYxQ&m=RKwbLbiwymmmOFn5llSgFJ9pe7uuxqeXDNYhSKEMus5MXjaoG8Gjc4z3OY33EpRs&s=go885urhkWT5cM-Qj_NMNfhmCQAK_Ybim4EPoN-URSk&e=>

CONFIDENTIALITY NOTICE: This message and any document accompanying it may 
contain confidential information belonging to the sender. The information is 
intended only for the use of individual or entity named above. If you are not 
the intended recipient, or the employee or agent responsible to deliver this 
message to the intended recipient, you are hereby notified that any disclosure, 
copying or taking of any action in reliance on the contents of this information 
is strictly prohibited. If you have received this transmission in error, please 
immediately notify us by telephone to arrange for return of the documents.

From: Brian Harris <[email protected]<mailto:[email protected]>>
Sent: Wednesday, September 11, 2024 8:42 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Re: [External]Re: main drain test

Meyer Fire has an estimating tool for Main Drain test you might find helpful.

Thank you,

Brian Harris, CET
BVS Systems Inc.

From: Rocci 3 Cetani <[email protected]<mailto:[email protected]>>
Sent: Wednesday, September 11, 2024 11:38 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Re: [External]Re: main drain test

No clue but it gushes and its a lot of water..... To get that info we would 
have to put a PITOT on it

Rocci Cetani III, CET
Senior Designer
Water-Based Fire Protections Systems Layout, Nicet Level III


Northern California Fire Protection Services Inc.
16840 Joleen Way Bldg. A
Morgan Hill, CA 95037
P-(408) 776-1580 EXT.1010
F-(408) 776-1590

To help better serve you. Please visit our new and improved website at:
www.norcalfire.com<https://urldefense.proofpoint.com/v2/url?u=https-3A__linkprotect.cudasvc.com_url-3Fa-3Dhttps-253a-252f-252fwww.norcalfire.com-26c-3DE-2C1-2CmklhcZzHoZPvChftzTitLgSMovE7oiIrLcVJlji0PrQzj916CayrBN15afOxmaG7kQOQFIAuiV7o-5F4S6PXK2LUIkm3W28F5UfdxAZCfgXZ8QFQ-2C-2C-26typo-3D1-26ancr-5Fadd-3D1&d=DwMFAg&c=euGZstcaTDllvimEN8b7jXrwqOf-v5A_CdpgnVfiiMM&r=hLXh1DXRDwJ3oz4y7iNesSsetYhUUV0wawfPGfwmYxQ&m=4MgkwyfUkSqSH5EthDszEx6bxHotseuzJPrGd0B3SN54F7kWYQO0OjgjvIOUm5gX&s=BFMUf-8lHBk9imzNQGhrrjN2JKb5_XtpjVjUokZkiTM&e=>

CONFIDENTIALITY NOTICE: This message and any document accompanying it may 
contain confidential information belonging to the sender. The information is 
intended only for the use of individual or entity named above. If you are not 
the intended recipient, or the employee or agent responsible to deliver this 
message to the intended recipient, you are hereby notified that any disclosure, 
copying or taking of any action in reliance on the contents of this information 
is strictly prohibited. If you have received this transmission in error, please 
immediately notify us by telephone to arrange for return of the documents.

From: Kyle.Montgomery 
<[email protected]<mailto:[email protected]>>
Sent: Wednesday, September 11, 2024 8:26 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Re: [External]Re: main drain test

Do you think, at 37 psi, that you're pushing more than 361 GPM through that 2" 
drain?

