See the annex material for the definition of open top container (a.3.3.149 in 
2022), if there’s nothing stored below it doesn’t matter.  Also if the side is 
all the way open so that water can’t collect in it it probably doesn’t fit the 
definition either.

Mike Morey
CFPS 3229 • NICET S.E.T. 123677
Project Estimator • Fire Protection Group
Shambaugh & Son, LP an EMCOR Company
7614 Opportunity Drive • Fort Wayne, IN • 46825
direct 260.487.7824 /  cell 260.417.0625 /  fax 260.487.7991
email [email protected]<mailto:[email protected]>
[cid:[email protected]]

From: Tony Silva <[email protected]>
Sent: Thursday, June 6, 2024 1:46 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] rack storage

This warehouse (for Sephora) has rack storage for ignitable liquids and 
aerosols. The roof has ESFR sprinklers. The racks are protected with standard 
in-rack sprinklers below plywood barriers. There is no storage above the 
topmost barrier. Question: 
ZjQcmQRYFpfptBannerStart
This Message Is From an Untrusted Sender
You have not previously corresponded with this sender.
ZjQcmQRYFpfptBannerEnd
This warehouse (for Sephora) has rack storage for ignitable liquids and 
aerosols. The roof has ESFR sprinklers. The racks are protected with standard 
in-rack sprinklers below plywood barriers. There is no storage above the 
topmost barrier.

Question: The tenant wants to have the products (at the lowest level) in 
cardboard boxes / bins that are open at the top and one side (that facing the 
aisle). The requirement for ESFR sprinklers prohibits open top containers. Does 
containers refer only to the individual packaging of the product? Or also to 
the bins where the products are placed? If it applies to the bins also, would 
the ESFR requirement (of no open top containers) also apply to the standard 
in-rack sprinklers?

Thanks,
Tony

This message is for the named person's use only.  It may contain confidential, 
proprietary or legally privileged information. No confidentiality or privilege 
is waived or lost by any mistransmission.  If you receive this message in 
error, please  immediately delete it and all copies of it from your system, 
destroy any hard copies of it and notify the sender.  You must not, directly or 
indirectly, use, disclose, distribute, print, or copy any part of this message 
if you are not the intended recipient.
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to