| Correct - for standpipe calculations purposes, buildings protected with NFPA 13R systems do not meet the requirements to limit the flow to 1,250 GPM
10.6.1.1.6 in NFPA 14 - 2024 John August Denhardt, P.E. Vice-President Engineering and Technical Services American Fire Sprinkler Association 301-343-1457
13R buildings are not considered to be fully sprinklered. Why would you do 1250 if it’s a fully sprinklered building? Shawn Foor, SET
FOOR DESIGN, LLC 10208 E 98TH ST TULSA, OK 74133 P:918-237-1400
Asking this on behalf of Rowe Sprinkler Systems (Temporally Un-Retired) We have a 4-story modular apartment building sprinklered in accordance with NFPA 13R with allowed exceptions, with 4 standpipes. The standpipes are connected at the 1st floor level. One each at the ends of the L shaped building and two at the approximate mid-point on either side of a 2-hour separation wall with self-closing, rated doors in the corridor. The question is for purposes of calculating the standpipe can these be treated as two separate buildings? For example, 250 gpm at the far end of the 4th floor, 250 gpm at the far end of the 3rd floor and 250 gpm at the at the connecting point of the middle standpipe, for a total of 750 gpm. Or do we have to calculate the additional standpipes up to 1250 gpm. Available water is the issue. Richard L. Mote CET Rimrock Design Services, LLC Middleburg, PA 17842 Mobile 570-541-2685 EMAIL [email protected] WEB: www.rimrockdesignservicesllc.com
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]
_________________________________________________________SprinklerForum mailing list:https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.orgTo unsubscribe send an email to [email protected]
|
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]