Kyle Montgomery
 [cid:[email protected]]
Aero Automatic Sprinkler Co.
21605 N. Central Ave.
Phoenix, AZ 85024
Direct: 623.580.7820
Cell: 602.763.4736
[email protected]<mailto:[email protected]>



From: Rocci 3 Cetani <[email protected]<mailto:[email protected]>>
Sent: Wednesday, September 11, 2024 8:17 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Re: [External]Re: main drain test

6" feed in the stairwell with a 4" sectional and 2" drain

Rocci Cetani III, CET
Senior Designer
Water-Based Fire Protections Systems Layout, Nicet Level III


Northern California Fire Protection Services Inc.
16840 Joleen Way Bldg. A
Morgan Hill, CA 95037
P-(408) 776-1580 EXT.1010
F-(408) 776-1590

To help better serve you. Please visit our new and improved website at:
www.norcalfire.com<https://urldefense.proofpoint.com/v2/url?u=https-3A__linkprotect.cudasvc.com_url-3Fa-3Dhttps-253a-252f-252fwww.norcalfire.com-26c-3DE-2C1-2Cwou81MxbTNFOb5Wrybk6hAM1TkdVtQn18-2DDS-5FMAvJT2hcqP7CydJobiIvDjYg2PpsvNscDJReCUEWlRWkvoSKX2sfg906Fxcig4N-5F4-5F4GicLUDc-2C-26typo-3D1-26ancr-5Fadd-3D1&d=DwMFAg&c=euGZstcaTDllvimEN8b7jXrwqOf-v5A_CdpgnVfiiMM&r=hLXh1DXRDwJ3oz4y7iNesSsetYhUUV0wawfPGfwmYxQ&m=4MgkwyfUkSqSH5EthDszEx6bxHotseuzJPrGd0B3SN54F7kWYQO0OjgjvIOUm5gX&s=vCmAO1iPPQj_ZKR0i-3jV35t8lPjv4qxQiEAuTfrZPM&e=>

CONFIDENTIALITY NOTICE: This message and any document accompanying it may 
contain confidential information belonging to the sender. The information is 
intended only for the use of individual or entity named above. If you are not 
the intended recipient, or the employee or agent responsible to deliver this 
message to the intended recipient, you are hereby notified that any disclosure, 
copying or taking of any action in reliance on the contents of this information 
is strictly prohibited. If you have received this transmission in error, please 
immediately notify us by telephone to arrange for return of the documents.

From: Kyle.Montgomery 
<[email protected]<mailto:[email protected]>>
Sent: Wednesday, September 11, 2024 8:12 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Re: [External]Re: main drain test

What size riser and drain?

From: Rocci 3 Cetani <[email protected]<mailto:[email protected]>>
Sent: Wednesday, September 11, 2024 8:07 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: [External][Sprinklerforum] Re: main drain test


Demand is 361 gpm  with 45 PSI @ BOR. Main drain test they are getting 37  
residual
Rocci Cetani III, CET
Senior Designer
Water-Based Fire Protections Systems Layout, Nicet Level III


Northern California Fire Protection Services Inc.
16840 Joleen Way Bldg. A
Morgan Hill, CA 95037
P-(408) 776-1580 EXT.1010
F-(408) 776-1590

To help better serve you. Please visit our new and improved website at:
www.norcalfire.com<https://urldefense.proofpoint.com/v2/url?u=https-3A__linkprotect.cudasvc.com_url-3Fa-3Dhttps-253a-252f-252fwww.norcalfire.com-26c-3DE-2C1-2Cypo-2DhmJif318ePaAIPvyejzM7sa42vkXcVSWq2hma8JCF-5FsYNcgOt9-2D58KHlgTq5dY4ZmdHUzWUmfQrxUZJ-5Fn6I1cvAMB-2DCvVk-2DH08hQ3FPMEdoavQ-2C-2C-26typo-3D1-26ancr-5Fadd-3D1&d=DwMFAg&c=euGZstcaTDllvimEN8b7jXrwqOf-v5A_CdpgnVfiiMM&r=hLXh1DXRDwJ3oz4y7iNesSsetYhUUV0wawfPGfwmYxQ&m=4MgkwyfUkSqSH5EthDszEx6bxHotseuzJPrGd0B3SN54F7kWYQO0OjgjvIOUm5gX&s=4epqfbB5mlpZ6nuXQESD6qKK1XFs9Rqt7bblZ_Tb_lE&e=>

CONFIDENTIALITY NOTICE: This message and any document accompanying it may 
contain confidential information belonging to the sender. The information is 
intended only for the use of individual or entity named above. If you are not 
the intended recipient, or the employee or agent responsible to deliver this 
message to the intended recipient, you are hereby notified that any disclosure, 
copying or taking of any action in reliance on the contents of this information 
is strictly prohibited. If you have received this transmission in error, please 
immediately notify us by telephone to arrange for return of the documents.

