Why would you do 1250 if it’s a fully sprinklered building?

Shawn Foor, SET

*FOOR DESIGN, LLC*
*10208 E 98TH ST*
*TULSA, OK 74133*
*P:918-237-1400*


On Wed, Apr 3, 2024 at 08:43 <[email protected]> wrote:

> Asking this on behalf of Rowe Sprinkler Systems (Temporally Un-Retired)
>
>
>
> We have a 4-story modular apartment building sprinklered in accordance
> with NFPA 13R with allowed exceptions, with 4 standpipes. The standpipes
> are connected at the 1st floor level. One each at the ends of the L
> shaped building and two at the approximate mid-point on either side of a
> 2-hour separation wall with self-closing, rated doors in the corridor.
>
> The question is for purposes of calculating the standpipe can these be
> treated as two separate buildings? For example, 250 gpm at the far end of
> the 4th floor, 250 gpm at the far end of the 3rd floor and 250 gpm at the
> at the connecting point of the middle standpipe, for a total of 750 gpm.
>
> Or do we have to calculate the additional standpipes up to 1250 gpm.
> Available water is the issue.
>
>
>
>
>
> Richard L. Mote CET
>
> Rimrock Design Services, LLC
>
> Middleburg, PA 17842
>
> Mobile 570-541-2685
>
> EMAIL [email protected]
>
> WEB: www.rimrockdesignservicesllc.com
>
>
>
> _________________________________________________________
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> [email protected]
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to