If the criteria for the greater hazard produces discharge characteristics equal 
to or greater than the what is required for the lesser hazard, you have met or 
exceeded the minimum protection requirement.

So, the answer to your first question is Yes.

Craig Prahl | Jacobs | Fire Protection SME - Special Hazards | 
[email protected]<mailto:[email protected]> | 
www.jacobs.com<https://urldefense.com/v3/__http:/www.jacobs.com/__;!!KZTdOCjhgt4hgw!-_khxU8gU0_6jc895I7kRbnU8JghRDsWgqOblZ4jr7Qp2IVbR30VYw_hWvNFtphnl0uWpB9KIvbYi1pvZz4$>
1041 East Butler Road   Greenville, South Carolina  29606
CONTACT BY: Phone 1-864-676-5252, Email or MS TEAMS


From: Kyle.Montgomery <[email protected]>
Sent: Monday, August 26, 2024 8:04 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [EXTERNAL] [Sprinklerforum] Re: Protection of Expanded Group A Plastics

Any thoughts on this?

From: Kyle.Montgomery
Sent: Friday, August 23, 2024 10:37 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: Protection of Expanded Group A Plastics

If a system is designed to protect EXPOSED Expanded Group A Plastics, then is 
it automatically sufficient for protection of CARTONED Expanded Group a 
Plastics?

In the NFPA 13 table, there is no option listed for protecting Cartoned 
Expanded Group A Plastics with K22 or K25 ESFR sprinklers. Why is that? There 
are options for K14 and K17 sprinklers.

There is an option to use K25 ESFR sprinklers to protect Exposed Expanded Group 
A Plastics. If a system is designed to that criteria, does that system also 
provide adequate protection for Cartoned Expanded Group A Plastics?

[Note: I do know that there are more protection options using FM datasheets, 
but I'm curious specifically about NFPA requirements.]

Thanks.

Kyle Montgomery
 [cid:[email protected]]
Aero Automatic Sprinkler Co.
21605 N. Central Ave.
Phoenix, AZ 85024
Direct: 623.580.7820
Cell: 602.763.4736
[email protected]<mailto:[email protected]>




________________________________

NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to