From: Steve Leyton 
<[email protected]<mailto:[email protected]>>
Sent: Wednesday, September 11, 2024 7:55 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Re: main drain test

Assuming that the demand from the calc area is for OH 1or 2 (and no inside 
hose), your demand is somewhere between 250 and 300 gpm If you modeled a full 
1,500 sq ft, no? And what is the residual pressure required?


Steve Leyton

Sent from my "Smart" Phone, so apologies for any typos or voice-to-text 
corruptions.



-------- Original message --------
From: Rocci 3 Cetani <[email protected]<mailto:[email protected]>>
Date: 9/11/24 7:19 AM (GMT-08:00)
To: 
[email protected]<mailto:[email protected]>
Subject: [Sprinklerforum] main drain test

We have a jurisdiction that failed our final inspection because the residual 
pressure during the main drain test doesn't match our BOR residual pressure 
from the hydraulic calcs for and OH extended coverage system.  Am I missing 
something? I don't see how the residual pressure on a main drain test has 
anything to do with the residual pressure  from our calcs.....I was always 
under the impression main drain tests were to verify there hasn't been a been a 
drastic change to the supply . This was an existing parking garage where they 
added solar panels on the top level so we added a sectional riser @ the top 
floor and added the new system. The fire department just keeps saying to upsize 
the riser from the 1st floor to the 4th floor which literally does nothing to 
my calcs. The building owner has spent 10's of thousands of dollars flushing 
the UG, inspecting the UG for obstructions, paid for additional flow test  and 
serviced the back flow.  We are at a complete loss on what else to do as the 
fire department is adamant that's the main drain test has to match the 
hydraulic calcs.....anyone ever come across a situation like this with a 
jurisdiction? Any suggestions?

Rocci Cetani III

Northern California Fire Protection Services Inc.
16840 Joleen Way Bldg. A
Morgan Hill, CA 95037
P-(408) 776-1580 EXT.1010
F-(408) 776-1590

To help better serve you. Please visit our new and improved website at:
www.norcalfire.com<https://urldefense.proofpoint.com/v2/url?u=https-3A__linkprotect.cudasvc.com_url-3Fa-3Dhttps-253a-252f-252fwww.norcalfire.com-26c-3DE-2C1-2C7zy7IWDFl7WhyVO2rc-5FfD2Qggpjudq9RY4UToa1lNX4cxZxcKfz-2D4g6Y3tjr6DoY84Hj-5F0-5F2DEaJ2Fj8xllC3pU-5FgdVH7kji7IxBk0jTQTv8T1utM-2DI15Q-2C-2C-26typo-3D1-26ancr-5Fadd-3D1&d=DwMFAg&c=euGZstcaTDllvimEN8b7jXrwqOf-v5A_CdpgnVfiiMM&r=hLXh1DXRDwJ3oz4y7iNesSsetYhUUV0wawfPGfwmYxQ&m=4MgkwyfUkSqSH5EthDszEx6bxHotseuzJPrGd0B3SN54F7kWYQO0OjgjvIOUm5gX&s=cw5j8NI1AgErRaOjhotqF82eM7CWpuwjoiSoRZP13Go&e=>

CONFIDENTIALITY NOTICE: This message and any document accompanying it may 
contain confidential information belonging to the sender. The information is 
intended only for the use of individual or entity named above. If you are not 
the intended recipient, or the employee or agent responsible to deliver this 
message to the intended recipient, you are hereby notified that any disclosure, 
copying or taking of any action in reliance on the contents of this information 
is strictly prohibited. If you have received this transmission in error, please 
immediately notify us by telephone to arrange for return of the documents.

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to