13R buildings are not considered to be fully sprinklered.   
  
  
  
  
  
  
  

  
  
>   
> On Apr 3, 2024 at 9:45 AM,  <Shawn Foor (mailto:[email protected])>  wrote:
>   
>   
>   
> Why would you do 1250 if it’s a fully sprinklered building?    
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
> Shawn Foor, SET
>   
>
>   
> FOOR DESIGN, LLC
>   
> 10208 E 98TH ST
>   
> TULSA, OK 74133
>   
> P:918-237-1400
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>
>   
>
>   
>   
> On Wed, Apr 3, 2024 at 08:43  <[email protected] 
> (mailto:[email protected])>  wrote:
>   
> >   
> >   
> >   
> >
> > Asking this on behalf of Rowe Sprinkler Systems (Temporally Un-Retired)
> >
> >   
> >
> >   
> >
> >   
> >
> > We have a 4-story modular apartment building sprinklered in accordance with 
> > NFPA 13R with allowed exceptions, with 4 standpipes. The standpipes are 
> > connected at the 1st  floor level. One each at the ends of the L shaped 
> > building and two at the approximate mid-point on either side of a 2-hour 
> > separation wall with self-closing, rated doors in the corridor.  
> >
> >   
> >
> > The question is for purposes of calculating the standpipe can these be 
> > treated as two separate buildings? For example, 250 gpm at the far end of 
> > the 4th  floor, 250 gpm at the far end of the 3rd  floor and 250 gpm at the 
> > at the connecting point of the middle standpipe, for a total of 750 gpm.  
> >
> >   
> >
> > Or do we have to calculate the additional standpipes up to 1250 gpm. 
> > Available water is the issue.  
> >
> >   
> >
> >   
> >
> >   
> >
> >   
> >
> >   
> >
> > Richard L. Mote CET
> >
> >   
> >
> > Rimrock Design Services, LLC
> >
> >   
> >
> > Middleburg, PA 17842
> >
> >   
> >
> > Mobile 570-541-2685
> >
> >   
> >
> > EMAIL  [email protected] 
> > (mailto:[email protected])
> >
> >   
> >
> > WEB:  www.rimrockdesignservicesllc.com 
> > (http://www.rimrockdesignservicesllc.com)
> >
> >   
> >
> >   
> >
> >   
> >   
> >   
> >  _________________________________________________________
> >  SprinklerForum mailing list:
> >   
> > https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> >  To unsubscribe send an email to  
> > [email protected] 
> > (mailto:[email protected])      
> > _________________________________________________________ SprinklerForum 
> > mailing list: 
> > https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org 
> > To unsubscribe send an email to 
> > [email protected]            
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to