There is not, as long as they have the same RTI. The big problem with mixing them is maintenance, as someone may swap out an EC for a standard and then there is a coverage gap.
Craig D. Hanson, CFPS Fire Division Manager West Coast Code Consultants, Inc. (WC³) Meridian Satellite Office *C:* 253.225.9977 | *E:* [email protected] | www.WC-3.com <https://www.wc-3.com/> *Teaming With Your Community to Make a Difference* On Thu, Jun 6, 2024 at 7:38 AM Joshua Taylor <[email protected]> wrote: > All, > > > > Is there anything in the code preventing the installation of extended > coverage and standard spray coverage heads of the same style (i.e. > semi-rec. style) in the same area? > > Assuming there is code issue, what are thoughts on taking this route? > > > > > > > > > > Thank you > > [image: Fire Protection Service] > > Joshua Taylor : Fire Sprinkler Designer > > 4132 Dumont Street #4 > > Cincinnati, OH 45226 > > www.dornfireportection.com > > > > > > _________________________________________________________ > SprinklerForum mailing list: > https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org > To unsubscribe send an email to > [email protected] >