Hi Craig,

Are the code sections you referenced, correct?

Tony

On Thu, Jun 6, 2024 at 1:20 PM Prahl, Craig <[email protected]> wrote:

> If the open top containers are limited to the bottom row they are not
> prohibited.  See NFPA 13, 2019, A.3.1.9.19, (2).
>
>
>
>
>
>
>
> Craig Prahl | Jacobs | Fire Protection SME – Special Hazards |
> [email protected] | www.jacobs.com
> <https://urldefense.com/v3/__http:/www.jacobs.com/__;!!KZTdOCjhgt4hgw!-_khxU8gU0_6jc895I7kRbnU8JghRDsWgqOblZ4jr7Qp2IVbR30VYw_hWvNFtphnl0uWpB9KIvbYi1pvZz4$>
>
> 1041 East Butler Road   Greenville, South Carolina  29606
>
> CONTACT BY: Phone 1-864-676-5252, Email or MS TEAMS
>
>
>
>
>
> *From:* [email protected] <[email protected]>
> *Sent:* Thursday, June 6, 2024 2:38 PM
> *To:* [email protected]
> *Subject:* [EXTERNAL] [Sprinklerforum] Re: rack storage
>
>
>
> By lowest, are they still “In-Rack” or on the floor?
>
>
>
> I would think that on the floor may help. But not sure of that..
>
>
>
> R/
>
> Matt
>
>
>
> *Matthew J. Willis, CWBSP, C.E.T.*
>
> *Ferguson Fire Design, LLC*
>
> D: (602) 337-0721 <http://(602)%20337-0721> C: (307) 236-8249
> <http://(307)%20236-8249>
>
> [email protected]
>
>
>
> *From:* Tony Silva <[email protected]>
> *Sent:* Thursday, June 6, 2024 11:46 AM
> *To:* Discussion list on issues relating to automatic fire sprinklers <
> [email protected]>
> *Subject:* [Sprinklerforum] rack storage
>
>
>
> *Caution:  This email originated from outside of the organization.  DO NOT
> click links or open attachments unless you recognize and trust the sender. *
> ------------------------------
>
> This warehouse (for Sephora) has rack storage for ignitable liquids and
> aerosols. The roof has ESFR sprinklers. The racks are protected with
> standard in-rack sprinklers below plywood barriers. There is no storage
> above the topmost barrier.
>
>
>
> Question: The tenant wants to have the products (at the lowest level) in
> cardboard boxes / bins that are open at the top and one side (that facing
> the aisle). The requirement for ESFR sprinklers prohibits open top
> containers. Does containers refer only to the individual packaging of the
> product? Or also to the bins where the products are placed? If it applies
> to the bins also, would the ESFR requirement (of no open top containers)
> also apply to the standard in-rack sprinklers?
>
>
>
> Thanks,
>
> Tony
>
> ------------------------------
>
> NOTICE - This communication may contain confidential and privileged
> information that is for the sole use of the intended recipient. Any
> viewing, copying or distribution of, or reliance on this message by
> unintended recipients is strictly prohibited. If you have received this
> message in error, please notify us immediately by replying to the message
> and deleting it from your computer.
>
> _________________________________________________________
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> [email protected]
>
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to