Hello fellows, hoping you're doing well.

I would like to know, based on your experience, what is the value you
consider as a limit to specify dry barrel sprinklers into a cooler.

Pure water freezes at 0°C (40°F), but in a cooler that is supposed to work
in the range of 2°C to 8°C (36°F to 47°F) is it necessary to install dry
barrel sprinklers?

NFPA 13 indicates 40°F the starting temperature in this table:

[image: image.png]

The minimum exposed barrel is 0 inches for all the exterior temperatures
when the protected area is 40°F. The actual exterior temperature is
about 87°F.

If there is no need for exposed barrel length, is this sufficient to
assume that a standard wet sprinkler is appropriate?

I would like to know your thoughts on this!

Have a nice day!



-- 
=?Este mensaje se dirige exclusivamente a su destinatario y puede contener
información privilegiada o confidencial. Si no es Ud. el destinatario
indicado, queda notificado de que la utilización, divulgación y/o copia sin
autorización está prohibida en virtud de la legislación vigente. Si ha
recibido este mensaje por error, le rogamos que nos lo comunique
inmediatamente por esta misma vía y proceda a su destrucción.


This message is intended exclusively for its addressee and may contain
information that is confidential and protected by professional privilege.
If you are not the intended recipient you are hereby notified that any
dissemination, copy or disclosure of this communication is strictly
prohibited by law. If this message has been received in error, please
notify us immediately via e-mail and delete it.
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to