> Correct - for standpipe calculations purposes, buildings protected with
> NFPA 13R systems do not meet the requirements to limit the flow to 1,250 GPM
>
> 10.6.1.1.6 in NFPA 14 - 2024
>
> John August Denhardt, P.E.
> Vice-President Engineering and Technical Services
> American Fire Sprinkler Association
> 301-343-1457
>
> On Apr 3, 2024, at 09:49, Fpdcdesign <[email protected]> wrote:
>
> 
> 13R buildings are not considered to be fully sprinklered.
>
>
>
> On Apr 3, 2024 at 9:45 AM, <Shawn Foor <[email protected]>> wrote:
>
> Why would you do 1250 if it’s a fully sprinklered building?
>
> Shawn Foor, SET
>
> *FOOR DESIGN, LLC*
> *10208 E 98TH ST*
> *TULSA, OK 74133*
> *P:918-237-1400*
>
>
> On Wed, Apr 3, 2024 at 08:43 <[email protected]> wrote:
>
>> Asking this on behalf of Rowe Sprinkler Systems (Temporally Un-Retired)
>>
>>
>>
>> We have a 4-story modular apartment building sprinklered in accordance
>> with NFPA 13R with allowed exceptions, with 4 standpipes. The standpipes
>> are connected at the 1st floor level. One each at the ends of the L
>> shaped building and two at the approximate mid-point on either side of a
>> 2-hour separation wall with self-closing, rated doors in the corridor.
>>
>> The question is for purposes of calculating the standpipe can these be
>> treated as two separate buildings? For example, 250 gpm at the far end of
>> the 4th floor, 250 gpm at the far end of the 3rd floor and 250 gpm at
>> the at the connecting point of the middle standpipe, for a total of 750
>> gpm.
>>
>> Or do we have to calculate the additional standpipes up to 1250 gpm.
>> Available water is the issue.
>>
>>
>>
>>
>>
>> Richard L. Mote CET
>>
>> Rimrock Design Services, LLC
>>
>> Middleburg, PA 17842
>>
>> Mobile 570-541-2685
>>
>> EMAIL [email protected]
>>
>> WEB: www.rimrockdesignservicesllc.com
>> <https://nam02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.rimrockdesignservicesllc.com%2F&data=05%7C02%7Cjdenhardt%40stricklandfire.com%7C52a2159dd68941f7805208dc53e4d0b2%7Cd658cbf30820420e8485ef2e373e8459%7C0%7C0%7C638477489453405076%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C0%7C%7C%7C&sdata=k2q4EC6bKriuy5Qi1xyhuuooVD3MtZeManZT0WESZQ0%3D&reserved=0>
>>
>>
>>
>> _________________________________________________________
>> SprinklerForum mailing list:
>>
>> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
>> <https://nam02.safelinks.protection.outlook.com/?url=https%3A%2F%2Flists.firesprinkler.org%2Flist%2Fsprinklerforum.lists.firesprinkler.org&data=05%7C02%7Cjdenhardt%40stricklandfire.com%7C52a2159dd68941f7805208dc53e4d0b2%7Cd658cbf30820420e8485ef2e373e8459%7C0%7C0%7C638477489453415712%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C0%7C%7C%7C&sdata=BpLdmfm45fv%2FTRsIkSNhQKlVj%2F0mVqZXJAn4NHWheH8%3D&reserved=0>
>> To unsubscribe send an email to
>> [email protected]
>
> _________________________________________________________ SprinklerForum
> mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> [email protected]
>
>
> _________________________________________________________
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> [email protected]
>
>
> _________________________________________________________
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> [email protected]



-- 
Shawn Foor, SET

*FOOR DESIGN, LLC*
*10208 E 98TH ST*
*TULSA, OK 74133*
*P:918-237-1400*
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to